I'm talking about the electric meter on your house. My house only has 100 Amps, which is fine for the house but I want to get a shop running in the detached 2-car garage. That would require at least one 20A 240V circuit and 2 20A 120V circuits (one for lighting and the other for whatever tool I have turned on plus a small dust collector)
There's no way these will fit in my current panel. So I have looked into getting an upgrade. That's expensive and still doesn't get the power out to my garage. I'd have to pull wire out there too. But my utility pole is actually in my back yard, right next to the garage, so my thoughts are it might be significantly cheaper and easier if I could just get a 2nd 50 Amp service from the utility pole directly to the garage. Has anyone succeeded in getting a utility to do this for you? Specifically it would be PSE&G. Thanks.
You might want to re-think this. Several thoughts come to mind. 50 amps is not much for a shop and your existing 100 amp in the house is obsolete. If you have 2 meters you will have to pay the minimum on each even if you use nothing in the shop for the winter months. Future buyers will want 200 amp service, even if you don't think you need it now. Some utilities structure the rates so that after x number of kilowatts the rate drops, with two meters you may not reach this threshold.
I work for a municipal utility, and we do this frequently. It's no big thing, but might involve some digging or overhead, depending on your service. Call them and find out.
I'll get poo-pooed from most for this but here goes . . . I can just imagine the complications a second of ANY utility at a residence is going to add to your life. I'm SURE there are very rational ordinances, laws and codes that allow one to do this but . . . I can't help but think that the city, county, state and feds will all be around to check on one's motivations. An up-grade to a larger panel in da' house was my choice. Expensive , yes, but I wasn't explaining to every civil servant in town what I was doing.
( No, I don't think EVERYTHING is a conspiracy. Just most things. )
Your residence is under powered by a significant margin. I strongly suggest that you upgrade your service to, at least, 200 - 300 amps, through a load center situated in . . . Riiiiiight, your shop.
You'll then pull a small panel off the load center to power the shop, and the balance goes back up the pole and over to the house with a single meter located on the shop exterior wall. Helped my FIL do just that with no issues.
You will, however, need a licensed sparky for the job, so pucker up and get'er done!
I solved this problem by by consulting with the local building inspector (didn't realize he was the father of a former student, might have helped). He recommended that I get a dual parallel meter base on the back of my shop and hook up a 100 amp panel in the shop and keep the 200 amp entrance in the house. This allowed one meter to serve 2 separate entrance panels with no sub panel and no disconnect required. When I explained to the electrician what I wanted to do he said it was a perfect solution to the problem. We ran the wiring from the shop to the house underground. It makes for a nice looking setup. Apparently the dual parallel meter base was kind of expensive. The utility company provides meter bases at no cost here. When I went to pick it up, they objected saying it wouldn't meet code. When I told them who recommended this set up and said that he said to call him if there was a problem they immediately gave it to me, and told me to have a nice day. It has been a great solution--no problems at all.
My utility shed was not far from the meter on the side of the house. I put in an 80 amp main breaker box and circuits for a 220 welder, 120/15 amp lighting and other 120/ 20 amp circuits for tools. I installed it all and ran the line over to the meter. Had my rural electric company come out and they connected the new line right into the meter box and resealed it. No cost.
I had somewhat the same situation, having only a 100-amp box in the house (and no way to put in a 200-amp unless I move the panel to the other side of the basement garage door).
The shop, though, has a 200-amp, 3-phase service, and I don't worry about overloads. I do get two power bills. The one for the shop usually runs around $22 if I haven't been out there too much. BUT . . . here's one thing to watch out for: The power company installed a demand meter on the shop, considering it commercial despite my protestations. If I pull an average of 5KW or more for a period of 15 minutes or more, my rate goes way up and stays up for several months. I've been careful not to do that. For example, I keep the breaker to the air compressor flipped off unless I'm using it, so it doesn't come on at the same time as the dust collector, all the lights, and the table saw are all running.
