Wood Stove

Posts

Wood Stove

#1

Wood Stove

mark

I have a 20/30 p.frame metal woodworking shop with concrete floor. I recently bought a small wood or coal burning stove to assist in the heating. I do not have a chimney so I was wondering if anyone had any suggestions on how the pipe should be run,and if the pipe should be at least a certain height. The shop has a 10' high metal roof for which I perfer to run the pipe out the side rather than the top. Any suggestions would be helpful. Thanks MS.

Re: Wood Stove

#2

Does it have a manufacturer nameplate on it?

Bill Houghton, Sebastopol, CA

If so, the manufacturer should have some info on clearances and so on.

Google, or books at your local library, should have articles on basic setup.

Re: Wood Stove

#3

Re: Wood Stove

Bill Turpin in WNC mountains

Single wall smokepipe should be a minimum 24 ga. It should extend to at least two feet above the roof peak. Clearances from stove wall or pipe to combustibles is a minimum of 36 inches. This means that 6" pipe thru the wall needs a total of (36"+36"+6") of clear space between studs. This is why smoke pipe is usually insulated and stainless which reduces clearances. It is very possible to spend more on the stack than a modern stove. The stainless keeps flue gases and acids caused by sulfur in the fuel from eating up the pipe from the inside. Single wall pipe needs at least three screws at every joint. This will prevent hinging of the pipe in case of a flue fire. Flue fires under the right conditions will generate 2000� in less than ten seconds. The pipe then ends up, cherry red, on the floor in the sawdust. Please check with local codes. Pine 2" x 4" studs will ignite at 475� after continued exposure to flue temps at less than these distances.

Re: Wood Stove

#4

Re: Wood Stove

Doc Green

Mark, keep the horizontal run of the pipe short enough so that it stays hot enough not to allow water vapor to cool and condense in the pipe. The allowable distance depends somewhat on the size of the stove and the size of the fire you intend to maintain. My guess would be that anything up to 6 feet would be OK for any stove.

Condensation in the pipe can result in a black, ugly substance (soot and water) dripping from the joints in the pipe. I've seen this happen where very long runs (upwards of 20 feet) were used.

Fire makes water, so you can have this problem even if you burn dry wood or coal.

~Doc Green (woodturner)

Re: Wood Stove

#5

Re: Wood Stove

FredD

We have a wood fired boiler which gives us zone heat in the floor slab and the stack is double walled, which you should use, rather it is stainless or not.

Keep the vent vertical if you can , far better draft and use a stack which has a adjustable damper close to the stove.

FredD

Re: Wood Stove

#6

Re: Wood Stove

steve mackay

I used double walled, insulated pipe (expensive but I'm a paranoid). Out side diameter six inches. The excisting pipe on the house was three feet above the roof so I just did the same. Works great. I burn wood but don't allow it to get "roaring" (again, paranoid). You mentioned coal . . . does that burn a lot hotter than wood ? Something to think about.

Re: Wood Stove

#7

Re: Wood Stove *LINK*

Galen Vetterick

If your shop concrete floor is subject to moisture near the walls put a floor protector down under the stove as it can get hot enough to create steam and pop the floor.

Use black single wall pipe inside and a commercial wall protector sleeve for side wall.

Use double wall stainless on the outside. It holds the heat for good draft and fire protection.

Start your vertical run with a tee and bottom plug for easy clean out. They make support brackets to brace off the wall and support the vertical run.

Do not install a damper if your stove has a built in one as most newer stove do.

The chimney needs to be 36" minimum above the roof or 24" above any point 10' back. It does not need to be measure above the peak.

I had a Vermont Casting stove similar to the one attached. Look at the users manual for suggested but follow local codes as needed.

Mine was in lower family room walkout so went out the side wall and up two stories and on low side of roof. Started well with crumpled newspaper to create a flash heat to start draft on cold days.


http://www.vermontcastings.com/products.asp?model=vigilant

Re: Wood Stove

#8

Re: Wood Stove

mark

Thanks so much for the responses! My shop is not studed, rather it just has horizontal treated 2x6's every 4' up to nail the metal to. So im guessing that the shop is probably about 90% metal. I bought the black stove pipe from lowe's. The stove is one of those iron stoves with 4 legs sort of like what you see at Lowe's or Tractor Supply. the only reason I wanted to exit the pipe out the side was because I didn't want to cut a hole in the metal roof. So do I still have to run the pipe so many feet above the highest point once the pipe exits the shop? I live in the country so I have no codes I have to go by, but I still want to be as save as possible. Thanks

Re: Wood Stove

#9

Moses Yoder

Re: Wood Stove

Moses Yoder

What country do you live in? If in the USA, I believe there are codes that will apply. Each county has inspectors who have jurisdiction over the whole county I think, not just within the city limits. Many people remodel their own home and pay no attention to codes or inspections, then when their home burns down the insurance doesn't need to pay. Another thing to keep in mind is that your insurance adjuster will want to know about your wood stove if the shop is insured.

Re: Wood Stove

#10

Re: Wood Stove

Curtis Gray

You may want to reconsider running the pipe through the wall rather than through the roof. If you run through the wall, you will be replacing the elbows once per year. Proper way to run through the roof with a metal roof is to have a sheet metal man fabricate a roof jack that is made per the pitch of your roof. Good luck.

