220-2x110
olbuck
Wuz wondering if i could split a 220 drop cord into 2 110 drop cords, use the 220 ground as ground for each of the 110 & have two 110volt cords/lines? Why wouldn't it work?
Knowledge You Can Build On — Est. 1998
220-2x110
olbuck
Wuz wondering if i could split a 220 drop cord into 2 110 drop cords, use the 220 ground as ground for each of the 110 & have two 110volt cords/lines? Why wouldn't it work?
Don't
JL
It isn't code.
You will have no real protection in terms of fusing.
And I quote:
"Not safely or by code. 208/220/240V appliances (excluding foreign electronics and small appliances that are running through a voltage converter to a standard 120V outlet) are supposed to have a dedicated circuit that has properly sized wiring, with correct size breaker for the appliance rating. Say for instance you had a 10A and a 20A device connected - if the 10A device fails and shorts out, the breaker would not trip till it saw about 30A - could take a small welder-like load before it tripped out. Might make for glorious fireworks as the appliance shorted out but I don't think that would be worth the risk.
If you split two 208/220/240V appliances off one circuit, when only one is running the breaker will be grossly oversized for it - so not providing the protection you should have.
If you are talking splitting the circuit into two 110/120V outlets, then definitely no - in 208/220/240V services the single neutral (return) wire does not see full power because the two incoming "hot" leads are out of phase, meaning the average voltage in the neutral is less, or in some feed configurations even techincally zero (which is why in come areas 240V appliances are not required to have separate ground and neutral wires). By splitting the two hots into two separate 120V circuits, the single neutral would be serving as the return for both circuits at the same time which could not only overload it, but because it would be acting as the return on opposite "sides" of the 240V circuit, depending on what type of power phasing you have, could even act as a short circuit between the two "sides" in some cases, resulting in it acting as a "live" wire rather than a neutral."
NO
Mark Mandell - Gone Round In New Jersey
Asking for serious trouble.
If you really want two 110 circuits you have two options:
1. Replace the 220 breaker with a pair of 110's and run the new wire.
2. Depending on local code, use the 220 line (if it's a 4-wire) to feed a supplemental box ("sub-panel") in which you have two 110 breakers, 1 for each circuit, each rated at less than half of the 220 line's amperage. If, however, it's a 3-wire 220 line you're s.o.l. because you can't use the ground for a neutral and you need both for 110 circuits.
The idiot who owned my house before took a 110 branch off of a 220 line feeding one of the A/C compressors for an extra receptacle in the garage. Fortunately, our house inspector found the screw-up. Today, with our township requiring CofO inspections on all house sales, it would have cost the guy $500+ to get the whole house's wiring system checked and recertified.
Re: NO
Bill Howatt
If the existing double-pole breaker feeding the circuit is rated for the wiring size/receptacles and it is a 4-wire installation, that is, a neutral is present as well as the ground then it would be turned into a multiwire branch circuit.
I don't see why a sub-panel would have to be installed with de-rated breakers IF the existing breaker is a correct size. If the breaker is too big for the 120V circuit wire or receptacles such as over 15, 20A typically, then it needs to be replaced.
Since the circuit is supplying 220V right now it means the 2 hots are indeed out of phase and there is no way the neutral can get overloaded.
Each half of the circuit is protected by its "side" of the breaker and if one of the 2 resulting circuits is overloaded the tripped side will turn off the other side of the double-pole breaker as well and this is a requirement for safety.
However, to reiterate the warning, the circuit must have a neutral, the ground wire cannot be used as a neutral!
Bill
Question
Mark Mandell - Gone Round In New Jersey
Bill,
Wouldn't using the two hots in a 4-wire constitute having two circuits operating in a single conductor? Always thought that was very prohibited. Hence my sub panel solution.
Re: NO
John K Jordan
It would certainly work as far as the electrons are concerned. But my latest reading of the code, admittedly without studying it deeply, seemed to indicate that this was prohibited. Even the previously accepted method of coloring the ends of the wires appears to have been changed. But remember, if following code the local authority trumps everything - it would be painless to call and ask.
I personally don't like to even have two 110v receptacles near each other if fed from separate sides of the breaker box. Any issue would have you dealing with a 220v potential instead of 110v. That may sound like a silly concern but so be it.
JKJ
Re: 220-2x110
Barry Irby
There was a time, fifteen or twenty years ago that the multi-wire thing was all the rage.
They (you know who THEY are) started requiring more outlets and two circuits in the kitchen. Someone hit upon the idea of running four conductor wire and then splitting it into two separate three wire circuits in the kitchen. Created all kinds of problems, shared neutral, must have a common trip device, not two separate GFCI breakers, On and On.