Bottom line: No problems, nice setup. Recommended.
When I built my shop, which is 75feet from my house, I had separate 200 amp service with meter run from the transformer on my driveway. I also installed the panel and interior wiring, including 3 x 30 amp 240v circuits and a 40 amp circuit for the heat pump and AC. I get seperate bills for the house and shop.
I have done this twice. When I lived in NC, I built a shop separate from the house. My panel in the house was full. I had the power company install a second meter for the shop. No problems.
When I moved to SC, I again built a separate shop, this time separated from the house by about 200 ft. Again all spaces in the house panel were full. I had a separate meter installed again. However, this time the power company, Duke, treated the second meter as commercial service. This has a higher minimum rate than my residential service. Works well but is somewhat more expensive.
I would recommend this solution if your utility does not charge significantly more for the second meter.
I asked my local utility, National Grid in upstate NY, about the same thing. Have 200amps in house and wanted 200 more for the garage shop. I figured another service could be run directly to the garage. They recommend upgrading the house and then running a line out to the garage. Their reasoning was that if the power didn't go to the house first it would be considered commercial use and rates increased accordingly.
Code in your area may vary, but around here, it's code to have a subpanel that is equal in amperage to the main panel. If you've got enough slots (two, one for each 120V leg) to run a breaker from your main panel to a subpanel in the shop, you may be able to get the circuits you want.
I've got a 60 amp subpanel for the shop and a 40 amp subpanel for a second shop building (my wife's), and expect, if I ever build the shop of my dreams, which is a two-car garage, to run an additional 80 amp subpanel, all from our 100 amp main. When I was considering all this, I talked with a very competent union and licensed electrician at work, and he confirmed that daisy-chaining like this is perfectly OK, as long as no subpanel is "fused" at a higher amperage than the main panel.
There are some additional requirements: both the outfeed from the main panel and the infeed to the subpanel need to have a breaker of equal size (that is, don't use a 100 amp breaker on the outfeed and an 80 on the infeed), and you'll probably need to drive a ground rod for the subpanel in addition to your ground rod for the house. Follow good equipment grounding practices on the subpanel - that is, you need a separate ground wire from main to sub panel, which is NOT bonded to the neutral bus, need a separate ground bus, etc. Run either big enough UF wire or wire in conduit, paying attention to depth at which wire/conduit is buried, and so on. Calculate the voltage drop and oversize the wire by one gauge.
Folks have been saying that 100 amps is too small for a house. That may be true for houses with electric hot water and in areas where air conditioning is required. Our place has had 100 amp service for well over a decade, and we've never had a single problem with overloads. Remember that, even when the fridge, oven, and so on are running, the total load on the panel may not be all that great, if it was balanced properly.
Which brings up: get your load balancing right on the subpanel: don't run, for instance, your compressor and your dust collector, tools that may be running constantly, on the same leg.
I have 300 at the house and 200 in the shop, transformer at each location, no problems whatsoever. One bill with two line items, no minimums. However, I have found that each utility is totally different. A friend is trying to put in service at his empty property and Duke wants $1500 just to put a single pole at the front of the property. My service, REMC, put in 3 poles, two transformers for nothing. I had to pay for the underground from the last pole to the house because they contract that out at $1.75/ft.
Regardless of what seems to make sense, you have to understand what local code practices are. Even though there's a limited number of building/electrical codes, everybody has a local set of rules.
You may find practice in your area is like this part of California; you may find that it's more restrictive. So do your research before proceeding.
Depends where you live , some states like Ca for instance, the major utility is PG&E and they only allow one metered service per residence.
Regardless of where you live , get a licensed Electrician , tell him what you want and he will tell you how to go.
People who have 100 amp services live with them and adapt to some of the eccentrics of a underpowered service.
Where I presently live , the home we bought in the country didn't come close to the power needs of a modern home , Barn and fully equipped shop.
