#1

OT - roof flashing question

DouginDenver

I have a two-story brick house with a one-story addition off the back. The addition has only a slight pitch to it, so the roof of the addition meets the brick back wall of the house at maybe 5 degrees over 90. Where the roof meets the wall has always been a leakage problem. Currently the roofing is just run up the wall a couple inches, with lots of roofing tar behind it and over the edge - no mechanical flashing. The sun bakes it and it cracks. So I want to redo the roof.

If I go to Home Depo type places, the only flashing I see is a strip of galvanized bent at 90 degress. That doesn't seem to be the answer because I can't see how to get a tight seat to a brick wall. On This Old House they use a strip of soft lead and put it in a mortar line of the brick. That is a lot of work, and my mortar lines are the real thin "bread and butter" type, so I would not be able to add mortar to hold the flashinh in. When I look at new roofs around the neighborhood, they seem to flash chimneys with an aluminum channel with some sort of rubber seal in it that is screwed into the chimney. That seems hopeful, but I've never seen it for sale or seen it close up. So, how does one flash a slighly pitched roof to a brick wall? Thanks.

Re: OT - roof flashing question

#2

Jason Roehl in Lafayette, IN

Re: OT - roof flashing question

Jason Roehl in Lafayette, IN

Flash, and counterflash.

You'll need a continuous strip of flashing that lays flat over the top course of shingles, and flat to the brick. It should be 5" or so onto the shingles, and at least 4" or so onto the brick, preferably more. You'll want to nail it through the shingles about 1" from the bottom edge about every foot or so, then seal the nail heads with butyl rubber caulk. The top section of the flashing just stays loose to the brick--it gets counterflashing over it.

The way to make the counterflashing is that you first make a bend at the top of your piece of coil stock, 90� and about 1" deep. Then you make another bend back a little beyond 90� and wider than the mortar joint in your brick. (Review--if you're facing the outside of the counterflashing, bend the top away from you 90�, then bend the far edge of the top back towards you more than 90�). You then cut away the mortar the depth of the wedge (angle grinder with a masonry disk) you made in your counterflashing about 8-10" up from the roof. Then use self-sealing sheetmetal screws or rivets and butyl caulk to attach the counterflashing to the loose flashing behind it. Then re-fill the mortar joint with either mortar (a little more tedious), or mortar-colored caulk. Don't use the cheap, thin aluminum coil stock--a good wind will rip it right off.

It sounds more complicated than it is, but it is a little time consuming and tedious to do if you don't have a sheet-metal brake. I've done it with a simple set of sheet metal bending pliers (2 large flat jaws with measurement marks on them).

Jason

Re: OT - roof flashing question

#3

'Round here...

Tony - Memphis

They step flash against the brick, then they install a piece of flashing that looks like it is made for this purpose. It has a slight bend such that it fits over the step flashing. This piece is simply siliconed in place. Now, in ten years, when the loose mortar they smeared in with the silicone falls out, you get a leak! A big leak! Long story, but I had to go buy a 28' ladder to get up high enough to fix it. Even then if the rain is blown hard enough to travel up to where the flashing stops under teh eave (spell that?), it will leak. We had katrina damage all the way in Memphis. The wind blew hard enough that it pushed the rain up and it found its way down to a ceiling. Other than that, the technique works ok. If a better install had been done, it would have never been a problem. There are thousands of homes around here with the same setup.

Tony

Re: OT - roof flashing question

#4

Sounds like you may have two problems

Bill Houghton, Sebastopol, CA

The flashing/counterflashing that Jason Roehl suggests is the way to do it.

It's hard to "flash" a low-pitch roof at the top edge. You need to seal your flashing to the roofing, which creates a problem because the roofing, building, and flashing expand at different rates. So, as Jason suggests, fasten the lower edge of the flashing to the roofing and caulk the living daylights out of it, using a flexible caulk. Years ago, butyl was the standard, but there are others now. Your best caulk for the purpose will be a bear to use, and you'll wind up covered in it; in some ways, the test of a good caulk for this purpose is that you should wear your worst clothes when doing it, and change before you set foot in the house, because they'll be a mess.

I was always taught that the counterflashing should not be attached to the flashing, but I have limited experience here; and if you're in a high wind area, you may need to fasten it. Caulk freely if you do.

The best mode of thinking when looking at flashing details is one I heard years ago: "Think like a drop of water." You want your drop of water to be encouraged to go out at all times.

Re: OT - roof flashing question

#5

Re: OT - roof flashing question

FredD

Doug , flashing the roofing is actually easier then has been described, especially if you own a SkilSaw or similar brand of circle saw.

The hardest part is cleaning away the roofing that is run up the brick surface.

If your going to reroof so much the better, then do this.