Don't see it anymore. Don't do it.
Re: Question *LINK*
Bill Howatt
Hi Mark,
Being in Canada I had a look at some US sites before replying; our rules tend to be the same but you wouldn't want to take it for granted.
Have a look at the link below. The second answer quotes the NEC as to the definition.
Actually each hot is on its own breaker and the only shared aspect is the neutral and since the 2 hots are out of phase the current never exceeds the breaker rating.
Here some people legally wire their 220V shop circuits with a 220V receptacle and 2 120V receptacles off the same circuit all located in the same box. The double-breaker supplying the circuit must be of the correct amperage, 15 or 20 depending on the wire and receptacle.
Re: 220-2x110
Bill Howatt
This was one of those things that tended to be different in the US and Canada from what I saw.
In the US kitchen receptacles tended to be 20A with #12 wire on a conventional single circuit. In Canada all kitchen counter receptacles were 15A multiwire - 2 hots, 1 neutral, 1 ground on a double-pole breaker. This did have the advantage that you could plug 2 high-wattage appliances into the same duplex receptacle without tripping anything. These circuits are dedicated to a single duplex receptacle so there was not an issue of things getting confused downstream.
This has now changed because of the requirement of GFCI circuits within 1 meter of the sink - implementing GFCI is virutally impossible on a multiwire circuit although I imagine it can be done if you throw enough money at it. Other than the GFCI issue multiwire works fine but I'll admit if I were building a new house I'd avoid it since you have to be more aware of how things are wired when you may want to make changes down the road.
Bill
Kitchen,
Mark Mandell - Gone Round In New Jersey
bath, garage, and outside circuits here have to GFCI so take a lot of wiring out of the multiwire branch situation.
GFCI applies here as well for those circuits,
Might Be Kosher
Mark Mandell - Gone Round In New Jersey
but in my view is it's a real opportunity to get lit up "Eat At Joe's" and earn the nickname of "Sparky."
Thanks, but I'll stay with the one circuit/one line/one breaker school.
I remember that now...
John in NM
You can share the common if the two hots are 180 degrees opposed in phase. I too prefer the 1 hot + 1 common arrangement, but I recall you can do it the other way too.
Though in fairness...
John in NM
That was the 2004 International Residential Code - it may well have been changed by now.
Re: 220-2x110
Jay Lombardo
Electrician for 43 years here. Using common neutral for multiple circuits was and still is legal. Residential 120-240 3 wire (Black Red White) network and Commercial 4 wire 3 phase (Black Red Blue White ) network is how almost all wiring was done unless specifically specked otherwise. Each wire was connected to it's own single pole breaker on separate phases. 3 Phase network was 3 110V circuits on a single neutral, and single phase was 2 120V circuits on a single neutral. We use all metal conduit around here so the ground was provided by the conduit. Recent changes to the code has made this type of wiring not as popular. Almost every circuit in residential now is either Ground Fault or Arc-Fault and they require their own neutral. New requirements to lock the breakers together so if one circuit blows the other circuits on the network will also de-energize. If you do use a network you have to identify the neutral for it throughout the wiring path. It is much easier now to just run a bigger pipe and have each circuit have its own neutral. There is nothing wrong and it's perfectly safe to use a common neutral wiring method unless some handy dandy do it youselfer opens a box with a couple neutrals in it and wires a couple of circuits from the same phase on to a neutral, thus creating an unbalanced load and turning the wire into a heating element!! It is still critical to keep the circuits identified throughout the run. Started using white wires with colored tracers the last few years I worked to keep everything straight. Sorry for the long winded response.
Re: 220-2x110
John K Jordan
Jay,
You can post many very long message as far as I'm concerned - good information.
I like the "turning the wire into a heating element" statement. 
Reminds me of working on a building at a kids camp in the middle of Mexico. I found a 50 amp breaker feeding a water heater on the other end of a long building with a 14 gauge wire draped across the ceiling joists in the attic. With no electrical supplies within a half day's drive I couldn't do a thing. It was several years before I could get back with supplies. The building was still there - yea!
JKJ
I Had to Cheat
Mark Mandell - Gone Round In New Jersey
When we put a secondary frig out on the garage, I learned that it wouldn't run on the GFCI line I had run for power to tools. Since I had used the first device in the line as the GFCI breaker, I had to move it to the next position downstream and then put in a singleton receptacle to run the frig. If I had used a GCFI breaker in the service panel I would have had more work to do. If we sell the house, I have a fair amount of "deconstructing" to do.