Air compression safety relief valve
Starry S Chan
The 145psi safety release valve on my air compressor is popped prematurely at 130 psi. This part is quite expensive from the manufacturer.
I would like to find out whether I can use either a 150 psi or a 140 psi version. How accurate is the pressure rating on these safety relief valves? They also specify to be "bubble tight within 10% of the set pop pressure". This implies that they are not 100% accurate.
Thanks in advance for your tips and comments.
Starry
Re: Air compression safety relief valve
Starry S Chan
I forgot to mention that the max pressure on my compressor is 130psi.
Starry
Dale Lenz
Dale Lenz
My a-c has an adjuster screw to set max pressure and when to come back on. My a-c is suppose to shut off at 135(??). The best I could get was 125, decided that's close enough. In theory, the compressor kicks on more often, not a major problem for me.
Gerry In North Surrey
Most air and steam safety valves can be adjusted, although most manufacturers don't permit adjustment without voiding any warranties. Don't suppose you could post a picture of your valve?
Gerry, who's an old hand at adjusting steam safety valves on miniature steam locos.
Bill Howatt
I don't see a problem using say the 150 PSI safety valve if your max working pressure is 130 PSI. The safety factor for bursting in the tank is way more than that 20 PSI difference so the additional 5 PSI going from 145 PSI to 150PSI is nothing.
Bill
Jim
Safety relief valves per ASME Sec VIII Div 1 UG 125
(c) Other than unfired steam boilers, when a pressure
relief device is provided, it shall prevent the pressure from
rising more than 10% or 3 psi (20 kPa), whichever is
greater, above the maximum allowable working pressure
except as permitted in (1) and (2) below and UG-127(d)(3).
(See UG-134 for pressure settings.)
Copyright
Check the tank label for max allowable working pressure, not the pressure switch settings.
Jim
Starry Chan
Here is what I found.
"Air tank safety valves should be set no less than 15psi or 10% (whichever is greater) above the operating pressure of the compressor but never higher than the maximum allowable working pressure of the air tank."
For my compressor, the operating pressure is 130psi. The WP of the tank is 145psi. Therefore, the required safety valve should be 145psi.
Starry