Semi OT - Furnace Repurpose

#1

Semi OT - Furnace Repurpose

Stuart Johnson

After remodeling we had to upgrade our heating and air conditioning. I saved both the furnace and outside compressor unit to eventually install in my shop. The shop is a 1200 sq. foot metal building with 12 foot ceilings, semi insulated at this point. I'm comfortable working in 60 degrees. I'm thinking about just building a stand for the furnace with a box to hold an air input filter and allowing the blower to blow into the shop and not use ducts or a thermostat. Once the shop is comfortable I'll just turn it off. This is an electric unit and I do anticipate the need to blow the dust off it on a regular basis. This is temporary until I finish the walls and will be plugged rather than hard wired until then.

The big question are there any serious reasons why this is a bad idea?

Re: Semi OT - Furnace Repurpose

#2

Re: Semi OT - Furnace Repurpose

Bill Houghton, Sebastopol, CA

If it's an upflow unit - warm air comes out the top - you might consider some sort of roof on it to keep shop dust from filtering down into the furnace when the blower's not working, which would reduce efficiency and might be a fire hazard.

Re: Semi OT - Furnace Repurpose

#3

Re: Semi OT - Furnace Repurpose

Bill Howatt

I'm with Bill Houghton, build something to reduce dust settling on the elements. Also, it's no big deal to hook up a cheap thermostat and it eliminates the "I forgot" factor.

Plugging the furnace instead of hard-wired may not be strictly legal.

Bill

Re: Semi OT - Furnace Repurpose

#4

JL

Re: Semi OT - Furnace Repurpose

JL

Most electric (heat pump and furnace) set-ups usually require a thermostat to "control" or trigger the unit.

I'm not saying it won't work - but why bother? A thermostat isn't that expensive. Heck - you could probably get it for $50 (Honeywell). That way you could have your shop at a reasonable temperature before you got there.

Just a thought.

Re: Semi OT - Furnace Repurpose

#5

Re: Semi OT - Furnace Repurpose

Bill Turpin in WNC mountains

An electric furnace can pull some serious amperage. My 15 KW electric furnace is wired with a 100 amp breaker. 100 amp plugs are hard to come by. You will need to put a low voltage switch in to simulate the missing t'stat. You do not want to disconnect a 100 amp plug under load.

Re: Semi OT - Furnace Repurpose

#6

Re: Semi OT - Furnace Repurpose

Barry Irby

Bill is right, Electric furnace draw a significant amount of current. 15 KW translates to 62.5 amps. (15000 watts / 240 volts = 62.5 amps) Each watt = 3.41 Btus so 15000 watts equals about 51000 Btu. You need an 80 amp or larger circuit for it. (You have to derate the circuit by 20%) So Bill's 100 amp circuit is entirely adequate.

Electric Furnaces usually come with rakes in them to allow for more or less heat installed in segments or sections which are often about 5 kw each, sometimes 10 kw. They are usually slightly undersized, like 4.8 or 9.6 kw. So, if yours is large, you could disconnect sections and get down to five or ten kw and use an appropriately smaller circuit. Not positive, but I think ten kw would be plenty and five might do the job for you. Depends on the insulation, the climate and your tolerance.

I also agree with the others that a simple Stat is a good idea. And so is some sort of shield to keep the dirt and dust out. A short piece of duct with an elbow or just a hole in the side would do a good job of that.

Re: Semi OT - Furnace Repurpose

#7

Re: Semi OT - Furnace Repurpose

Stuart Johnson

The old circuit was 70 amp. I don't know why I thought it was lower than that but you are right I don't want to just pull the plug. This might be a case where hiring someone to do it properly might be the wiser choice.