OT-Electrical problem
Clint Searl
Returned from a three week absence to find the 120v/15Amp breaker serving the septic leach field pump tripped. Disconnected the pump and tried to reset the breaker. It tripped immediately. The only other things on the line are a TV and cable box and a pull chain light. With everything disconnected, the breaker cannot be reset. Assuming that I have found and removed everything on that line, is it possible that the breaker has failed? Note: it is the original breaker, and has fed the pump, which may pull close to 15 Amps on starting, for almost 30 years.