I am running a 100 amp circuit from an existing building to my new garage/shop. The feeder panel has two hots, a neutral buss and a separate equipment ground. Total length between panels will be a maximum of 65 feet. I plan to use #2 copper for the two hot wires (red and black). The neutral (white) will be #_____copper. The ground (green) will be #_____ copper.
Hi Jesper, I just finished running service to my new shop in Feb. First why wast money on copper? All you need is aluminum and it may be required (Not sure). Pull a permit and Get it inspected for no other reason then insurance. Here is what I had to do by code. 100AMP service #2 alum./ a 100 amp breaker at the main and a 100 amp breaker at the sub panel (enough for 24 breakers) I ran everything in pipe at 12" otherwise its 18" for direct bury I'm in VA the farther north the deeper you need to go. Your supply people will tell you the code. I ran 4ea. #2 AL, direct bury cable, 2ea. hots 120VAC, 1 ground and 1 Neutral I also had to use 2 ground rods 8' bonded together and tied to the neutral in the sub panel. Inside I used #10-2 with a ground for my 240 VAC ckts and 12-2 with a ground for my 120 VAC ckts (Passed inspection) You don't have to use colored wire just be sure to wrap the wires with colored tape. By the way I had to run 73 feet I think #2 is OK up to 100 feet for the load I am requiring.
Joe - l am basing my recommendation on the conclusion that you are installing the wiring in conduit. If so the three current carrying conductors (number 3 THHN is the minimum required - I would agree with you using #2 ) should all be the same #2. I am an advocate of only using copper as I have seen many problems with terminations of aluminum. The ground wire should be bare copper, minimum of #8 - I would recommend #6. You may want to contact your local utility but I feel sure this will meet their requirements. You only need to identify (color) the neutral, the other two current carriers can remain black - and ground copper. I usually just laid the coil of neutral wire on a cardboard or grass and painted it white with a spray can of quick drying paint. You can use white tape but it does have a habit of dislodging when pulling the wire through conduit.
I would suggest CAUTION on the use of aluminum wire. As an insurance agent I have sceen too many fires and failures due to it. In California, most homeowners insurnce companies will not insure a house if it has it. Go copper, may cost more but it is only a onetime investment. Just my 2 cents worth.
Would you please expand on the reason for the following in your note:
"I also had to use 2 ground rods 8' bonded together and tied to the neutral in the sub panel."
If the subpanel is grounded via cable to the main panel ground bus, what is the reason for the seperate ground rods on the subpanel? And, why are they connected to the neutral bus in the subpanel?
I understood that the code requires that the neutral and the ground not be bridged (connected) in a subpanel, but only in the main panel.
When I went to pull the permit the senior inspector told me I had to have 2 ground rods and said it was code? I did not look it up, I saw no point he said he wanted it and he was the one to inspect it so I said OK thanks.
I ran 4 #2 Aluminum wires (2 Black) (1 White) (1 Green) all from the main panel. The green Neutral where you put the bare copper wires is also the one where the ground rods are boned to in series not a loop and must be no less then #8 cu #6cu is recommended and it must be copper
A picture is worth a thousand words.
When the inspector says do it this way, you do it the way he says or he/she will fail it. If its inspected and passed your insurance company has no choice but to pay up as long as everything was inspected and done to code if they don't pay they were never going to pay any way and you would get the claim at court plus damages for your trouble. In 1971 I sewed Allstate for not honoring my claim for 22K the judge awarded me another 3K plus lawyer fees to be paid in 90 days of it would double. Just be sure its to code and inspected and inform your insurance company, the work you did may raise the value although you may already be at you limit for out buildings. Bottom line is do it right and you will not have a problem. If your going to put up sheet rock and insulate it as I did your county may require a building permit as well I had to do that as well. I was required to use 5/8" Fire code sheet rock and because the ceilings are 10 feet I had to put fire stops in every bay.
Sorry about the additional information.
. I think the reason for two ground rods is if one fails, we have a lot of clay here and I think its got to do with ground water but I don't know for sure (they do need to be no closer then 6 feet to each other). I can send you a photo
Thank you for that URL, Tom. The discussion on that site was very informative on the issue of ground rod / no ground rod at a sub-panel. After reviewing it, I believe I am OK with my garage/workshop sub-panel grounded back to the main panel with the N-Ground bridge removed in the sub-panel.
I can't believe MD is that much different then VA here is a photo of my panel. You can see I have 4 #2 Alum cables all 4 go back to the main panel. You can see the Green stripe on the right most insulated cable and right above it is the bare copper wire that goes to the ground rod, from the ground rod is another bare copper wire that goes to another ground rod. I really don't know why the inspector insisted on the second ground rod. He did say you had to have one even if the main panel was grounded to the water pipes or its own ground rod. I would have thought it would create a ground loop which you don't want. Let me know if you get any clarification on this.