What's "code" for wire size and conduit to run a 90 amp generator feed 30 feet to an ATS?

I'm putting in a 20kw generator and soliciting bids for licenses. Since I'm getting the gen- set, transfer switch, and doing the pad and install, I'm tending to think this should be a fairly minimal amount of work for the electrician, and I'd like to get a handle on materials. I'm thinking that #4 copper in 1-1/2" conduit should do this, but . . .

TIA

Re: Sparky Question

#2

Re: Sparky Question *LINK*

Bill Houghton, Sebastopol, CA

You want a "voltage drop calculator" or "voltage drop table."

I can't guarantee the link below; it was just the first one I found.

The outcome varies by voltage, amperage, wire type (although there are so few wire types in residential use that this isn't a big deal), and how the wire's run, whether in conduit, in the air, etc. Over 30 feet, I'd expect minimal drop.

Bill, not an official sparky but I've done a lot on my house


http://www.nooutage.com/vdrop.htm

Re: Sparky Question

#3

More Info

Mark Mandell - Gone Round In New Jersey

Thanks, Bill, but drop is not my issue. 30-40' on copper will be negligible. I'm concerned about materials cost. I had one guy quote me $2k in materials for 40' of generator feed in 2" PVC conduit + 1 run of 1" conduit for the control circuitry and with two branches for the A/C circuit contactors. I was born at night, but not last night. I can price the materials for myself, but I need to know the base size on the wiring. The gen set puts out 83 amps at 240v max although it's unlikely to ever draw that much because the load-shedding processor will kill the A/C if total draw gets to 70amps.

So two narrow questions:

1. Feed wire size? [2 or 4 or ?? awg]

2. Conduit size in steel for that wire size [must be run through the garage]?

m

Re: Sparky Question

#4

Re: More Info

Stuart Johnson

Two conduit fill tables

http://www.jhlarson.com/ind_tables/fill/emtfill.htm

http://www.alanwire.com/tech/conduit.html

Conductor size. It looks like 4 would be sufficient.

http://www.allaboutcircuits.com/vol_1/chpt_12/3.html

I would price out on both 2 and 4 in order to have the figures in hand.

Re: Sparky Question

#5

Re: More Info

Bill Houghton, Sebastopol, CA

Well, I guess I was figuring that the voltage drop calculation would also tell you the wire size - I have to confess, I hadn't looked at the calculator. The tables I usually use, from a book of some age, give you wire size; and the tables on the next pages give you conduit fill. On my own work, I've learned to oversize conduit, just as I oversize the fixture boxes. Easier to have too much room than just enough.

Copper's gotten more expensive, but $2,000 sounds more than a mite pricey for materials. He must be burying some of his labor cost in there, and, even so...

Re: Sparky Question

#6

Re: Sparky Question

Joe W

The few homes that I have worked on, we have used 2 AWG copper for 100 Amp panels. I know you are a little smaller, but, it depends on what type of wire the electrician is using. My Ugly's shows 4 AWG THHN good to 85 amp, so 2AWG would be the correct size. I assume you are using a wire something like THHN since you are going to use conduit.

Fill also matters on what type of wire. Again, using THHN, it looks like like 1 1/4 plastic PVC Sch 40 will take 5 2AWG wires. Should be OK since the ground will not be larger than probably 6AWG.

Copper wire is pretty expensive and you may want to consider aluminum instead. The short run and the increase in conductor and conduit size would probably be offset by the price of aluminum vs copper.

The electrician's price may still be based on him getting the materials. He may not be comfortable with you purchasing the materials. He may have had a bad experience with a client who wanted to get too involved in laying out a job in the past. He knows what he needs and wants, and if he shows up and you have forgotten an item or purchased the wrong item, it will cost him a lot of time. If you trust him, it may just be worth it to let him do his job and suck it up.

Re: Sparky Question

#7

Re: Sparky

Mark Mandell - Gone Round In New Jersey

I have no plan to supply materials beyond the generator and ATS. I do, however, want to assess the propriety of the quote. Right now I've got a quote for $2k in materials and $3,800 for 48 man-hours labor. I think both are high, but I have to spec the job to tell. F'rinstance, we may be required to pull 60' of new 200 amp feed with ground, to the service panel because of the ATS install which backfeeds the entire house. Comment has been made that, in that situation, the ATS technically becomes the main service panel requiring a grounding conductor be added to the feed cable (now, 2 hots and a Not) which runs in a conduit underground from the meter pan to the sill entry.

Re: Sparky Question

#8

Re: Sparky

Larry Clinton At Frankfort, (Central) Indiana

Mark, I have done a lot of electrical, Residential, commercial and industrial. However, many areas have different specifications and requirements that go beyond the national codes. IE: about half of Indiana is served by Northern Indiana public service and the other rural area's by a second utility - REMC - one required bonding the entrance box to ground and the other wouldn't hook up if it was grounded, both had different ground rod requirements and conduit stand heights etc. If I were in your situation, I would contact the local building inspector and/or the utility company that provides your service to obtain this information.

Re: Sparky Question

#9

Re: Sparky

Joe W

Ah OK. Thought you were wanting to buy the materials. Is the ATS near your house panel or is it 30 feet away by the generator? If it is by the generator 30 feet away, then you will have to run the 30' of 2AWG to feed the ATS and then pull how many circuits you want to run back into the house. Don't forget that you will have install the correct size breaker in the house panel too. The 48 hours seems a little high to me, but trenching is a lot of work too. It is fairly easy if you can make the splices in the house panel, but if local code requires a separate junction point, then that can be quite a bit of work to pull those circuits back, locate them and then then re-feed them. I know this isn't giving you the answer you deisre, I'm just trying to point out some things you may need to consider before hiring the contractor.

Re: Sparky Question

#10

Re: Sparky

Mark Mandell - Gone Round In New Jersey

Hi Joe.

Thanks. No circuits as this is a 20K full back-feed on the whole house with the (200 amp service-rated) ATS in the main line from the meter pan. Generator supply will be run in conduit through the garage to the ATS. Feed from the ATS to the service panel runs through existing 3" conduit- no digging involved, but we may either 1) pull a new, 4 conductor feed set or 2) run a separate binding ground in conduit through structure from the ATS to the service panel. Given all that, I have trouble seeing this as more than a 20 man-hour job, especially as I'll be doing most of the prep work (gen set placement, structure accessways, etc.)

Re: Sparky Question

#11

Re: Sparky

Joe W

OK. The way I see it, he will have to pull a new 200A feed from the meter can to the Normal side of the ATS, pull appropriate size wire from Gen set to Back up side of ATS, and then pull right size from supply side of ATS to the existing main on your panel. Conduit is in place from ATS to your home panel.

I'm a maintenance electrician, so I work slow when it comes to this stuff, but 48 man hours sounds excessive. Even to feed the ATS from the gen-set could probably be down in a couple of hours by an experienced electrician, especially if its done in PVC. I must say that I am jealous though, a back up generator is something that I have been wanting for awhile, just haven't been able to convince the Mrs of the need.