I've retired an old belt sander and am replacing it with a smaller model, both 220v. I was using a 25 amp female plug (clothes dryer plug) with 3 wires, black, white and red. I need to replace it with a 15 amp plug but the plug only has provision for 2 wires, presumably black and white. What do I do with the red wire? Can I just cap it with a marrette?

Re: OT: electrical question

#2

Re: OT: electrical question

NickinMass

Use the black and red wire. Your old plug (and the outlet that went with it) was set up to power both 220 and 110 elements (you need the white, or neutral, wire to run 110, but you only need the two legs, or red and black, for a purely 220v machne). So, use the black and red and put a cap on the neutral.

Re: OT: electrical question

#3

Re: OT: electrical question

Bill Houghton, Sebastopol, CA

No equipment ground wire? I'd never operate a stationary power tool without an equipment ground.

Re: OT: electrical question

#5

Re: OT: electrical question

John in NM

If there's a ground in the outlet box, it's well worth replacing the equipment lead to use it. Then you just screw the ground wire to any part of the metal structure of the sander.

Re: OT: electrical question

#6

Re: OT: electrical question

Larry Clinton At Frankfort, (Central) Indiana

Why would you need to replace the receptacle? You can use the dryer plug from your old unit and hook it up just as your old unit. The plug rating does not matter as long as it is rated for at LEAST as much as the load carried. The breaker in the circuit protects the stationary wiring and receptacle (as long as it is rated to carry the breaker current - from that point you can plug in any device. IE: you can plug in a desk lamp that pulls 1 amp into a 20 amp circuit or a sweeper that pulls 15 amps. The breaker normally does not protect any "plug in device". So I would use your plug from your old grinder and install it on the cord of your new unit. NOTE that Black and Red wires are normally the Line or hot wires with White being a neutral (or in a unit that only uses 240V an earth ground) and Green or bare copper being an earth ground. If your new grinder has only 3 wires in the cord you would hook the Red and Black to the line, and the white to the earth ground. If you look at the new unit wiring connections and it is only three wires, the white wire should be connected to the case and used as an earth ground instead of being a neutral. If the Sander does have a 120 Volt light then I would replace the cord with a 4 wire and connect the green or bare copper to the case (some metal part).

Re: OT: electrical question

#7

Yes, also...

Bill Howatt

If it is necessary to use the white wire as a ground it should be marked with green tape or colored with a green marker at the ends so it will not be confused with the normal use as a neutral.

The circuit should be checked to ensure this white wire is tied to the panel ground not the neutral buss throughout the circuit even if they are electrically bonded at the main panel.

Bill

Re: OT: electrical question

#8

Re: OT: electrical question

Ryan

Thanks everyone. BTW the plug does have an existing ground, I just didn't mention it.

Nice to have all these experts to answer questions!

Re: OT: electrical question

#9

Re: OT: electrical question

Rick Christopherson

Please be careful Ryan. There were so many problems with this topic that I chose to not even respond to it when I read it last night. If your dryer circuit does in fact have the ground (a 4-wire circuit), then at least one of those concerns did disappear. You cannot re-identify a neutral as a ground with tape on a circuit this small. Your existing dryer outlet is actually 30-amp, not 25-amp, and is likely a NEMA 10-30 receptacle. Contrary to what was stated, you cannot legally install a 15 or 20 amp receptacle on a 30 amp circuit.

I don't normally discourage people from doing their own electrical work. To the contrary, I actually encourage it. However, as I read this thread last night, my first reaction was to discourage you from proceeding further in your endeavors without hiring an electrician. There were too many red-flags in your existing setup, your questions, and in the existing responses.


img

Re: OT: electrical question

#10

Time to re-read the OP?

John in NM

Rick, he's talking about the lead and plug from the belt sander itself rather than the circuit it gets plugged into - at least that is what I got from the post. The re-marking of wire I also took to be applied to that lead, not circuit wires. From that point of view, I think most or all red flags disappear.

Re: OT: electrical question

#11

Re: Time to re-read the OP?

Rick Christopherson

No John. I did understand the OP, and I do know code. I waited over 24 hours before making my posting, and it was not made willy-nilly. It stands as-is.

Re: OT: electrical question

#12

Have it your way then


Re: OT: electrical question

#13

Tone it down

Rick Christopherson

I don't post here very often. I can be challenged in many areas, but electrical is not one of the wiser areas to challenge me on. If you have an issue with something I have posted, then please make your case against what I state, instead of making a drive-by insult. :-(

Re: OT: electrical question

#14

Re: Tone it down

Larry Clinton At Frankfort, (Central) Indiana

Rick I don't know what your credentials are - Have you ever installed electrical in residential, commercial or Industrial? I do know I have - over 25 years in residential, commercial and industrial wiring. You make some statements that I find offensive. One error in your reasoning is that you can't mark the ground line in the wiring to the sander with tape. This is the device wiring NOT stationary wiring - To the best of my knowledge the electrical code does not specify color coding on device wiring in fact it does not even address that issue. UL does have some requirements but color is not one of them. My recommendation was that he leave the existing stationary wiring intact and install a dryer Plug on his device - which is perfectly legal (or was when I was doing electrical contracting) and wire the new device with a 4 wire connection if it did use any 120 V. (changing if necessary the device wire to 4 wire) and using green or copper as earth ground and white as neutral. - if it only used 240 V. and only had three wires in the device wire, the white wire in the line can be wired to the ground connection of the plug.

Re: OT: electrical question

#15

Re: Tone it down

Rick Christopherson

Re-read the OP's posting. He was discussing a "FEMALE plug". That's a receptacle or outlet, not the cord on the tool. He wanted to replace his NEMA 10-30 or 14-30 receptacle with a 6-15 or 6-20 to supposedly match the plug on the new tool.

Prior to the OP later stating that there was a ground wire, some respondents were telling him to re-identify the white conductor as ground, which is a code violation. As I already stated, it is also a code violation to install a 15 or 20 amp receptacle on a 30 amp circuit.

The OP will need to change out the breaker to a 20 amp breaker. Then pigtail into the existing conductors to reduce the wire size to #12 so it will fit the new device. Install a NEMA 6-20 receptacle using the black, red, and ground conductors.

Re: OT: electrical question

#16

Re: OT: electrical question

Brian from Monument

There is this marvelous device known as a telephone directory.

It is occasionally use a weight.

But on this occasion there is section devoted to the people you really need.

They are called electricians.

You should call one and have him/her do the work.

That is if you don't know what yo are doing.

A shop fire is alot more expensive than what they charge.

Granted they charge an arm and a leg.

Re: OT: electrical question

#17

Re: Tone it down

Richard Jones

I don't see where the OP ever said what size the circuit conductors are.......was it just assumed he had the proper size for his 30 amp circuit?

Oh, the shame............

Re: OT: electrical question

#18

Bob

Re: OT: electrical question

Bob

I've retired an old belt sander and am replacing it with a smaller model, both 220v. I was using a 25 amp female plug (clothes dryer plug) with 3 wires, black, white and red. I need to replace it with a 15 amp plug but the plug only has provision for 2 wires, presumably black and white. What do I do with the red wire? Can I just cap it with a marrette? Before any answer can be given I think we need to know what the CKT is #12 or #10 wire?

Is it #12 wire with 20 breaker?

Is it #10 wire with a 20 or 30 AMP breaker?

In any case its my understanding you can't use a 15AMP rated plug on either or is it ether?

Not enough information to really give a safe answer.