Is this a 220 volt extension cord? and would it work in my dryer plug? http://www.amazon.com/gp/product/B002FCP8YE/ref=noref?ie=UTF8&psc=1&s=hi
Knowledge You Can Build On — Est. 1998
220 volt extension cord
Charles Jackson III
Is this a 220 volt extension cord? and would it work in my dryer plug? http://www.amazon.com/gp/product/B002FCP8YE/ref=noref?ie=UTF8&psc=1&s=hi
No.
Jason Roehl in Lafayette, IN
That's a 120V/20A cord, which means it is 10-ga. wire. You could certainly cut the ends off and put on new 240V/20A-configured plugs, but at that point, you're probably better off buying bulk extension cord by the foot and the appropriate plugs.
Jason
Re: No.
Charles Jackson III
Where do find a 220 volt extension cord from? Look for one to run a 3hp Unisaw off of.
I make them when needed....
John in NM
Couple really good reasons to do it that way.
First, you can make one just the right length - why buy extra 10 AWG wire for a cord going to what is quite likely a stationary machine.
Second, a lot of cords for sale these days have an outer jacket made of pvc or something similar. I find them stiff and annoying, especially on cold mornings.
The are easy to make, and you can use a good quality cable with a nice rubber jacket.... They coil beautifully 
Re: 220 volt extension cord
Don Stephan
Memory suggests there is a wider range of 220/240V plugs than with 110/120V, for different amperage ranges. This might be one reason there are few ready made cords. It's not hard to make extension cords, but it's essential to match the amperage draw of the applicance (Unisaw) with the amperage carrying capacity of the extension cord, plug, dryer plug, wire from the circuit panel to the dryer plug, and the breaker in the circuit panel.
Re: 220 volt extension cord
JL
As others have said - no, it isn't.
What sort of distance are you trying to run a cord? If it is anything greater than 20' or so - you'll need something a LOT beefier than 10 gauge wire for your 3 hp Unisaw.
If you are talking about running from the drier, across the yard and into your shop - DON'T DO IT. If you are talking about running it from a drier plug in your shop to a machine in your shop - then go ahead.
I just went to Home Depot and found some nice flexible jacketed 10 gauge cable. I put a plug on one side L6-30 to fit the receptacle that I put on the wall and wired it directly into my saw.
Re: 220 volt extension cord
Charles Jackson III
I figure it was a bad idea!
Re: 220 volt extension cord
Charles Jackson III
A 100 ft JL.
Re: 220 volt extension cord
JL
If it is 100' - get an electrician to run a line from your service out to the shop. The current drop on any commercially available cable would be too much - not too mention it would cost quite a bit.
Ideally you would have a buried conduit or line and put a 60 amp or so box out in your shop.
Re: 220 volt extension cord
Charles Jackson III
I would if my shop was built right.
Bad Shop is not justification for bad wiring.
Re: 220 volt extension cord
Rick Christopherson
There is nothing wrong with having a 240 volt extension cord, but because they are not in common demand, it will be harder to locate.
Your best solution is to buy a standard 120 volt extension cord in the length and gauge (wire size) that you need. Cut the ends off and install new 240 volt ends. Surprisingly, it is less expensive to buy a complete extension cord than it is to buy the equivalent wire by the foot.
For a 3hp unisaw, you are fine with a 12 gauge cord for a reasonable length. Over 50 feet (definitely at 100 feet) and you may want to use a 10 gauge cord. The majority of the voltage drop on an extension cord occurs at the plugs because many of them are rather cheap, and it is just a compression fitting to the male plug. When you buy your own ends, this is less of an issue because they are typically of a higher quality to begin with.
Your Unisaw probably came with a NEMA 6-15 plug installed on it. So your extension cord can have either a NEMA 6-15 or 6-20 female cord cap. Your dryer is either a 10-30 or 14-30 receptacle. The 14-30 would be better because it contains a ground. The 10-30 is ungrounded and uses the neutral as a chassis ground.
NEMA 6-15
NEMA 6-20
NEMA 10-30
NEMA 14-30
Good post Rick
A suggestion
Jason Waters
My 3 hp Unisaw saw is about 6-8 feet from the box on the wall. I made up a receptacle with flex rubber 10 gauge from the wall (using a nice right angle plug so the cable drops straight down), and mounted it under the saw. That way I can unplug the saw to change blades, etc. Otherwise, I had to walk all the way around the saw to unplug it (my setup is confined). Also, it keeps me from having to bend down and and find an extension cord plug to plug it. It's been real convienent. I should take a pic.
Jason
Re: A suggestion
Charles Jackson III
Please do! I got to find a use 3hp motor for my Unisaw to replace the original 3hp motor I gave away.
Motors
John in NM
I got a replacement motor from Saw Center, along with belts and pulleys as my old motor was a slower speed repulsion induction motor. Not cheap, but it only required minor tweaking to install in the old saw.
Re: 220 volt extension cord *LINK*
Galen Vetterick
You might try looking at a welding supply shop. Our shop usually just made one up as we needed rather than purchase ready made, We had a whole spool of wire so it made it a lot cheaper.
http://www.harrisweldingsupplies.com/220-volt-extension-cords.aspx
Re: 220 volt extension cord
bud
I used a four wire 10 gague generator cord to my 3HP unisaw - got the cord on closeout at Lowes.
My real comment is that the factory cord that came with the saw has only 14 gague wire for a motor rated at 20 amps.
Look around Generators @ H.D. *LINK*
John M in Mid Mich
You can get a ready-made 220V extension cord in the generator section of Home Depot, and probably the other big boxes. Also online, see link.
220V cords at HD
By one at an RV Center I forgot I got one there.
Not doubting the 240 V cord - just the length
JL
I don't think running a 100' extension cord from the drier plug in the house to the shop is the right way to go.
He should have a 60 amp (or more) box in the shop. If he wants to run a cord there, fine - but not one across the yard.
IMO - that isn't the best thing to do. He'll always need power in his shop. Currently he is running extension cords for all of his tools from the house.
Re: Not doubting the 240 V cord - just the length
Rick Christopherson
In my experience, the people that routinely bring up voltage drop discussions are also the ones that have never completed a voltage drop calculation. Your previous posting supports that because it makes no difference whether it is flexible cord or hard wiring. The voltage drop for a given conductor gauge, length, and actual amperage load will be the same. That is why I pointed out that the cord ends are the more critical aspect.
While it may be true that the OP would be better served with a subpanel in the outbuilding, that is not the question he asked. He asked about an extension cord.
He cannot run multiple permanent circuits to the outbuilding (only 1 is permitted), but he can run temporary power distribution to it. There is a whole industry for that, and I have set up system well in excess of 1 megawatt spanning several acres of distribution.
Voltage drop along a long cord is real, but most people that bring it up don't understand it.
Re: Motors
Charles Jackson III
How much did it cost?, I would have to sell my old 1-1/2 Unisaw motor for the cost of the new one. I have a 34-802 Unisaw made 1989.
Re: Motors
John in NM
Around $500 IIRC
Re: Motors
Charles Jackson III
Ok thanks!