Re: Wood Stove

#11

Re: Wood Stove

Bill Turpin in WNC mountains

Mark:

I stated earlier that the clearance to single wall pipe as 36", however it should be 18". The clearance to a simple, metal stove, without insulation or a blower is still 36". Take a 36" stick and wave it in all ways from every part of the stove to anything that will burn or is combustible. If you put the stove in a corner check the stove corners. If your stove is ~30" high, then the 2" x 6" at 4' high will have to go or the stove will have to be far away from the wall.Do you have a 8' to 9' diameter circle free of any thing that will burn?

Install the pipe with the crimped, male end facing down towards the stove. This will prevent the creosote from running on the outside of the pipe. Metal covered wood or conduit also must be kept away.

If you penetrate the roof with the pipe, it must go above the roof (at the penetrate point) a minimum of 3'. It must go at least 2' above any point on the roof that is within 10'. This will prevent downdrafts and help to lessen smoke when the wind blows.

Smoke pipe installation is a common web topic. Do a Goggle search.

A vertical sheet of metal, installed with one inch wall spacers and one inch away from the floor creates a chimney effect to cool whatever is behind it. This will cut the 36" distance to 24". Measure with a 24" stick from top of stove to combustibles to determine the sheet's needed height. Think of the clearance as a sphere, not just a flat object

All of these are why I do not heat my small shop with wood scraps. In old cabins they used to use the stone chimneys to support the rafters. Since most chimneys were not 36" thick, after about ten years a chimney fire would burn the house down. Talk with the local VFD since you are in the country.

Re: Wood Stove

#12

Re: Wood Stove

mark

Well, Here in this part of Tenn. If you dont live in the city, you can actually add on without a permit. I know because I called the city and they said I didn't need one if your outside the c. limits. But you have to have one in the city or not for new structures. When I lived in the city,you had to have a permit just to set a yard barn down on you property. but not outside the c.limits

Re: Wood Stove

#13

Re: Wood Stove

R Payne

Maybe you can add-on without a permit. Maybe not. I don't know the details of where you are but where I am in Ks, I'm outside the city limits and wouldn't need a city permit but would need to contact the county for a county permit. If you live in the US there are national codes (I know minimums for electrical and plumbing I don't know if there is a national code for stoves) then there are state codes, county codes and city codes. To be sure you are within code, contact whichever has jurisdiction over where you are, either county or city.

ron

Re: Wood Stove

#14

Re: Wood Stove

james runchey

Mark, when I did my woodstove. my neighbor, who had a lot of experience laying block, came over and we laid up a precast block chimney in about 6 hours . It is maybe 17' high overall. I made a flashing to fix the hole through the roof. Whole thing done in one day and makes a great chimney. Very fireproof.

Re: Wood Stove

#15

Re: Wood Stove

Keith Newton----Little Rock, Arkansas

Mark, If you have a ridge down the middle of the roof, then just to one side of the other of it will take care of easy flashing on that metal roof, and eliminate a lot of other problems. Even if the roof flashing boot can't get under the edge of the ridge, you can make a flashing to go above the lower and under the upper, to keep from damming up the troughs.

Nothing works better than a long straight up flu, and you can be getting heat out of that flu until it gets to the attic or roof.

During these long really cold nights, you may / will want to really load up the stove, and close the intake and flu dampers to keep a fire going all night. You can come into a warm shop in the morning, and still have coals. But if you plan to put a couple of elbows in and have a lot of pipe out in the cold, you need to start learning how refineries work, because that is the process you are heading toward.

Uh,,,,,,,,,,, hum, I knew a guy once who thought it would be easier to make a few turns to locate the stove where he wanted, but not under where he could go straight up. I won't mention his name. He thought he was smart, but he was really ticked when he had to undo everything, and start over.

Keep it painted black, to get the best radiant heat transfer.

Re: Wood Stove

#16

Re: Wood Stove

mark

just for the record, we do have codes,very strict codes,but different states have their own restrictions as to what you can or must do. For instance, I'm not a licensed elect. but where I live, I can do my own elect. on my own house. If you screw up, they won't allow you to do it again, and you may be refused insurance. But, there are alot of things that is just too much to go into. The main thing is to call and make sure you're within code.

Re: Wood Stove

#17

Re: Wood Stove

FredD

County permits on Kansas depend on what county your in Ron.

In Dickinson county where I live a permit is required for new construction , but there is no code officer per se, or inspection, the permit only tells the Assessor how much to jack up you property tax.

The only place I ever lived that is still firmly entrenched in the 19 th century.

FredD

Re: Wood Stove

#18

Re: Wood Stove

FredD

Good, accurate answer Curtis.

FredD

Re: Wood Stove

#19

Re: Wood Stove

R Payne

You are correct. I didn't intend to imply that all of Kansas was a particular way. What I meant by "where I am in Ks" was the county I live in. There are a few places left that even allow new construction without permits (or permits that are only for appraisal purposes with no inspections) if you intend to live in the structure yourself.

ron