My jointer is listed as a 15A 230v motor. I am currently wired with a 20A 2 pole breaker, 12 gauge wire and the recommended plug (I forget the number, it's what Grizzly stated to use). I'm moving some wiring and reading up on things. Is this something I should have used 10 gauge for or is 12 easily able to handle the volts? Or should I be looking for the jointer's wattage to determine the wire size?
Also, has anyone here hooked up the Jet Xacta 3HP saw to know what size cord and type of plug to use? Mine didn't arrive yet, but I'm checking the manual to see what I need and it doesn't say.
The question I would ask is what is the distance of the line from the breaker to the jointer? If it is 100' then #10 would be better. if it is 50' or less I would say that you are fine with #12.
I'll concur with Howard in general terms about the wire size (there are tables that show voltage drop for a particular wire size and amperage). Just to be technical, it's not the voltage the wire size needs to handle, but the amperage. Think of voltage as pressure, amperage as flow - undersized wire will reduce the flow and restrict the pressure. This is an incomplete metaphor, but works for this example. Most any code-rated wire should handle residential voltages; if you get up above 230 volts, you need to consider the type of insulation, but not the wire size per se.
Why not call Jet and ask them? Tell them you're in the middle of rewiring your shop and need to know what you'll need for the saw when it arrives?
When I wired up [funny term, eh?] my shop, the primary 220 feed was done with 10-3wg and a 25 amp breaker.
Overkill? Not necessarily, because I have an 18" bandsaw, planer, and 3hp lathe plugged into the same circuit as well as 2 4x 110 outlet boxes pulled off for ancillary use. The 25 amp feed insures that I've got enough juice for the start phase on the 3hp motors without dimming the lights.
I used 12ga heavy jacket wire for the extension cord from the wall to the saw and a 25 amp-rated 3-prong plug. The extension cord is needed because my saw is (as are most everything in my shop) on a mobile base to move.
#10 AWG copper wire in a insulated sheath is a 30 amp circuit.
Generally speaking which seems to be the approach around here , 230V machines are one to a circuit , never have seen multiple Machines or appliences allowed.
In a one-man shop, with all machines working from outlets rather than hard-wired into the circuit, and only one machine running at a time, all is well.
Now the big compressor and the 2hp dust collector are both on separate 220 circuits so that they can safely and properly run at the same time as a shop saw.
Mark is correct for a one-man shop. The only time I can see a problem is with some idiot of an inspector that might not like the setup. And there are a lot of idiot building inspectors out there.
When I built my house 10+ years ago I was just over the line where building inspections were not required. Across the road, 150 yds away, they were required. In 2007 the county changed the rules so that all of the county is treated the same requiring inspections. My observations have been that many of the county inspectors are just incompetent. It is strictly a revenue increasing operation for the county as far as I am concerned. Considering the state of the economy I guess I shouldn't be surprised.
but in defense of those with good intentions, there's an awful lot to know. Consider that they're inspecting the product of multiple trades, each of which individually requires an apprenticeship all its own to reach full competence.
My parents had one inspector on my father's looooong remodel who got upset because he'd exceeded building code. Dad was at work, and Mom had to ask him, so what code violations are there here? None, he said, he's just exceeded building code.
She called the supervising building inspector, and that particular one never showed up at the house again.
Around here you get a different inspector for each trade; sparky, puddles, woody, and the mechanic. We gutted our kitchen 2 years ago. Had two guys in twice each. They each actually caught one or two deficiencies that the GC had missed. I used it as a test to see if they were doing what they were supposed to be doing so I didn't have to correct the GC.
which has been a problem in the past. One past inspector, who was very weak on structure, told me he wanted an engineer's stamp on our drawings and that he'd then be sending them out for a second engineer's review and charging us. I never followed through on the small project; the engineering costs would have exceeded the materials costs.
The current inspector is sharp and very supportive of homeowner-remodelers. I'm hoping he'll keep working until I'm done with the work on this house.
A word about Inspectors, Howard, they are critical to a safe ,competently built Residence and a Buildig Code enforced, results in lower Fire , Police and Home Owners Insurence costs and after years of being in place, a much better housing stock and yes, a larger revenue for the City or County.
Ask any Fire Marshall, Police Officer or Insurence agent or a person like me who is a retired General Contractor who welcomed the inspection , signed off so the Bank backing the construction loan would issue the draw, which kept all of the people engaged in the building of the subdivision or custom house employed.
Only incompetent , untutored people who have either something to hide or can't pass a inspection disparage Building Inspectors.
There are one or two who frequent this forum and I venture to say they resent someone outside of the Industry referring to them as idiots.
Like any industry , I have in the past run across some Inspectors who needed to find a another way to make a living , but they never last very long and there is always a remedy for that individual.
