>I just bought a brandy new early Christmas present for myself (I'm soooo hard to shop for...get it "Shop")
I bought the 18" Rikon, and I will be using it to cut up my old Crapsman :-) (that's the gloat)
Here's the question:
How much should it cost me for an electrician to install a single 220V outlet in my garage? Figure that the run is 15' max from the panel. I did the 110V stuff, but I'm not comfortable wiring 220V.
>Steve, if you're not comfortable, don't do it. With travel time, it'll probably run you more than $50 plus parts.
OTOH, 220 is only 110 x 2.
Home Depot has everything you need. Wire the outlet first. Same box as 110, and a duplex receptacle similar to the 110 except the slots are turned 90� and it's alittle more expensive. A 15 amp circuit should more than suffice, so you need to buy 14/2 armored cable. The 220 cable cable contains 2 insulated wires plus ground. Whereas on a 110 circuit only the black is hot and the white is neutral, on a 220 each insulated wire carries 110, and there is no neutral. One wire to each side of the receptacle and the ground to ground. If your insulated wires are black and white in colour, wrap a piece of red or black tape around the neds of the white wire to signal that it's hot.
At the panel end, instead of one breaker for 110v, you insert a pair that are linked together. Each of the hot wires goes into one of the breakers, and the bare ground goes to the ground bar NOT the neutral.
>Gee, I guess I can gloat also. I bought it while it was still on sale at Woodcraft on Monday. It was cheaper to buy it on line as opposed to the store. The wiring isn't difficult as Garrett said. There are some good books available on rewiring and wiring - see your local bookstore or library.
Re: Worst part is that I have a BE in electrical e
John Lucas
>Steve I'll agree with Garret, don't do it if your scared of it. I just jumped in figuring each leg is just 110. I did buy a book from Lowes on wiring to make sure I didn't do something stupid. What I did find was the last guy who wired my garage did do a bunch of things wrong so I redid them while I was wiring the 220. So far nothing has burned up, Knock on wood.
>Garret, Canadian dat youz is, youz is fagedin' dat dis is New Joisey.
Darefor,
Stevie could best plan on a coupla C notes on dis job unless, of corse, his box is full. If dats bein' da case, he could plan on a coupla more for da sub-panel plus sumpin for my brudda-in-law whose da 'lectric inspecta, and den dare's da poirmit . . .
What, you got a problem wit dat?
Steve, It's pretty simple stuff as long as you've got space in the box. Book's at the library or find a friendly sparky with a little spare time on Saturday.
If your Lowes is like the one around here, they have a few circuits wired up on a board. You can see how 220 is different from 110. Some Lowes even have some people knowledgeable about wiring and they can walk you through it. Since you know about 110 all you need to know is the differences from 220. You might even check out how some of your buddies' 220 circuits are wired.
If you are still concerned after investigating it, you could do all of the mechanical stuff, such as running the wire and mounting the boxes where you want them. This would save the electrician time and he could just make the connections in the boxes and the panel.
I think you might plan on spending closer to $200 than $50, unless you have connections (no pun intended).
>220 is like 110 except it causes a louder bang when something goes wrong.
Get a 220 breaker, run your wire, turn power off, connect W to the breaker, connect Black to breaker, connect ground to neutral bar in power box. Install your 220 plug. Turn power on and you are good to go.
>If you did the 110 you should do the 220 as well.Get a little guidance from someone who knows what they're doing.I did all the wiring in my shop-you can do it.
>Steve As others have said 220 is just 110 two times.
The breaker has two screws for the wire. Use 3 wire romex with a ground. Red and black go to the two terminals on the breaker and on the plug in the wall. Wire the white and bare copper just like 110 v.a.c.
Unless he plans to pull a 110 feed off the cicuit (like for a light on the saw) somewhere, he doesn't need 3-wire stock; two hots and the neutral/ground is all that's required.
>Mark, most electrical inspectors I have dealt with will insist on the red wire for the second leg, or at the bare minimum adding red tape to the second leg on all terminations to code it as 220V vs 110V. As a couple others have said, it will likely cost in excess of $200 to have an electrician come in cold. I would imagine anyone with an electrical or electronics degree can determine the difference between 110 and 220, with very little research, and 20 feet of three conductor with a ground can't come close to what an electrician call-out would cost. Steve, you are quite capable of wiring 220, with a simple understanding of the difference. I would use 12 guage wire, and size the breaker to suit the motor. Go for it!
>>most electrical inspectors I have dealt with will
>insist on the red wire for the second leg, or at
>the bare minimum adding red tape to the second
>leg on all terminations
Unless it's changed from the last time I read it, the code says you just have to color the end of the wire. If the inspector wants something else, ask him politely to show it to you in the code. (Don't forget it is his job to enforce the rules, not to make or even interpret them.)
I don't think it being 220 should make any difference in deciding whether to wire it yourself. 110 will kill you just as dead as 220.
As for the wiring, it is no different from 110. Run the wire to the box, wire up the outlet end (if you use a receptacle), kill the power to the box (recommended), punch a hole for the romex connector, plug in a 220 breaker (don't use 2 independent 110 breakers), wire up the ground to the common block and the hot leads to the breaker, check for shorts with a multimeter(optional), flip the power on, test all legs of the circuit with a meter, all done.
