Moved into the cottage, basement is very wet from seasonal condensation. The breakers, which are only a few years old, do not show any tripped circuits but a large run is not working. Mixture of lights and outlets. Can moisture cause this kind of malfunction. Will it likely correct itself as it dries out.
What is the best way to narrow down the circuit that isn't working. I will try to just put things on and off, but so far haven't gotten into it, waiting for it to dry. When I get the right circuit. Should I just go ahead and replace the breaker?
Just a caution to make sure that everything is dry, circuit panel etc before making any adjustments. if you plan to switch the breakers on and off use a radio plugged to know when you get the right breaker.
Sounds like a GFCI in the circuit has tripped. Electricity doesn't stop flowing because the wire may be damp. You have something else "wrong." Look at all of the duplex outlets in the effected area. You may find one that has 2 buttons in the center with a telltale that's not lit. That will be a GFCI which will trip in the presence of condensation in the device. Remove the trim cover to allow more air circulation into the outlet box. If you find the culprit, you will also need to isolate the circuit at the main service panel and then pull and inspect (and replace) the GFCI for corrosion.
Diagnosing electrical problems at a distance is tough. I like Mark's Answer. Don't know how old the cabin is or the age f the wiring, but if it has a GFCI that's a good thing to check. They are usually for Kitchens, bathrooms, Basements, and exterior outlets. Places that might actually combine water and electricity.
You could check the breakers themselves if you have a simple tester. Anything that will register the presence of electricity will do. There are "sniffers" that can do this without touch anything. About the size of a Magic Marker with a plastic tip. You hold it near the terminal and if it "hot" the device will flash and beep. Or you could use a glow plug type that has two leads. Touch one to the terminal on the breaker and one to the ground in the panel and if its hot the little light in it will glow. You could make one of these with a lamp or bulb and socket if you feel comfortable doing it. Of course any multimeter will do this as well.
The first thing to do might be to reset all the breakers just to see if one has tripped internally without showing it much or at all on the handle. Turn them off and firmly reset them. Might not have anything to do with the condensation.
Also, be careful around the panel. Rarely, but sometimes we find the box or shell of the panel electrified. Dangerous in a any situation, but especially in a wet basement. The old school way to test it is to rap your knuckles on the panel to test for a tingle. The sniffer mentioned above is a safer alternative.
If all the breakers are good and you don't have a GFCI, try to find the first outlet or device in the string and start checking it for an "open", a disconnected hot wire. At least half of these I have found were not obvious. No dangling wire. Just remade the connections and for no apparent reason it went back to work.
Great advice given! Don't be afraid to call a recommended electrician if necessary. It can be very difficult to determine which outlet or device is first in a run unless the wiring can be followed. No guarantee the work was done correctly. Tester is more expensive but I like the one with two probes that "wiggles" or vibrates with current. More expensive but more definitive and useful, in my opinion.
If basement is damp, GFCI protection throughout the basement would be something to strongly consider.
You say you have both outlets and lights on the same circuit. Normally, you have them on separate circuits, so you don't have a situation that is common. You may have an outlet that is fried, or a loose wire at the connection. This would cause everything down-line to not work. I would recommend a dehumidifier for your basement to handle the condensation.
You're more likely to trip the breaker with a device plugged into an outlet than by turning on too many lights; and having the room suddenly go dark because, say, for instance, you plugged in two electric heaters on the same circuit as the refrigerator* is not so much fun. When I rewired our house, I made sure to isolate the lights from the outlets on separate circuits.
*Subsequently, I ran a separate circuit for the fridge; it makes for a much calmer wife not to have the fridge go dark during Thanksgiving meal preparations.
Some oaks took out our power and phone, so we are dead. One advantage is that there really isn't any risk of electrocution since the panel and shut off are not energized in any way, until the cable is fixed. Would this present any ways to run test without risk of electrocution. It is so wet that I wouldn't fully trust a shut off even. We had the system re-upped last year with new panel and breakers, and I replaced all recepticals above the basement. We had an electrician for some of this, who tested for hot wires by gripping the wire ends!.
None of the wiring was 3 wire, and so the decision was made to route the grounds to the neutrals. I don't own the place so my concerns were not determinative. I also suggested moving the panel out of the shower like area it sits in., but that would have meant getting the entry shut down, which would have meant getting a permit, and you can imagine where the quality thinking went from there.
I have most of the electrical testers referred to, and I guess I could continuity test the system while it is dead.
I have personally had the experience of having a freezer malfunction. I wired homes and commercial for many years. When possible I always wire a well used light to the circuit used for a freezer. Many freezers are kept in Basements in this area, when this is done and I wire, I wire the basement lights to the freezer circuit. If upstairs I try to wire the kitchen light to the freezer circuit. It is far better to have to use a flashlight to access the breaker box than to open a non-operating freezer after a week or so, and haul out several hundred dollars worth of groceries! I have had a few people call me and thank me over the years as they found the freezer not working BEFORE everything thawed..
In 2005 there was an exception to that in the IRC, but I've forgotten what it was, and I've loaned that book out, never to be seen again.
Of course local codes are often more strict than the IRC - for example here in NM where the soil is dry, we have to run a ground wire to any outbuildings powered from the primary service. The IRC does not require that ground wire if there are no other wires (such as telephone) also connecting the two buildings.
Ironically, the dry soil does not keep us from having to vent crawl spaces as if it were Florida. Common sense only goes so deep in the bureaucratic mind.
My cousin was in Saudi Arabia with the S.C. Air National Guard for Desert Storm. He told some pretty tall tales of the troubles they had getting grounds in dry soil for the static sticks to drain static off their F-16s.
I was assigned to Riyadh in '97-'98 (USAF). We built a small office park of modular buildings and grounding problematic. The solution was to dig a hole fifteen feet deep (this took three guys -- one working a jack hammer to bust up the rock hard soil; one with a shovel, clearing out the loose soil; and the last guy had a bucket on a rope, to haul out the soil when the hole bacame too deep for the guy with the shovel), then pound a twenty foot section of re-bar into the bottom of the hole, for a total depth of 35 feet. Then the grounding problem was solved. Took a couple of days to dig the hole and a couple more to pound in the re-bar.