OT-AC Unit

Posts

OT-AC Unit

#1

OT-AC Unit

mdclor

We moved into a 13 year old house in Virginia 2 months ago. We set the AC unit to 74* and it held that temp fine until yesterday when the temp got up to 77* and this afternoon it got to 78*. We were in the low 90s each day and it has been warmer previously. Does this behavior suggest that the AC unit may be dying or is there some other less drastic potential explanation? Thanks.

Re: OT-AC Unit

#2

Re: OT-AC Unit

David Yoho

Sounds like it would be worth having someone have a look at it. Could be several things causing that. Have you noticed the unit running long? See any frost on any of the lines? Filters clean? Thermostat working right? Coils clean?

Re: OT-AC Unit

#3

Re: OT-AC Unit

Keith Newton

the first things to try yourself, is to change filters.

Buy some coil cleaner to spray on the outside unite, then blast it out from the inside out. Be sure to turn it off first, of course. If that doesn't help, there may be a leak, and you may need to call for service to add some freon.

Re: OT-AC Unit

#4

Re: OT-AC Unit

R. Payne

The outside unit may be dirty, the filters may be dirty, could be low on coolant. If it's low ob coolant and it's more than a few years old, it may prove cheaper to get a new AC than recharge this one.

Re: OT-AC Unit

#5

Re: OT-AC Unit

Dick Coers

Service technician time, and as mentioned, probably new unit time as well. Talk to the tech for some options, 1) If I buy a new unit, would you deduct today's service call?. 2) Will you keep the old unit charged until the new unit is installed for no additional charge? 3) What rebates are the utility company offering.

We put in a new unit last year, furnace and AC. Maybe because we bought the whole deal, but then subtracted the first service call, recharged the old unit a second time before they could get out and install the new equipment. We bought the highest efficiency unit we could. The outside unit is much bigger than the old one, but the fan turns much slower, so is quieter. We went with Carrier, very happy with it.

Re: OT-AC Unit

#6

Re: OT-AC Unit

mdclor

Thanks for all the quick replies.

1. It seems to run most of the time.

2. I put a new filter in July 1.

3. I haven't seen any frost.

4. The thermostat seems to be working properly, but I'm no expert.

5. I will need to turn it off and check the coils this AM.

6. The outside doesn't appear to be dirty, but I will look at it more closely.

7. Three excellent suggestions and appreciated info.

Re: OT-AC Unit

#7

Re: OT-AC Unit

John K Jordan

Years ago my sister had an old unit that quit cooling correctly. I foind loose set screws causing the fan to slip.

Re: OT-AC Unit

#8

A few more checks

Lee Schierer in McKean, PA

Turn the unit off and check the coils behind the filter. If they are covered in ice, you are likely low on refrigerant. Then check the fan belt for condition and proper tension if it has one.

Lee

Re: OT-AC Unit

#9

Re: OT-AC Unit

Bill Turpin in WNC mountains

Is the larger diameter line at the outside unit "sweating"? Pull the insulation back a little to check. If not it is probably low on charge. If it is iced, probably low or filter is stopped up. All the other advice is spot on. Temperature of smaller line should be thirty degrees above outside temperature, warm but not burning hot. Be careful checking this!

Dirty filters KILL 90% of all HVAC compressor failures. The filter needs to be changed every thirty days, or more often, unless you have a very clean house. Are there kids, pets, workshop, husbands or other sources of DIRT? Do not buy the cheapest filters at Wally World. If you can read a book thru it, do not buy it. Would you rather spend a couple of bucks a month or buy compressors @ $1000? Every month when you write your mortgage check change the filter.

Re: OT-AC Unit

#10

Re: OT-AC Unit

Ralph Lipeles

I had a problem with my A/C unit a few years ago where the coils were freezing up. The tech said it happened because the coils were not clean. He sprayed a foamy cleaner on them and let it sit for 15 minutes. After that it worked good. The A/C company had an outrageous pricing policy which included a diagnostic charge, a repair determination and the actual repair. My bill was $165. He was at my house for only 1/2 hour. I now buy a can of the cleaner at Home Depot for $6 and spray the coils myself every year.

Re: OT-AC Unit

#11

Re: OT-AC Unit

mdclor

The AC guy looked at it this afternoon and everything checked out okay. He surmised that my issue might have been caused by the shop construction workers leaving the door open. He suggested changing the filter every couple days during construction and daily after drywall sanding, because the drywall dust will kill the condenser coil faster than anything and can't be cleaned off once it hardens to a concrete like consistency. Again, I greatly appreciate all the helpful suggestions.

Re: OT-AC Unit

#12

Uh, Merle...

David Yoho

You never mentioned the open door dude! That sounds reasonable though. Glad there wasn't anything really wrong with the system.

Re: OT-AC Unit

#13

Mea culpa

mdclor

That just shows my ignorance, I didn't realize that an open door in the basement would affect the temperature on the main level. I always keep the basement door closed.

Re: OT-AC Unit

#14

Re: OT-AC Unit

Gary Bindel

On some condenser units, the coil is made up of two layers. The outside can appear clean, but between the coils will be loaded up blocking airflow. To clean this type, you need to take off the top and sides and remove the screws holding the two halves together. Then gently spread the halves apart and using a hose, clean the inner surfaces. Always direct the spray parallel with the fins.