Wiring the receptacle (and the matching connector on the cord) can be the most confusing part since there are many different configurations, but they are all labeled inside if you take the time to look. We once almost electrocuted a summer student in the optical lab when he touched a ground and an optical table holding some high-powered equipment. A pair of licensed electricians had wired a high voltage receptacle/extension cord incorrectly and we ended up with power on the ground.
>I think is the term, Doug. If I remember correctly, residential Code says "hots" must be either black or red wires (let's forget about yellow 4-way traveler circuits) with ground/neutral as bare or green. You therefore recolor the white wire at all circuit connections with either black or red e-tape so the next guy who's absorbed a few too many electrons doesn't get confused. |;-}}
>Yeah, Mark, in another life I did a lot of electrical work, both industrial and residential, and found some situations you just wouldn't believe. I have been one of those with too many electrons, at times, as well. I was in the air about 30 feet on suspended ceiling T-tracks when I got 277V from one hand to the other. It's hard to keep up your precarious balancing act when you are dancing with lightning, you know what I mean? Or the one about the 45 year old machinery that used 480V controls on the remote panel in a dusty environment? I more than once have watched as the arc path proceeded from one switch to the other, having noticed it when I heard a small hiss. Remarkable how the carbonized trail inches so slowly from one spot to the other. I can identify as well with JKJ's experience of an electrified table. In the Air Force 35 years ago we had a test bench with 300VDC on it. Let me tell you, when you inadvertently hit that much DC, it's an eye-opening experience. I flew ten feet over the back of the stool I was sitting on.
And reflaggging is the term I was looking for, as well. It helps to have some discrimination for 220V conductors, for those of us that come behind and have to figure these things out later.
What little I know, I learned from a PP&L Senior Foreman by way of practical on-site applications. He always maintained that he'd rather be playing with 60Kv lines than dealing with ordinary house currents. He explained that residential AC, working at 50-60 cycles and 15 to 30 amps was the most likely to stop your heart by scrambling its electrical tempo.
I have been planning to wire my shop for 240V and was considering the fast and easy route of a single 240V circuit directly from my service panel. Unfortunately the panel is full so I'm thinking of installing a 60-70 amp subpanel in the shop (with a lockable master switch) but I'm not sure how that should be done. If I tap into the service feed (i.e. before the exisiting panel) will that potentially exceed the service capacity to the residence (the existing service panel has a 200A main breaker). Since this may get complicated, I intend to hire an electrician to do at least some of the work but I like to be educated so I can understand all that is involved and not put blind faith in a potentially shady contractor. Any advice is appreciated. TIA.
>I had 100 amp sub panel installed in the garage. The electrician put in a bigger meter box and connected a small 100 amp breaker box similar to an airconditioner box to the meter box. He then ran the feed wire to the 100 amp panel. I still need to run the the 220 and 110 circuits.
The cost for 2 men, new mast, meter box, breaker box, new feed to house panel, feed to the sub panel and the sub panel was just over $1,000. It might have been less if there had been a clause about me not spending the day watching and asking questions
You will need a sub-panel with say, 12 bays, a 60 amp 240 breaker, and the required wire and armored shielding. The procedure is to pull 2 existing single (full size) breakers from the main box, install the 60amp breaker to power the feed to the sub, then move the displaced breakers and circuits onto the subpanel. You now have 10 circuit bays for your shop wiring. All that said, you MUST have this done by a licensed Sparky. Were this done by you or even by "someone who knows electric" and then something go wrong and a fire start, guaranteed your home insurance would be cancelled, and any claim would be denied.
A sub-panel job such as you describe is, at most, an hour's work for a license; especially if you have the sub's mounting prepared in advance.
My answer assumed you were asking about the simplest way to get some extra circuits for your shop in a situation where a 1-man shop might have a 12amp 220 dust collector running along with lights and a 3-5hp saw or lathe at the same time. If, however, you're looking for MORE POWER[!!!] like Stuart did with his 100amp garage box fed directly from the service, that's not going to work as a sub-panel as I described. You will need your service checked to see how much you're actually getting from the street, and you're talking a 2-man job, with possible power company involvement and change of hardware if your service is limited to the 200 amps you now have for the residence.
Your assumption was correct in that I'd like to be able to simultaneously operate a 240V machine (probably 3 hp maximum) and dust collector (my current dust collector is 16A at 120V but I may rewire it for 240V). The shop already has decent lighting on dedicated circuits so I'm covered there but I was thinking of adding one or two 20A 120V circuits for receptacles.
Based on the poor quality of "craftsmanship" I see too often around here (here meaning SoCal), I've learned how to DIY most home improvement tasks. But I understand that electrickery is a special case so I guess I'll begrudgingly break down and get some bids from pros. At least now I have a better handle on my options. Thanks!
That sounds like the magic number for any bid in my area.
Need some tile installed? "That'll run about $1000".
Need some trees trimmed? "That'll run about $1000".
Need a subpanel installed in the shop? "That'll run about $1000".
Hmmm, the electrician might want more since I'll ask plenty of questions too!
I've got a Unisaw that I picked up used over a month ago just taking up space awaiting power so I guess I'll get the crowbar out and treat myself to shop power for Christmas (I don't think SWMBO was expecting anything anyway 8-| ).