dumbwaiter findings
Gary Smyth
Several days ago I posted asking about how I might install a dumbwaiter. Several suggestions were provided. One response mentioned to be aware of the possibility of fire traveling up the laundry shoot. I stopped in at a local fire station to ask about building the dumbwaiter and was referred to the building inspector. Today was Veterans Day (Hoo Rah) and no one was working but the fire guys told me several things. 1. The old laundry shoot has to be removed and in its place a metal self-contained duct where the car will fit has to be installed. The new duct has to have a top and bottom and wiring openings sealed. 2. The �doors� at the end of the floors have to be metal and must close. The duct has to be isolated from the wall framing. 4. A smoke detector has to be at both ends of the duct. 5. The motor for the car has to be a fire rated motor. Then they told me I would also need a permit and inspection. Basically they treated this as a small elevator.
I shouldn�t have asked. Another person will do the dumbwaiter. relative of mine or not I just don�t want to take the chance.