O.T. Electrical Question...

Posts

O.T. Electrical Question...

#1

O.T. Electrical Question...

Darita

You guys know everything here, so thought I'd ask...Just got an Eastwood 175 Mig that uses a Nema 6-50 plug. The machine states it requires a 30A circuit to operate. I have 220 30A in my shop, but use NEMA L6 30 250V twist loc. Will it be OK if I make up a short jumper to go female NEMA 6-50R to NEMA L6-30 twist male. Hope I made that clear...

Re: O.T. Electrical Question...

#2

Re: O.T. Electrical Question...

John K Jordan

All my 220v welders and the plasma cutter came with the 50 amp plug.

I'd think you could

- run a new circuit,

- make an adapter,

- replace the 50 amp plug on the cord with what you have in your wall,

- save the factory cord and make a new cord with the desired plug, or

- add a 50 amp wall receptacle to the 30 amp circuit.

I don't know about the code for the last one but it would work but the guy who bought your place some day might plug in something that actually draws 50 amps and pop the breaker.

Or if you have the capacity in your panel maybe add a 50 amp breaker and run new wire to where you want the welder. This could give you the receptacle to plug in the existing welder, the new plasma cutter you'll buy next week, AND that big TIG welder your brother in law is going to get you for Christmas.

I would personally prefer to leave the factory plug on the welder - if it's molded on it might be more reliable in the long run than one you replaced it with. And what if you took the welder somewhere that had the 50 amp receptacle? I'd probably either replace the cord or make an adapter. Or use this opportunity to make up a long adapter extension cord so you could use the welder out in the driveway.

JKJ

Re: O.T. Electrical Question...

#3

Re: O.T. Electrical Question...

Grant Smith

Hi Darita,

I will speak in general terms, then get to your particular question:

The key thing to remember is that the outlet on the wall, and the wire between it and the supply panel must by code be protected by a circuit breaker or fuse that will trip before the wire or outlet is overloaded. This means you can't (legally per codes) install a larger outlet on the wire than the wire is rated for in that situation. You didn't ask that though, so this may or may not be a useful statement to you. I think it is worth mentioning so other folks reading this can get their heads around the thinking on such things.

You can, however, make the adapter you describe and use it for the welder you describe. The circuit breaker should protect the outlet and in wall wire if it was installed properly. Apparently, the welder maker decided to use an oversize plug for their welder, perhaps to standardize their line, or perhaps that particular plug is common in similarly sized welders.

You could also just change out the plug on the welder to match the outlet. Both would be OK. Just know that if you find that the breaker trips often (It shouldn't, if the manufacturers info is correct), you may need to run larger wire in the wall than what was likely there before upgrading the outlet. This assumes the electrician who installed the wall plug used the minimum sized wire necessary for the installed outlet, which may or may not be the case. I'd talk more about wire size, but there are variables such as distance of run, conduit, and wire type that figure in, so I will leave it at "It's complicated".

Enjoy the new welder, and get yourself a 4" or 4.5" angle grinder to cut parts, clean surfaces of rust, and grind away mistakes. If you buy one, make sure to get plenty of cutoff wheels, grinding wheels, and maybe a wire cup brush to have on hand. I do not recommend wheels of other than those made by major tool makers. The store branded or Harbor Fright type wheels will not likely perform as well. Get yourself a face shield in addition to the welding helmet and thank me later. Wear light leather gloves when grinding, and don't grind or weld around your woodworking area without doing a thorough cleanup and then staying in the shop for a few hours afterward to guard against fire.

And make sure to have a fire extinguisher, recommend at least a ten pound extinguisher.

Regards,

Grant in Iowa

Re: O.T. Electrical Question...

#4

One more suggestion

Grant Smith

Since my welder is in my wood shop too, I made up a long cord of suitable amperage capacity to enable me to take the welder outside, or to the other side of the shop as necessary. It is best to keep welding and woodworking shops separate.

The long cord also allows me to weld larger items outside such as my log trailer, etc.

I was just thinking that instead of making a short pigtail, you might consider making one longer to meet other situations and needs.

Regards,

Grant in Iowa

Re: O.T. Electrical Question...

#5

Re: O.T. Electrical Question...

Bill Howatt

That will be just fine since your circuit is the recommended one and you are not using any components that are not rated for at least 30A.

The manufacturer should know the requirements so you are good. Besides it is unlikely that you will often be using the machine at full power plus welder loads are quite intermittent (breaker cools down) and actual welding time is relatively short. Breakers also don't trip instantly just over their rated value and will supply more current for several seconds or more. The actual time depends on how much over the rated value you are. My Miller stick is supposed to have something like a 60A circuit but mine is on a 40A breaker. I've run the Miller flat out for 10-15 second bursts and have never tripped it.

Bill

Re: O.T. Electrical Question...

#6

Re: O.T. Electrical Question...

Jay Lombardo

Short answer, yes you are fine to make a pigtail adapter. Make sure you use #10 AWG wire when you make it. A short piece of 10/3 SO cord will work nicely with whatever mating connectors necessary.

Re: O.T. Electrical Question...

#7

Re: O.T. Electrical Question...

Darita

Thanks for the advice. I ended up making the jumper as I first stated, but made it about 10 ft. long. Hope it works OK...I mean, hope I work OK.

Fire thing has me a bit paranoid, so I'll try to be as careful as I can. I do have an area outside, beside the garage, but it would take a longer run and I don't know if it would be wise to run a 20ft extension for this machine. Thanks all very much and wish me luck!

Re: O.T. Electrical Question...

#8

Big extension cord

John K Jordan

>>> I don't know if it would be wise to run a 20ft extension for this machine.

I believe you can run a longer extension if you size the wire appropriately. There are wire size calculators on-line that give the voltage drop for a given wire size for a given length, for example the first one I see with google:

http://wiresizecalculator.net/

From that it looks like 20' at 30 amps with a 1% voltage drop can still use #10 copper, but I would probably use #8.

I made a 20' extension cord for my welders, sized to pull 50 amps. Even with the AC/DC stick welder I have no problem. I can't remember the wire gauge I used, either #8 or #6 gauge stranded cable from the electrical supply house. This is thick cable but very flexible.

I used the extension cord to stick weld the rebar for the vehicle bay end of my shop, over 700 connections. 1' spacing, 6" concrete, good and solid!


JKJ