#1

OT - Plumbing reno/ground

ThomD

>I had to redo some plumbing in the basement, including removing a water line that ran over the top of the breaker panel and entry. In redoing this stuff I used Pex tubing for the most part, all non-drinking water lines. In the process, I took out a section of copper pipe that had a ground wire from the panel attacked to it. Bridged that section, for the time being, but even with the pipe removed and no bridge, my circuit tester indicates an intact ground. Ok there might be another ground though we haven't located it, but I did wonder whether there is any way of getting a false ground indication. I want to be sure the household electrical is properly configured (short of calling an electrician :)).

Re: OT - Plumbing reno/ground

#2

Re: OT - Plumbing reno/ground - long

Bill Houghton, Sebastopol, CA

>In (at least most of) the United States, the neutral leg (white wire, when you're wiring) of the 220V service is grounded at the transformer, and, in wiring up the main panel, you bond this wire to both the neutral bus and the ground bus*. In addition, a properly wired panel will have a ground wire fastened to a ground rod of some sort, driven into the earth** 8-10 feet.

Thus, you'll get a ground reading at the panel without the wire being connected. Wiring systems, properly done, have redundant grounds; I believe it's still true that in most jurisdictions it's required to drive a ground rod for subpanels in outbuildings, even though the ground wire is connected to the redundantly grounded main panel. But I digress.

The purpose of the ground wire on the plumbing is not to ground the electrical service, but to serve as an equipment ground for the plumbing system. Since plumbing systems may or may not be grounded naturally, if you happen to grab something with defective wiring and a plumbing fixture at the same time, you can get a shock and/or get dead (depending on many variables: the strength of the current, your personal conductivity at the moment [wet/dry hands, etc.], your physical condition [heart condition, age, size, all those fun things]) if the plumbing does not have an equipment ground.

I'm not familiar with current practice for PEX and other plastic plumbing - it's been more than 30 years since I briefly earned a living as a sparky - but, if you've got mixed plumbing, I'd certainly bridge over any plastic and get a good connection from plumbing to panel.

Wire size: my local county permits No. 8; I'd step up to No. 6, myself. A little extra money but worth it. Use the same gauge for your bridge(s).

NOTE: remember, as I noted, that my information's not current. If your city/county has a good building inspection department, it might, as my county does, have a general guide to building practices. The $20 I invested in my county's guide has repaid itself about 10 times over so far. You might call: "I'm thinking about a remodel; do you have any guides to building practices?"

If you're not sure of yourself on this, call friends until you can locate a competent electrician (licensure does NOT guarantee competence; my son's had to clean up after some licensed electricians who ought to have their wire strippers taken away) who's willing to come out and inspect it for a reasonable fee. $100 for an hour of inspection time is trivial compared to being dead. If your employer has a maintenance department, you're likely to find that one of the electricians there does weekend work; again, do a little research about competence.

*ONLY at the main panel. After that, the neutral and equipment ground wires run separately, and the neutral bus is isolated from the panel.

**Which is why the British and perhaps others whose English is closer to the mother tongue refer to the "earth" side of the circuit, always entertaining when referring to, say, motorcycle wiring, where there's an "earth" side too, although you always want to keep the motorcycle from contacting too awfully much of the earth.

Re: OT - Plumbing reno/ground

#3

Said that wrong

Bill Houghton, Sebastopol, CA

>The main safety issue is if the PLUMBING becomes energized - say, a hot wire touches it due to chafing, or there's an internal fault in some water-connected appliance like a dishwasher - you want it to conduct the power to ground (and, one hopes, trip the relevant circuit breaker), rather than you conducting it to ground.

Sorry - it's been a long, long day at the end of a long, long week.

Re: OT - Plumbing reno/ground

#4

Re: Said that wrong

ThomD

>Thanks bill, that would seem to explain my situation. Currently I have the bridge in, in the form of jumper cables. I only have two water connected applicances both of which now has pex on them, and are presumably grounded through the wire. That means they can't energize the plumbing. Though other faults could. I will see what I can find in the way of local advice.

Re: OT - Plumbing reno/ground

#5

If I recall correctly

Bill Houghton, Sebastopol, CA

>at one time, it was code to ground the electrical service through the water lines. This was back when plumbing was metal - "plastic" being a punchline in a far, far future moving picture show.

Trouble is, galvanized, the most common plumbing material back when, eventually rusts in the ground*, and fails to provide as thorough a path to ground. Thus ground rods.

So it's an understandable mistake to presume that the wire to the plumbing is for the service ground.

*Personal side note: in the course of doing the crawl space insulation, I've discovered a large galvanized pipe that's flaking off rust, and seeping - moisture all around it. It's in front of - toward the street from - the pipe that juts up out of the crawl space to feed the house plumbing, but I don't yet know if it's the connection to our city service. When the house was hooked up to the city, they just tapped into the existing plumbing (previously fed from a tank atop the tankhouse, aka watertower) - but I have no idea where. I suspect I'm going to have to pay someone to bring in one of those fancy machines to trace it from the connection at the street, then dig it up and replace it. Gawd. There are days when I'm ready for a condo (one with a large shop, if there are such things).