Home A/C question

#1

Home A/C question

Nat Robison

We had our first truly hot day recently and I turned on the A/C and it appeared to be working OK but I think I have a problem. I have not heard the outside compressor kick on at all. I think the furnace blower was just circulating cool, dehumidified air from the basement.

Assuming the unit is getting power (the breaker wasn't off or tripped), what are my issues?

If it's refrigerant, would the unit still kick on?

If it's the compressor, would it act like it is (which is nothing)?

I know this won't get fixed without me calling someone, I'm just trying to get an idea of the problem.

Re: Home A/C question

#2

Multiple causes possible

Lee Schierer McKean, PA

There can be several reasons. Low refrigerant pressure is one, motor start relay is bad, motor is bad.

Turn the thermostat down to it's lowest setting and turn the system on. Then go outside and listen. If the motor hums (no particular tune) then the start capacitor is bad or the motor bearings are stuck. If the motor hums and you can rotate the fan by hand the motor relay or motor itself is shot.

Low pressure will also prevent the motor from running. It is not uncommon for systems to lose refrigerant due to leaks caused by corrosion from the winter.

In your favor, if you upgrade your unit to a new energy efficient unit you get up to 30% back from the government as a tax credit.

Good luck

Lee

Re: Home A/C question

#3

Re: Multiple causes possible

Barry Irby

Lee pretty well nailed it.

If the outside fan is running it will be obvious. If the fan is running it may be a little harder to tell if the compressor is running but you probably can.

If you have an amp meter you can check the current draw. The fan will draw something like 1 or 1 1/2 amps. The compressor considerably more. (The label will tell you.)

Many units have a low pressure switch, but not all, so if the refrigerant is low, it may not allow the outdoor unit to run.

If the unit is running and the compressor is on, you can feel of the tubing. The larger line should be cold and the smaller on about room temp. If both are dead fish air temp and the compressor is on, you have lost the refrigerant. If the larger one is just a little cool but not sweating, you may have lost some or most of the refrigerant.

If they replace the unit, they should replace both the indoor and out door units to get them matched for best performance.

Re: Home A/C question

#4

Re: Home A/C question

Gary Bindel

The outside unit (condenser unit) contains the compressor and a fan motor. With the thermostat set to cooling and set to a temperature lower than the room temp, check if compressor and fan are operating. If neither are running, check to see if the outside disconnect has fuses. If it does, check the fuses for continuity with an ohm meter. If fuses are OK or non-existent, remove control panel cover on unit. Locate contactor and check for power on both sides of the contactor (should be between 220V and 240V). If you don't have power to the contactor, remove cover from outside disconnect and check to see if you have power coming to the disconnect. If no, go to the electrical panel and check to see if you have power coming out of the circuit breaker. If you have power into but not out of the contactor, look for the low pressure switch switch which is ususally located on the large refrigerant tube between the housing and the compressor. With the volt meter on the low range, check across the pressure switch terminals. If you get a reading, it means there has been a loss of refrigerant.

I hope this helps.

Re: Home A/C question

#5

Not mentioned yet

Galen Vetterick

I had to replace the low voltage transformer located in the furnace when I found there was no cotrol power to the compressor contactor. Some little rodent had eaten into the wire near the compressor and it had in turn shorted out the transformer. Wire was fixed and covered so it did not happen again.

Re: Home A/C question

#6

Re: Home A/C question

Bill Turpin in WNC mountains

Most modern units have electronic modules to protect against brown-outs, power blips, power surges, etc. Reset them by removing demand for cooling at thermostst, wait a few minutes, turn demand for cooling back on. There may be a 5 minute wait then for compressor to start. If you have a horizontal flow air handler there may be a safety float switch to protect from overflows. Condensate pumps have additional float switches. If outside fan is running then the compressor should run, they have the same power source. If inside fan is running you do not have a bad transformer. Power Companies can install radio controlled demand savers(that save you on your bill), they can go defective. If you have a mercury bulb thermostat, is it installed level? Has it been knocked?

Re: Home A/C question

#7

Re: Not mentioned yet

John McGaw

Typically, if the low voltage transformer was dead then the fan would not be triggered and the heating functions of the furnace would have been inoperative.