Take the saw , install a Masonry blade available at all hardwares , , set it for a 1/2"depth of cut , cutting from right to left will have the saw running on the table edge closest to the blade and will give you a slot a 1/2" deep , about 1 1/2 inches up the brick surface.

Much deeper then that , you would be inviting a brick failure.

Have a sheetmetal shop bend you a strip of 26 GA. G.I. about five inches wide , so that it looks like a Zee bar with a 1/2" lip at right angles to a flat of 1 /1/2 inches and then out onto the roofing , set in a bed of roofing mastic and nailed down every foot or so.

At the top edge where it runs into the slot caulk with a bead and your done

Re: OT - roof flashing question

#6

Re: OT - roof flashing question

Barry Irby

Jason got this right.

What you have is the lazy way of doing this and is quite common locally. Around here it is called a "Gummy Top" It fails as soon as the gummy stuff turns loose.

What Jason describes is called counter flashing and allows for the flashing to move as it does and then the flashing can remain secure. The slot for the counter flashing is called a Reglett. You can cut the reglett with a circular saw and a masonry blade. Set a 2x4 or whatever on the roof to raise the saw and cut the groove. You might have to make two passes to get a groove wide enough to do the job.

I have not had as much trouble with eh caulking as Bill did, but it is inclined to get from a$$hole to Eyebrow, so the old clothes are a good idea. Also, have a roll of paper towels handy to keep things clean as you go. Also, practice releasing the pressure on the caulking gun each time you stop.

There are other things to look at as well. If you are in snow country you should raise the height of the flashing to six or eight inches. Also, examine the wall above carefully. Look for voids in the mortar. If you are on the windward side of the house, you cold have wind driven rain passing right through the joints and leaking down the back side of the wall. (Not a roof or flashing leak at all.) And, it would be good if you had a wide roof overhang above and gutters to keep the rain and drip off the wall. Many of these leaks I find on home inspections are caused or greatly aggravated by water splashing off the adjacent roof. Since you have the buttered joints, I am assuming your brick have slick faces. If they are rough or particularly sand faced, all bets are off.

Re: OT - roof flashing question

#7

Jason Roehl in Lafayette, IN

A picture to help. *LINK*

Jason Roehl in Lafayette, IN

Instead of step flashing, you would want as continuous of a piece of flashing as you could manage. If you have to use more than one piece, overlap them by a foot or so and put a couple lines of sealant perpendicular to the fold.

Jason


Counter Flashing

Re: OT - roof flashing question

#8

Caulking guns

Bill Houghton, Sebastopol, CA

"...practice releasing the pressure on the caulking gun each time you stop."

And spend a little extra on a good gun. It took me a long time to learn that the more expensive guns cost more because they're better.

I would NOT buy one of those guns with the built-in caulking-tube hole-poker, because I always wind up with caulk on my fingers from the hole-poker; but one of the guns that automatically backs off a bit when you let up on the trigger is well worth it.

Re: OT - roof flashing question

#9

They all work better after....

Barry Irby

the tube of caulk f@rts or should I say passes gas. If the tube has an air bubble, it compresses as you squeeze out the caulk and then continue to expand once you stop.

Re: OT - roof flashing question

#10

Re: OT - roof flashing question

Justin Szeliga

In a situation like this you will need a cant strip, a piece of wood on top of the roof deck & against the wall which makes the transition from roof to wall into a 45 degree angle instead of the 95 degrees it is about now. Then run your roofing up the roof about 6" above the cant strip, attaching it to the wall & then covering with the counterflashing to about 2" above the top of the cant strip. If you install the flashing w/caulk you will need to watch it as the years go by as all caulk is going to fail. Using a urethane caulk like the kind CR Laurence makes will greatly extend the life of the flashing to brick joint & the cleanup time. If you install the flashing w/a soft mortar, lotsa lime in the mix, that would work well to but the kerf needs to be wide enough & undercut if you can to help lock the mortar in the joint. Your roof needs to be high enough to not have snow melt, driven rain, & what have you run up under the flashing & into the inevitable gaps between the brick & the roofing.

Re: OT - roof flashing question

#11

Re: OT - roof flashing question

Hamish

Dougin, what nobody has mentioned is the possible problem of condensation. I have a similar low angled roof abutting my house, and at the moment it is completely sealed to the smooth house wall with a wide sticky strip. This works well at keeping the water out BUT I have noticed on hot days that drips of water appear from under the high end of the roof, caused by condensation.

My approach to rectifying this will be to flash the roof to the wall with aluminum strips that have first been bent to a step shape. I will not use galvanized sheeting for this, as the galvanizing will crack along the fold line and rust in time. They will be either cemented into the wall along a cut made with an angle grinder or fixed with screws and covered over with the sticky band that I have used before without problems. The step shape of the flashing, will allow a breathing place for the air to escape from under the roof and stop the condensation.

Hope this helps. Hamish.