OT electrical question.

Posts

OT electrical question.

#1

OT electrical question.

JohnV

Can I safely remove one leg from a 220 circuit and make a 110 circuit?

I'm replacing an electric range with a gas one. There is no convenient 110 outlet to power the gas circuit. I know I'd need to replace the 220 breaker. I'd leave the wire intact so a future owner could easily reinstall an electric range.

Re: OT electrical question.

#2

Re: OT electrical question.

Dick Coers

You need a hot, neutral and a ground for a 110 circuit. Are you proposing using the existing wire and using both hots from the 220 for hot and neutral?

Re: OT electrical question.

#3

Re: OT electrical question.

John McGaw

Four wire or the older three-wire 220V circuit?

Re: OT electrical question.

#4

Re: OT electrical question.

Walter Ahlgrim

1 Understand if you do put an outlet in this circuit the fuse/breaker must be changed to 20 amps max. The original fuse/breaker is likely 40 or 50 amps if you had a 120 volt outlet on a 50 breaker and something were to short circuit inside an appliance plugged into that outlet, the cord would very likely start a fire before the 50 amp breaker tripped where a 20 amp would likely trip without a fire.

2 What gage wire did the stove have? Is a the current cable 2 conductors and a ground or 3 conductors and a ground?

Walta

Re: OT electrical question.

#5

Re: OT electrical question.

JohnV

I would use the existing wire connecting one hot and the neutral and the ground. Leaving the other hot for future reconnection should a future owner wish.

Re: OT electrical question.

#6

Re: OT electrical question.

JohnV

I would replace the breaker with the appropriate size.

Re: OT electrical question.

#7

Re: OT electrical question.

John K Jordan

1 Understand if you do put an outlet in this circuit the fuse/breaker must be changed to 20 amps max....

That's if the existing wiring is 12 gauge. If smaller, don't use a 20 amp breaker.

JKJ

Re: OT electrical question.

#8

Re: OT electrical question.

JohnV

current wire is 10 gauge.

Re: OT electrical question.

#9

Re: OT electrical question.

John in NM

Given that it was running a stove, it must be pretty stout wire - 10 awg at least. Kind of a pain to work with, but feasible. If it's 8 or 6 I doubt you can do it just due to the large diameters not working well with an outlet designed for much smaller wire.

Other than that, there is really no reason why it won't work, wire is wire. Just disconnect and cap at both ends any conductor you don't use (I would also label it). Replace the 240V breaker with an appropriately sized 120V single (smaller ok, so you can put a 20 amp breaker/outlet on 10 awg wire).

This is assuming you have a 4 wire setup (or more accurately 3 with ground). If it's just 2 with ground, you could use the other, formerly hot conductor as the common and label each end with white tape or heat shrink. That may not be an accepted practice in your area however (or anywhere these days), so do so at your own risk. If the old circuit is just 2 conductor without ground, you can't make a modern circuit out of it.

Re: OT electrical question.

#10

Re: OT electrical question.

Barry Irby

Since you have a copper wire No. 10 copper circuit you can do what you propose. Cap the unused hot on both ends. The no. 10 will the stiff and difficult, but it's doable. Might be easier to add a short leader of No 12.

Re: OT electrical question.

#11

Re: OT electrical question.

Bill Tindall, E.Tn.

If replacing the breaker anyway, why not just replace the breaker with a 110 breaker wired with 3 of the 4 wires in the 220 cable and wire nut off the 4th in the panel? The 110 breaker could be sized to the wire in place, or less.

Re: OT electrical question.

#12

Re: OT electrical question.

Larry Clinton At Frankfort, (Central) Indiana

You can do as Bill said EXCEPT you must size the breaker to the lowest amperage rated permanent item in the line. In your case that includes the wire AND the outlet. Most house outlets are 20 Amp, if that is what you install you must install a 20 Amp breaker. The breaker is not rated to protect the device cord or the device - only the permanent items that are fixed to the house. IE: You can plug in a table lamp with #18 wire or a 18 gauge extension cord into a 20 Amp outlet!

Re: OT electrical question.

#13

Re: OT electrical question.

Brian Anderson

I doubt a licensed electrician would do what you are suggesting. The safest move is to replace breaker with a proper breaker for what you are installing. If it is a permanent item such as stove, that would mean sizing the breaker for that alone. AND replace the wiring. Then there is no debate as to capacity. It is a correctly wired installation, not a jury-rigged circuit. An inspector would most likely nix your idea as not being to code. AND if you have a fire with your rig no doubt if they learn of your jury rig, they might well deny your claim as it does not meet code and or was not inspected.

Re: OT electrical question.

#14

Re: OT electrical question.

Larry Clinton At Frankfort, (Central) Indiana

First, I did industrial, commercial and residential wiring for several years in Indiana, for NIPSCO, and other power supplier customers. In Indiana there is NO "Licensed Electrician" nor Licensed Contractor. There is state licenses for Plumbers, Barbers, Bartenders etc. I was insured and bonded and much of my work was inspected by municipalities and or the power company.

I admit I haven't kept up with code changed for 10 years or so, but as I posted as long as the correct wiring is done and the wire size is as large or larger than the necessary conductor amperage and not to large to properly be attached properly to the terminations, (it can be spliced to the correct wire size in the main and /or outlet box if necessary) it would have passed all codes I am aware of when I was doing this work in the evenings and weekends.

Re: OT electrical question.

#15

The capricious  of codes

Bill Tindall, E.Tn.

