New shop electrical layout

Posts

New shop electrical layout

#1

New shop electrical layout

Guillaume Dery

Ok, so I am at the point where I am starting the layout for my shop electrical and want a sanity check. Seems that even for us mostly handtool guys, we kill a lot of electrons (although I am more of a hybrid I guess and can't seem to part with machines or stop accumulating them)!

Equipment Electrical needs/consumption:

Planer/jointer - 20 AMP 240V

Bandsaw - 20 AMP 240V

Tablesaw - 15 AMP 240V

Dust Collector - 15 AMP 240V

Small stuff - 120V

Drill Press - 1/3 HP

Table router -3 HP

Chopsaw

Handheld routers and laminate trimmers

Misc chargers

Stereo

Task lighting

??

I was thinking of running 3 240V 20 AMP circuits. One dedicated for the planer/jointer, 1 for the table and bandsaw and a dedicated one for the dust collector.

I am definitely doing 20 AMP split receptacle for the other stuff but am on the fence if it should be 2 or 4 circuits (one run of split receptacles around the shop or divide it into 2 runs)

2 15 amp circuits for the overhead lighting (12 FS fluorescent fixtures). As far as draw goes I would be OK with one but it is over the maximum number of light fixtures they like to see on a circuit. I could also drop down a plug from either of those circuits so I would have a working plug in the shop if I had to work on the other stuff.

Thoughts? Sanity check?

Thanks in advance,

Guillaume

Re: New shop electrical layout

#2

Re: New shop electrical layout

Jason Waters

For your 240V, you have to figure what you have and use. For me, I have 3 240V circuits-Tablesaw, Dust Collector, and Air Compressor, all 20A circuits.

As to the 120V, put your lights on seperate circuits, 15a or 20a for any tools, that way if you trip the breaker, you are not in the dark with a spinning blade. If you want an overhead reel, have it on a different circuit than the lights.

Lastly, depending on layout, I ran multiple circuits. I have 4 110v 20A circuits. On the main wall with chop saw, drill press, jointer, etc., I pulled two circuits in one conduit, and alternated the plugs as to which citcuit they were on. So I could tell them apart, on that wall, I have Ivory/Brown/Ivory/Brown. That way if I wanted to run the shop vac and a tool that pulled 15amps (Think circ saw), I could plug into two different circuits. There is another circuit, which is Gray on the adjacent wall, and lastly one more I ran over near the garage door so I can run tools outside, it's on a seperate circuit all by itself (It's Ivory too, but it's far enough away I know it's seperate).

Does that makes sense?

That's what I did, all 120V are GFCI, and in metal conduit, etc. to code.

If you have an electrician do it, lot cheaper to do it now.

Re: New shop electrical layout

#3

Re: New shop electrical layout

Larry Clinton At Frankfort, (Central) Indiana

I think it depends on how you intend to finish your shop. Running circuits now is no trouble and far less expensive than doing it after the walls and ceiling are covered. I know there are many that disagree with me, but I firmly believe in total overkill when wiring a new shop. First I would wire all the 240V circuits in #10/3 and use 30 amp breakers - 1 circuit for each machine. That way in a couple of years if you decide to upgrade any of the machines the power is there. I installed 4 lighting circuits - with separate switches on each bank of fluorescent lights. This way I don't have to light the entire shop if I am working in one area. I also installed outlets 4 1/2 foot high every 32" on every wall in the shop and added a couple of 240V outlets in the corners. I filled up every breaker in the largest 100 amp main I could find. I haven't regretted any - after using the shop a while I wish I had added a couple more outlets. When I built the shop I had a 120V joiner and planer - now both have been replaced with larger 240V units. You didn't mention an air compressor - if you start spray finishing you may need a 240 circuit for that. Exterior motion sensing lights help protect your shop - may want to install a circuit for that. By the way I personally don't recommend buying the high priced outlets when installing - as long as you leave adequate extra wire in the junction box, you can replace any worn out outlets in 15 minutes later - then you may want to purchase heavy duty ones for those you use a lot.

