Posts

OT-Electrical problem

#1

Clint Searl

OT-Electrical problem

Clint Searl

Returned from a three week absence to find the 120v/15Amp breaker serving the septic leach field pump tripped. Disconnected the pump and tried to reset the breaker. It tripped immediately. The only other things on the line are a TV and cable box and a pull chain light. With everything disconnected, the breaker cannot be reset. Assuming that I have found and removed everything on that line, is it possible that the breaker has failed? Note: it is the original breaker, and has fed the pump, which may pull close to 15 Amps on starting, for almost 30 years.

Re: OT-Electrical problem

#2

Re: OT-Electrical problem

John Veerkamp

breakers do fail. 30 years is past the average life. Replace it.

Re: OT-Electrical problem

#3

Re: OT-Electrical problem

Barry Irby

One possibility is that you have a short somewhere in the circuit. Hard to imagine it happened while you were away but it could have. Mouse damage, whatever. If you had a tester you could check for continuity.

Its also possible the breaker has failed. What happens if you remove the wire from the breaker? If it won't reset with nothing hooked to it it has failed. You could test that by moving another breaker into that location momentarily and see if it works. (Or just move the wire to another breaker.) Or you could just by another breaker if you are not snowed in like many of us.

And of course you could use an electrician.

Re: OT-Electrical problem

#4

Re: OT-Electrical problem

Ralph Lipeles

Clint,

Can you disconnect all outputs from the circuit breaker and see if it still trips with nothing connected? If it does not, then connect the outputs one by one to see when the breaker trips.

Re: OT-Electrical problem

#5

Underground wire?

Dick Coers

Do you have underground wire to that pump? That's a likely culprit.

Re: OT-Electrical problem

#6

Clint Searl

Re: OT-Electrical problem

Clint Searl

Thanks for the responses. I was hoping not to futz with the panel, but it looks like it's either that or an electrician.

Re: OT-Electrical problem

#7

Full off?

Gary Smyth

This may be too simple, but are you certain that you threw the breaker to a full off position before turning it back? Recently had a new breaker that I thought would not reset. Much frustration. After testing adjacent breakers it turns out I had to throw the switch to the full extent (with some effort) of its limits on both left and right before it would reset. It was a simple error based on not being familiar with the breaker.

Re: OT-Electrical problem

#8

Re: Full off?

Jay Lombardo

Over 40 years an electrician and I can't begin to tell you how many times what Gary described was the problem. Most people are used to turning a breaker on and off, not resetting them. Resetting requires pushing it ALL the way off, then back on. Resetting the breaker still doesn't solve the problem though, they don't trip for nothing (except for those miserable arc faults!). Remove the wire from the breaker in the panel, if it still won't reset, it's the breaker. In my experience this is very rare except for the old Pushmatic breakers. If that's what you have then call an electrician to replace your panel and get rid of them, they are dangerous. As others have mentioned the likely suspect is probably the underground.

Good Luck