County/city inspectors are not critical to a safely built house Fred. I disagree completely with that premise. Competent tradesmen are what is critical to a safely built house. Unfortunately there are a lot of incompetent tradesmen out there also. In the case of incompetent tradesmen an inspector can solve the problems created by that person. However in this county, Yavapai County in AZ, the 2007 decision to insist that all parts of the county be covered by the inspectors was strictly a revenue enhancement decision I am sure.
This last winter a GC friend of mine was building a log home several miles off of the paved roads. The only way that he could get there during the winter was by using four wheel drive. The county inspector insisted that he have a Porty Poty on the site. The provider of the PP refused because none of his trucks could get to the site to service the unit. This went on for over a month. The GC finally purchased a PP and put it on the site and then never used it but the inspector was satisfied. If that isn't asinine I don't know what is. The GC has now said that he has built his last log home in this county even thou he has a backlog of people that want him to build that would take him two years to complete.
Your experience in Northern CA may have been with competent county/city inspectors but that is not the situation here.
I don't know that I made it clear in my earlier post that I see the inspector as a partner in making my work sound and safe. Even the act of developing the drawings for the building permit forces me to think about what I'm doing and improves the design.
Before we bought this house, we saw some unpermitted work on some of the houses we viewed, and, as I said in another post over on the Turning board, some people shouldn't be permitted to hold a hammer. Not all unpermitted work is bad, but good inspectors encourage or enforce safe work.
Looks like I am doing the right thing and I can continue along those lines. I'm working in my own garage and we don't require inspections here. I do keep my big tools on separate circuits, right now just the jointer and soon to be table saw. Even at 1 1/2 horse I run the DC separately whenever I can. Since my shop is small and very moveable I have a couple of circuits worth of receptacles to keep from ever overloading any one.
Next up is to wire my newly cleared and painted concrete wall. 5 20A receptacles split over 2 circuits and I'm going to move the 20A 230V circuit for the jointer onto this wall as well. I'm going to try a new mounting option for everything. Run a strip of 3/4 ply down the wall, nailed onto the concrete. Then mount the boxes and conduit to the wood. I find that is much easier to do than screwing into cinder block.
I've never had a whole lot of luck with liquid nails holding over the long term, but some kind of filled polyurethane adhesive will help keep your strip nailed to the wall. Things nailed to concrete block seem to fail from frequently repeated small tugging loads - like pulling a plug from an outlet. Personally, I like 1/4" Redheads (those nail in sleeve expanders) for conduit and boxes on a block wall.
I was going to grab one of those powder actuated concrete nailers. My electrician use one to attach the board the panel is on and it holds super tight. Maybe some liquid nails underneath for good measure.
Stuff up, include a couple of 20A GFCI duplexes to put in as the first outlet in each of those 115 circuits. In my neck of the woods, any 115 circuit in a garage MUST be GFCI. While you should test their trips each month, people rarely do, so get the units with the LED tell-tail to alert you to the circuit having been tripped.
Howard, you can disagree all you want to ,this seems to be your theme.
It sounds to me like you have chosen to live amongst people who have rug burns on their knuckles on purpose , excuse me if that is not the case.
As for your assertion that Inspectors are not critical to well built , safe to live in housing , you are a lone voice in the wilderness.
Simply put, people left to their own devices produce everything from a nightmarish safety hazard to liveable abodes that one need not fear for safety in....
Since we are dealing with all types and personalities and skill sets , it follows that the product is not uniform and dependably safe.
Therein enters what used to be called the Uniform Building Code and enforcement of it for all of the reasons I stated in the previous post, none of which has changed.
I now live in the country outside Abilene , Kansas and I own several homes as rentals in Abilene and the Uniform Building code is the same one that California used and permits are required and have to be signed off .
As for portable Toilets on construction jobs ,they are required everywhere I have any experience in.
For instance ,the Carpenters Union requires one for every fifteen men on the job. State Health and Safty codes also require them.
Regulation in Home Building is absoulutely required .
If you were to apply for a construction loan at a Bank that backs them and during the application process ,mentioned that you didn't need to have Bank draws attached to signed off inspections of the various stages of construction , because you knew all you needed to know to build the house and you didn't trust the local subcontractors and in your opinion , Building Inspectors were not needed and idiots to boot, how far do you think the application would have gone , before it was denied?
Better yet , why don't you go to a County Commission meeting and tell them all of the reasons you know for a certainty , that a Building Code enforced by a Building Official is a bunch of Crap and the local Sub Contractors are in league to fleece the population and it puts a unbearable strain on you to conform?
Asking for advice on electrical work in a woodworking forum just doesn't seem like the right thing to do. Find a reputable local electrician that knows the codes in your area, it's well worth the piece of mind. Even the manual for your saw states that it should be hooked up by a qualified electrician. Atleast get an estimate, it may not be as expensive as yoiu think. As far as the electrical cord and end, someone at JET should be able to tell you weather the saw comes with one or not.