Re: New shop electrical layout

#4

Re: New shop electrical layout

Bill Houghton, Sebastopol, CA

Jason's given good advice. Not much to add.

I will say, were I wiring a shop from scratch, I would:

1. Put in way more outlets than code requires. Consider doing this even for the dedicated 240 V circuits.

2. Run outlets near the floor and also at 52" or so, so that they're still exposed if you happen to lean a sheet of plywood against the wall.

Whatever layout you've designed for your shop will turn out to be imperfect; you don't want to have to run long extension cords across the floor because you failed to put in outlets where you didn't know you'd need them during the build stage.

Re: New shop electrical layout

#5

Re: New shop electrical layout

TomD

This is the forum I go to for electrical, though it is Canadian. http://forum.canadianwoodworking.com/forumdisplay.php?23-Shop-Electrical

As everyone else has said, there are never enough outlets. They soon get covered up with tool racks and tall machines. I don't run many machines at once, so my overall draw is not that great, but I can't get to the outlets. Also, a welder is super useful, and may be in the mind of a buyer, even if you don't want one now. That's another 50 amps in capacity, which can be somewhat cheap at the outset.

Re: New shop electrical layout

#6

Re: New shop electrical layout

Gary Smyth

Are you heating the space? That may need consideration. Hot water that may need 240 too.

Re: New shop electrical layout

#7

JL

Re: New shop electrical layout

JL

I would run the three 20 amp 240 circuits. I would tend to agree about using heavier gauge wire (10 gauge). You may want to have a 30 amp circuit. I ended up with a 5 hp cabinet saw which definitely needs one.

I've got a few "quads" scattered throughout my shop with 120 V. Each receptacle is on a different circuit. All of my receptacles are at greater than 48" from the floor.

I have three lighting circuits - one main circuit and two task light circuits. The main lighting circuit is NOT on the shop subpanel, it runs off of the main house panel.

Re: New shop electrical layout

#8

Re: New shop electrical layout

Jason Waters

Bill,

Great additions! The 240V ones can be a pain to add later. One or two spares are always good. One other thing, is I have a 240V and 120V right on the bottom of my subpanel. If you ever have trouble with a circuit, these usually work until you can figure out the problem.

The only thing I could see is if you get an inspector saying you have too many circuits for your panel. Even though you will never use them all at once, it can become an issue. But if it's not, then by all means, add more circuits.

I like your idea of receptacles up high. I do have one for an overhead fan now that you mention it. Since it's a 1/2 hp motor, it's on it's own dedicated circuit as well.

In the shop, all circuits are 20 amp with 20 amp receptacles and proper wire.

Re: New shop electrical layout

#9

Re: New shop electrical layout

Bill Houghton, Sebastopol, CA

New (that is, not used) panels will state what the breaker capacities are. I don't think the inspector can ding you for filling the panel up to its capacity.

Re: New shop electrical layout

#10

Re: New shop electrical layout

Jason Waters

If he believes you will exceed the capacity of your service, they may not sign off. It's probably not going to happen if you have a 200 AMP main on your house (or even a 150). But if you have a 100 AMP main for whatever reason (older home, etc.), I can see it being an issue and they wanting you to possibly upgrade.

But you are right, nothing to do with the number of circuits in a box. It's the number in use.

Re: New shop electrical layout

#11

Re: New shop electrical layout

Guillaume Dery

Yup, I paid extra for the 200 AMP service up front (current standard now is 100 AMP) so no worries there. I hate seeing an overfull panel so even though I have 24 single breaker slots left, I will add a 100 AMP pony panel for the shop. Other reason is that with the basement reno, I can see myself filling 22 of those slots if I kept the shop circuits on the main panel. It is amazing how quickly you chew these up doing things right. Bedrooms need to be on an arc fault circuit so there goes 2 slots. Bathrooms on their own 20 MAP GFCI circuit, Fridge and freezer need a dedicated outlet, 3 more slots. 2 circuits for general basement lights, 2 more slots. outlets, 2 circuits, 2 more slots, etc. Just the reno is eating up more than 1/2 my empty slots!

