Current draw on  VFD

Gary Evans, Tallassee TN

Does anybody know about the current draw characteristics of a Variable Frequency Drive?

I have a 3HP VFD that I've had on the shelf for a few years. I want to check it out before I sell it, but the current rating is 27 AMPS and I only have a 20 AMP circuit available. I'm assuming since I'll be running a motor with no load, that the current draw will be something less than 20, particularly at low speeds. Just thought I'd ask and see if anyone has knowledge on how the current correlates with the frequency on one of these drives.

Thanks,

Gary

Re: Current draw on VFD

#2

Re: Current draw on  VFD

Rick Christopherson

That's the rated input current for maximum power consumption. The actual amperage will be dependent on the load. For testing this out, it will work fine on a 20 amp circuit. Even for running most motors, it would be fine too. Only when operating a motor at full load will it exceed the circuit ampacity, but that would also exceed the ratings of most 3 hp motors too.

The actual current consumption of the single-phase VFD will be √3 x motor amperage, plus the consumption of the VFD itself (a few extra amps). An idling motor will typically consume 1/2 of its full load rated amps.

Because this is a 3hp VFD that appears to be factory rated for single-phase input (implied by the 27 amps), that is an important selling point. so make sure to list that in your ad to improve the sale.

Re: Current draw on VFD

#3

Re: Current draw on  VFD

Bill Howatt

if I look at the book for my VFD, the input current for the rated 3HP output current of 11A is 19.8A which is very close to root 3 x 11A. If I use the transient output current the VFD is rated for (allowed for 60s), the input current is 26A which agrees with your 27A figure. The recommended fuse size is 30A.

For my 2HP VFD the recommended fuse size is 20A but I've never had any trouble with a 15A breaker.

Bill

Re: Current draw on VFD

#4

Re: Current draw on  VFD

Gary Evans, Tallassee TN

Thanks guys,

I assumed that the current demand would be fairly small just to make sure the drive would run a 3 PH motor without a load, but I've found over the years that it isn't a good idea to make assumptions regarding electrical circuits. Ohm's law and the power formula don't deal with frequency.

You are correct that this drive is designed for single phase input, Rick. If it's good, you'll see it soon in the classifieds.