Re: OT Garage Freezer
Bill Turpin in WNC mountains
Think of the refrigerant cycle like water: liquid, steam, ice, vapor. Liquid absorbs heat, boils, forms vapor, looses heat, and condenses back to liquid. Refrigerant happens just the same, but at much lower temperatures. R-12 boils at -30�F, R-22 at -41�F, and R-502 at -50�F.
The compressor pumps against ~200 psi head pressure to condense the refrigerant, it is strong enough to do this no matter how cold.
The real concern is that the liquid refrigerant (during the OFF cycle) migrates, just as if was pumped, to the coldest point in the system. If the compressor is colder than the freezers set point, the refrigerant will go to the compressors crankcase. The liquid can replace the oil being pumped to the bearings causing wear and bearing failure. Commercial units have crankcase heaters, ~40 watt, to keep the crankcase warm. My chest freezer is on my deck, works fine because its set point is -22