Another comment I saw here was to run it in conduit. I like that because I can fish out and rewire as needed. Will definitely do that for the shop.

So I am now, based on input here, thinking I will now proceed as follows:

100 AMP sub-panel (20 feet from main panel), wired with 2 gauge

Circuits off the sub-panel:

20 AMP 240V - Dust Collector

20 AMP 240V - Bandsaw

20 AMP 240V - Tablesaw (I intended to put both saws on the same circuit but it seems that having more than one outlet on a 240V circuit is against code)

20 AMP 240V - Spare circuit, future use

4 X 20 AMP 120V Split circuits (2 split circuits, alternating every other outlet) spaced every 4 feet, 50 inches off the ground

All above wired with 12 gauge in conduit

2 X 15 AMP 120V Shop lights (12 overhead fluorescent fixtures) plus 2 over head plugs

1 X 15 AMP 120V traditional plugs at traditional low height. Chargers, shop stereo, etc.

Above 3 circuits wired with Romex.

I think that would take care of future-proofing. Only thought I have would be to perhaps downsize the sub-panel to 80 AMPs and feed it with 4 gauge because 2 gauge is a PITA to work with. I doubt I would ever draw even near capacity.

Does everyone think this should take care of future-proofing^ Anything else I didn't think of?

Cheers and thanks,

Guillaume

Re: New shop electrical layout

#12

Re: New shop electrical layout

Jason Waters

I have a 60 AMP sub, but would do 100 if you could. Really, you could use a 100 amp panel if it doesn't have it's own main unless I am missing something. My 60 amp sub has a double 60 in the main which runs to a lockable disconnect above the subpanel which is only about 5 feet away since it's in the garage. The sub has no main.

I'm not sure about the 2 outlets on 240v, but I have never tried that but I could see the issue. If you use conduit, and possible want to upgrade in the future, use something other than 1/2" EMT. I used 1/2 EMT (except main to sub) and wish I had done 3/4. Not that it is a big deal as I am happy. If I had a 5 hp saw, and needed 30 amp, that could be different. So maybe just upsize your conduit or a particular circuit if you believe you will upgrade. I would have run some of my 120V with romex or armored cable if I had stud walls, but since I have block, it was EMT all the way.

Lastly, I have been having a heck of a time finding the larger metal "Handy Boxes" that are rounded for surface mounting. I have two, and they both have GFCI's in them as you need the extra space sometimes. The regular small single gang handy boxes aren't big enough for a GFCI outlet. That's why I have one with a GFCI breaker. Which was a pain because the breaker wasn't rated for stranded, so I had to wire nut the stranded from the conduit to the solid in the subpanel and connect to the GFCI.

You plan looks great. Have it inspected and make sure it's to code.

Re: New shop electrical layout

#13

Re: New shop electrical layout

Dick Schmidt, Stuart, VA

My shop is a separate outbuilding 32' x 48' with all of the considerations you and others have mentioned, however there is one thing that I recommend. When I go out at night to the shop to put a log in the stove or get a tool, instead of having to flip on a bank of overhead fluorescents, I installed 4 ceiling mounted can lights with 65 watt incandescent floods. This gives all the light I need for the two minutes or so that I'm in the shop. Saves a lot of wear on the fluorescents.

Re: New shop electrical layout

#14

Re: New shop electrical layout

Brian Anderson Gunsmith

I don't think I saw a comment about this.

I would use a 20 amp for your chargers and stereo might as well besides needs change.

I would have a single 20 circuit that serves 2 overhead outlets. I am glad I did.

Run as many 20 amp 220/240 as you can since you may change layouts. I have change the layout of my shop several times and repurposed it once and have not had to add outlets.

I have at least 6 - 20 amp 220 circuits.

And 6 - 20 amp 120 circuits.

Plus a single 15 amp light. I should add another 15 amp for lights.

More is better. More is more expensive. More is more flexible and adaptable.

I would inquire more about having 2 outlets for the 220 circuits.

My 2 cents worth.