compressor start up draw

Posts

compressor start up draw

#1

compressor start up draw

Jerry Gibbs

Bought a used Sears air compressor. Motor is rated at 1.5 hp and 15 amps. At my daughter's house it tripped a 15 amp breaker most of the times it tried to start. Once it started it ran. At my house it started and ran fine on a 15 amp circuit that did not have a delay breaker. I bought this as a portable compressor. Am I going to have trouble if I take it to an ordinary 15 amp circuit with no delay breaker? I realize that I can't have much else running on the circuit. Thanks. Jerry

Re: compressor start up draw

#2

Re: compressor start up draw

Neal in San Jose

You may have already figured this out, but NEVER use an extension cord with your compressor. The voltage drop thru the extension cord may be enough to damage either the starter contacts on the compressor motor or even the windings. I've had both happen as a result of an apprentice not listening. Use a longer air hose instead.

As for the problems with the breaker, it's probably that the breaker is "weak" and tripping too easily. Can you try a different circuit?

Re: compressor start up draw

#3

Re: compressor start up draw

Barry Irby

You need to look at the data plate on the motor. It should list the RLA or Running Load Amps and the LRA or Locked Rotor Amps. An electric motor pulls the maximum amps when the shaft is sitting still and much less when it is spinning. There may e a four to one difference. You should run the unit on a circuit that is about is about 25% over sized or the unit should draw about 80% of the circuit size. Breakers are designed to "ignore" the nearly instantaneous surge it takes to spin the shaft up to speed. For a 15 amp unit you should probably plug it into a 20 amp circuit.

Also, check and see if the little bleeder on the pressure switch is working. There should be a little "flipper" on the pressure switch that bleeds off the head pressure when the unit stops so that when it restarts its not trying to start against the tank pressure.

Re: compressor start up draw

#4

Re: compressor start up draw

John McGaw (Bodger)

Easy way: install a 'hi-mag' breaker which is designed to accommodate the startup surge of electrical motors. It is very common for an electrical motor to draw considerably more than its rated current for a fraction of a second when spinning up so to protect properly you need a breaker which will allow the surge but which will also trip normally with a continuous draw of over-current. Installing a breaker which has a higher trip current will also usually stop the nuisance triggering but having one will also be almost certain to start a fire when things go badly.

Re: compressor start up draw

#5

Re: compressor start up draw

Bill Howatt

Sounds like the draw is close to the edge on startup but there is a good chance the breaker that tripped was weak - this is not uncommon. A 15A breaker is not carefully built to trip at 15.0000A and even a new breaker has a fair bit of latitude as to when it will trip.

This is fine if you always use the same circuit for the compressor but if you need to take it to different sites then it can be a problem because you don't know if it will trip. OTOH, most compressors sold for use on a 15A circuit should work on a 15A circuit.

I'd try the compressor on various different circuits and see if the trip was just because of the breaker on that one circuit.

The advice to avoid extension cords is very good and if you do need one, use a #12 or heavier cord.

I think you'll find that all breakers now conform to Heating Air Conditioning & Refrigeration (HACR) specifications which allow for motor starting.

Bill

Re: compressor start up draw

#6

Re: compressor start up draw

Bruce, a MN Galoot

Mine did exactly the same thing, and on a trip through our electrical inspector measured the start-up amp draw at more than 60. I had the motor rewired for 220, wired up a 220 circuit just for that compressor, and the problem went away.

Re: compressor start up draw

#7

Re: compressor start up draw

Jason Waters

It's possible the breaker is getting old. Replace the breaker that is tripping and see if that helps. I had a house once where the breakers started going, and after replacing the breakers with new ones, the problems were resolved. I think I had two that went out. Did you try a different circuit? Was it possible your daughter had something that drew power on that circuit you didn't know about?

Maybe even a light?

Re: compressor start up draw

#8

Re: compressor start up draw

Larry Clinton At Frankfort, (Central) Indiana

If it is a portable compressor and built within the last few years it should start and run on a 15 Amp circuit. As far as I know all portable power tools that meet the new standard will function on normal outlets. If it starts and runs on your 15 amp breaker there are only two things that (both have been mentioned) would cause it to not function at your daughters house. 1) The outlet you are using has some other load that is on at the same time you are trying to use your compressor. This could be a couple of light bulbs, TV etc. or 2) The circuit breaker that is tripping is tripping before the normal 15 AMP load - this is definitely not unusual. As a breaker is tripped the contacts often have an oxide layer build up and this causes heat - the normal circuit breaker functions by "heating" as a load is applied, after the heat reaches a certain point the breaker opens. (old fuses also have a limited life due to the same causes). I would not blame the compressor, I would try to see what other loads are on that circuit, then if none, replace the breaker. Or just try another circuit. By the way a long extension does cause more motor heating BUT the breaker will not open as the actual circuit draw on the breaker is less. That is what causes a lot of fires.

Re: compressor start up draw

#9

Re: compressor start up draw

Howard Acheson

>>>> It is very common for an electrical motor to draw considerably more than its rated current for a fraction of a second when spinning up

That is particularly true with a compressor motor. A compressor starts up under full load unlike most power tool motors. The full load startup will cause many breakers to trip. If the motor is rated at 15 Amps it should be on a dedicated 20 amp circuit.

Re: compressor start up draw

#10

Bob

Re: compressor start up draw

Bob

15 AMP ckts are typically for lighting and not appliances or compressors or power tools. The fact that it’s used could mean the motor will draw more amps due to ware and age. The breaker at your daughters may have a lot of other things on it so try another outlet on another ckt. Three things could be the problem. Most important #1 there is an electrical problem. #2 you have a weak breaker. #3 you are stuck with a bad compressor.

Re: compressor start up draw

#11

What else is on that circut ?

Pete in Holland MI

Account for everything else that is on that circut before you make judgments.