circuit needed for Hammer A3-31
Howard Pollack
I have a Hammer A3-31 on order. Can someone tell me what sort of circuit I need to run that machine? Thanks.
-Howard
Knowledge You Can Build On — Est. 1998
circuit needed for Hammer A3-31
Howard Pollack
I have a Hammer A3-31 on order. Can someone tell me what sort of circuit I need to run that machine? Thanks.
-Howard
here's one answer
Bruce, a MN Galoot
http://festoolownersgroup.com/other-tools-accessories/what-size-circuit-hammer-a3-31-jointerplaner-or-n4400-bandsaw-w-4hp-motor/
Re: circuit needed for Hammer A3-31
Derek Cohen (in Perth, Australia)
I have the A3-31 with spiral head. This runs very happily on a 15 amp circuit. The original requirements were for a 20 amp circuit, however this was written up in the days of pre-spiral heads. The spiral heads appear to draw less current.
My machine was installed by a professional electrician, who took all sorts of readings. I also have a Hammer N4400 bandsaw, also 4 hp, and this uses a 20 amp circuit.
Regards from Perth
Derek
look on the motor
Bill Tindall, E.Tn.
The motor plate will provide voltage and current data. A 4 HP motor will require a 220 circuit, 15 to 20 amp ( a 5 HP motor I checked was rated at 22 amps). Don't starve a motor for current capacity or you will burn it up. Son-in-law recently did that experiment. Motors are expensive. Unless you are running a long line just put in a 30 amp breaker, 10 ga wire and you can run anything in the future. Cost difference between running 12 ga wire and 10 is not much.
Re: circuit needed for Hammer A3-31
John in NM
I tend to like bigger circuits for future capacity. But just remember that the breaker protects the circuit itself and the machine should have its own overcurrent protection -- often that is the large push button motor contactor.
Thanks everyone+ additional question
Howard Pollack
Thanks for the help. I called Felder and their technician called for a 30 amp circuit. Is there any disadvantage to this?
-Howard
Re: Thanks everyone+ additional question
Bill Tindall, E.Tn.
It will cost you 10 ga wire instead of 12 ga. Not a huge price difference.
Re: Thanks everyone+ additional question
Bruce, a MN Galoot
My wiring inspector also said there can be nothing else, no branches, on that 30 amp circuit. They usually require special plugs, too. Or at least that's the way it is in MN.
Re: Thanks everyone+ additional question
Keith Newton
Howard, it sounds like this may be new to you, and you don't give us enough information to tell you everything you should know, like whether you will need to run 120 volts or 220 volts, and if there is a cord both can be rated for 30 amps.
Besides getting the information off the motor, if there is cord with a plug on it, you need to match the receptacle to that configuration. If you plan to hard wire right into the switch, you don't need that expense.
Most motors of this size can run on either 120 or 240 volts, depending on how the wires are arranged in the motor. This information will usually be on the motor plate, or under the cover for the wiring. You would be screwing up if you need 240 volts, but only ran a 120 v circuit, so look closely at that plate, then see how many amps are required for each configuration.
Also, you might look in your breaker box to see if there is an opening for another 240 v breaker, or even another120v.
If the tool already has a cord with a plug, you should be safe to just match what that. It will tell somewhere on the plug in small print.
Re: Thanks everyone+ additional question
Bill Tindall, E.Tn.
You can't run a 4 HP motor on 110, at least not for long under load.
Re: circuit needed for Hammer A3-31
Rum
I'm running mine (pre-spiral) on a 30a 240v circuit. No regrets, the extra cost of the 10g was minimal over 12g and I know its good enough.
The other thing to note is that the pigtail supplied is very very short (mine was under 24"). I built a "whip" (cough extension cord.. but a dedicated one..) out of SJOO 10/3 wire with L6-30P/L6-30R plugs on the ends and stuck a L6-30P on the end of the pigtail. I used a L6-30R outlet on the wall.
Some folks will argue whether locking or not locking outlets. I don't claim to be smart enough to know one way or the other but like the positive click on higher amp stuff.
Talk to your electrician, there might be local codes on some of this that change the install.
Re: Thanks everyone+ additional question
Johanna Johanson
All my large tools are on 30 amp circuits - that was my electrician's recommendation.