When we built there was a local code change for the connector from house wire into a metal fixture like a fluorescent light fixture or range hood. The old style with a threaded stud and locking nut were replaced with an expanding affair that was a pain to deal with and offered no benefit I could discern.

Daughter is building a deck. "Code" for her area forbid a 14' span of 2x10's on 16" centers. Really! Every house I ever worked on, or saw, that was 28' wide had a floor of free span 2 x 10's on 16" centers.

No doubt many codes are a response to some historical event that resulted in a hazard of some sort. Others I am mystified where they come from, or they fit generic situations that may be irrelevant to one's current situation. In cases they add unnecessary cost for no benefit. A cynic could speculate that some are perpetrated by materials manufacturers.

I don't treat them as rules from God. If they don't make sense I ignore them, and fortunately I live where in most cases I can. The bare minimum wiring went into my barn and shop. When the panel was inspected and the power turned on, then I wired for my convenience.

Re: OT electrical question.

#16

Re: OT electrical question.

Jay Lombardo

Retired Sparky here, the short answer to you question is yes. Just change the breaker to a single pole 20A. depending how old the original wiring is you may or may not even have a white neutral at this box. Is this installation done in romex (not used around here) or EMT with individual wires? Just use existing neutral if present or convert other existing wire to neutral and clearly identify it with white phasing tape. Your fine.

Re: OT electrical question.

#17

Re: The capricious  of codes

Barry Irby

The limiting of spans on decks may be the result of the endless number of deck collapses over the years. Knowing they will be left in the weather and will degrade over time they may be looking ahead. Also, I am not sure, but in the dim recesses of my mind I seem to recall that the treatment process degrades the strength of the lumber as much as 25%. That would be something to check out. And in addition there is the thing known as "the wedding party deck". Everything is fine until the 4th of July or maybe Labor Day, Or your daughter gets married and fifty of your closest friends walk out on your deck. A crowded deck is much more heavily loaded than your bedroom.

Last year I got a call on the 6th of July. The deck on one of my rentals collapsed. The tenants just don't know what happened. The neighbor came over while we were replacing the deck and was Laughing about the big party and the keg and and all. When the dancing started, the deck went down. Fortunately no one was hurt, except my wallet.

On Emerald Isle, NC the authorities realized they had hundreds of decks, some of them two stories off the ground that were over thirty years old. They made them replace them.

So, as much as I hate Codes maybe a conservative one for decks is a good idea.

Re: OT electrical question.

#18

Re: OT electrical question.

Brian Anderson

Larry, I would like to apologize as it appears you interpreted my post as a response to YOUR post; it was not. It was a post in response to the original post of this thread .

2nd I am not interested in a pissing contest.

BUT my research shows that Indiana DOES INDEED have licensing program for electricians. It is performed on a country basis and is a written exam.

My post was intended as generalized advice. Follow the building codes or your house insurance might not be able to pay off in the event of a house fire related to electrical problems.

And even if you are an experienced electrician, an inspection by the local building department is a good idea. As a law abiding professional, don't you agree?

Re: OT electrical question.

#19

Jason Roehl in Lafayette, IN

Re: OT electrical question.

Jason Roehl in Lafayette, IN

Electrical licensing in Indiana is spotty. A few municipalities require it. Most of the state does not. I live in Tippecanoe County. The county seat is Lafayette, which requires licensing, I don't know about West Lafayette, and outside city limits, there is no requirement. Larry lives in Clinton County, and I'm pretty sure there are no requirements there. Indiana has a large number of rural counties which don't have the resources for extensive licensing and building inspection. Not to mention, Indiana also has a "Log Cabin Law"--you can build on your own property without inspection, but that doesn't mean the local authorities won't give you grief over it, and you more than likely won't be able to insure the structure, mortgage it, or sell it.

For that matter, I work for the county as a maintenance tech. I do electrical work quite a bit without a license. Today, however, I'll be working with an experienced union electrician as we're adding some exterior lighting to my building and my boss wants to tap into his experience since it's a DMX-controlled setup.

As for the original question, I'd replace the breaker with a 20-amp, re-identify a wire as a neutral if necessary, and add some 12 AWG leads to the end to make it easier to connect the receptacle (using the screws, of course--I don't like to back-stab). Also, if you take out a double breaker and replace with a single (to go from 240V to 120V), you should cover the hole in the panel cover. There are snap-in plastic pieces made just for that purpose.

Jason

Re: OT electrical question.

#20

Re: The capricious  of codes

Larry Clinton At Frankfort, (Central) Indiana

Often codes in areas are dictated by political reasons, not safety or even reliability. For instance years ago in Northern Indiana or Southern Ill (can't remember), I remember when the code required masonry chimneys. The code was enacted due to a mason's union that didn't want the Triple wall or brands like Dura vent used as it made them lose work. This was done after the metal pipe had been approved and proven in tens of thousands of homes throughout the USA.

Another example was the requirement that they use metal conduit for house wiring, several states required it due to pressure from Electrical Unions. The code allowed the conduit to be used as the ground for the outlets etc. A few years after this was required it was found the conduit was corroding and losing connection (Ground) in coastal areas of CA and Florida. This caused all the "grounded" appliances to not be grounded. If / when an appliance shorted the entire "grounded" portion of the electrical system became 120 Volt "hot" with reference to earth ground. This resulted in many people being shocked and even killed in bathrooms and kitchens!

Remember many of today's code's were enacted by politicians not scientist's or Engineers!