Why would there be a 1/4 inch hole in the pipe leading from sump pump?

My daughter and SIL recently bought a townhouse and the home inspection report said the sump pump was not working/had to be replaced. (It's in a somewhat awkward spot that will be my SIL's workshop, so I'm not sure how hard the inspector looked at it.)

The sump pump (located in a standard pit) is directly plumbed into a 1.5 inch PVC pipe that runs straight up (8 feet or so) to the top of the basement wall and then turns and exits the building.

When I poured water into the pit, I found the pump ran but...and this is the curious (at least to me) part...someone had drilled or punched a 1/4 inch hole in the vertical run of the PVC pipe just above the pump, but still in the pit. So, when the pump ran, water squirted out of the hole in the PVC pipe and then continued to leak out after the pump stopped running (from the column of water in the pipe that's below the check valve). So, while most of the water in the pit was pumped out, some drained back and the pump had to run longer.

My set up at home is nearly the same and I don't have such a hole, so I replaced the PVC pipe at my daughters.

My question is, did the hole in the PVC pipe have a purpose (such as releasing pressure)? Should it have been there? And did I screw up by replacing the PVC pipe and not including the hole?

Re: OT sump pump plumbing question

#2

Re: OT sump pump plumbing question

Barry Irby

I don't have a definitive answer or even one based on the Code, but I saw the set up you are talking about just yesterday. It was in an exterior sump pump set up to keep an outdoor pit dry because there were controls in the hole for a sprinkler system. The explanation for the hole was that it allowed the water to drain out of the vertical pipe preventing it from freezing. This pump discharged into the curb, not into the plumbing system. The hole did spray water while the ump was running and water drooled out of it when the system cut off. The volume of water in the pipe was small compared to the sump so there would not be a tremendous amount of recirculating.

As a home inspector I do not recall ever seeing this set up on a system inside a house where freezing was no danger. A check Valve would reduce the re-circulation of the water, but might allow the water in the vertical column to freeze.

Re: OT sump pump plumbing question

#3

Re: OT sump pump plumbing question

Jim in N. Va

Thanks Barry.You are right that there is no freeze danger so the hole is still a mystery. But glad to know that I haven't overlooked something obvious.

Re: OT sump pump plumbing question

#4

Re: OT sump pump plumbing question

john Veerkamp

siphon break

Re: OT sump pump plumbing question

#5

Re: OT sump pump plumbing question

Bill Turpin in WNC mountains

Check out some sump pump installation instructions. They will tell you to drill that hole. If the heat fails, or if their is an extended power outage it could freeze in a heated basement.

Re: OT sump pump plumbing question

#6

Re: OT sump pump plumbing question

Jerry Nicholson

Must sump pumps I have installed came with instructions that said drill the hole but not a 1/4 inch hole. I usually drill a 1/8 inch hole slanted upwards so the water will squirt down.

Jerry

Re: OT sump pump plumbing question

#7

Re: OT sump pump plumbing question

Jim in N. Va

Is it just to drain in case of a freeze? Or something else?

Re: OT sump pump plumbing question

#8

Re: OT sump pump plumbing question

Jerry Nicholson

I think it is to allow the pump to start under "no load" conditions. If the pump tries to start against a column of water, the water between the pump and the check valve, it might not have enough torque and might stall. These are AC motors and have limited starting torque. Of course after the pump has set for a few minutes it should drain down anyway.

Jerry