I am changing over from LP to natural gas on my shop furnace. I changed out the orifices and the spring in the regulator. I now need to set the water column inches. Not having a gauge I see via YouTube that you can " clock" a meter to verify the BTU's. Has anyone here done it?I assume I can then adjust the regulator screw to adjust the BTU's.
About 20 years ago in our previous house we had a gas water heater changed over to natural gas. The gas company came out and did it for us. Maybe giving your provider a call to do this would be the way to go.
Can't speak for other companies, but the natural gas supplier I work for would check your pressure for free. It isn't something I do every week, but I have done it more times than I can remember. Unless there is a regulator somewhere in the system that is downstream of the meter, pressure has to be adjusted upstream of the meter. My company prefers that the customer leaves it to us.