We upgraded the service to 300 amps at the pole, after I had the utility company move the pole closer to the highway and under grounded all of he feeds with direct burial cable , which wound up with a divided service panel at the house and one half at the shop and a Main breaker at the pole.
This is probably more then your looking at , but you get the idea, I would suggest strongly to get more capacity then you think you need , rather then trying to guess how little you can get by with .
Also a upgraded service change gives you a leg up over lesser homes power in the event that you sell down the road.
My power utility (a co-op) would have required me to put the service entrance within 10 feet of the corner nearest where the power came on to my property. No way would they have let me put in two meters. In order to use the original service entrance (whem we set the house and shop back down the relastionship to the power transformer was different)the co-op let me install a mobile home service entrance at the property line and then I could run the power however I wanted, at my expense, the co-op also "let" me install the line (1200 feet) to my house and then give it to them, $28,000 to the property line, another $3,500 or so to the house. Oh well I love my house and location, and yes I would move a house again.
They can even vary from one power supplier to another in the same general area.
I have always found the difference between the several REMCs around here and the "other" power supplier interesting. The "other" at the present time is Duke, but when I first started doing electrical work 35 years ago it was Public Service Indiana. Then for a while it was Cinergy. I have pretty much quit doing electrical work, but I'm pretty sure that Duke requires the same installation as the old PSI.
PSI always preferred that the ground wire from the panel not pass through the meter base. They would not connect the power if the meter base and panel were bonded together. It was unsafe.
All three of the REMCs were/are exactly the opposite. They considered the installation unsafe if the meter base and panel were not bonded together. They really preferred that the ground wire be one continuous piece, but they usually allowed the use of a terminal block in the meter base.
Both could give good reasons for their respective policies. Since I�m not a double E, I have never concerned myself as to which, if either, of them were right. I just did it the way they wanted.
Ron Jones� reply above about what he had done mentioned not needing a disconnect. For quite a while, around here anyway, any panel that is more than ten feet from the meter base requires a disconnect between the two. I can see what he did possibly getting rid of one disconnect, but not both.
Bottom line. I have always avoided getting into code discussions here because, NEC aside, there is just too much variation from one place to another. If it were me, I would do just about anything to avoid having two meters if I could get by with one.
I have a three car which had a 40amp box already installed. I put in new circuits, wired up new outlets with seperate circuit breakers. I do run 220 saw and 220 jointer...less amps. I seldom run two machines at the same time. One instance is the dedicated router table with the shop vac...no problem. The other being the saw with a 15amp dust collector. Maybe this would be the way to go and save.
Not necessarily. The zoning, local code requirements, building permit requirements, and union influence will determine who may/must do the electrical work. When I did mine, I did everything but hanging the meter and running the line from the xformer to the mast and I'm not licensed. I had to have it inspected to get the CO.
Licensed as in a masters certificate, as opposed to a old retired elephant trainer , wood worker , housewife and like that.
I am not aware of any current up to date jurisdiction that will let a homeowner upgrade his service , but I suppose there are some places still doing it .
That went out in California years ago.
Regardless of the permitting process , the Electrician is the qualified person to survey the work and recommend what is needed.
Anything less is risky and in many places illegal and to suggest to a person less qualified , that he can do it his self , does him a disservice, puts his home owners insurance in a position to bow out in a fire caused by faulty wiring .
but my California mileage varies. I did a full upgrade, from knob and tube frightening wiring to breakers, in 1996, myownself, under a permit, with no trouble. Just this March, the inspector signed off on a bathroom remodel that required replacing the main subpanel in the house (the main itself, because of space constraints, doesn't have enough spaces, so the house runs off a subpanel), because it needed more breaker spaces for some of the added circuits.
Maybe it's my semirural, used-to-be-farm-country location.
I agree with Fred that people who don't know what they're doing shouldn't do electrical work. Of all the building trades, it's probably the most dangerous if done wrong. It's not rocket science, and someone who's basically competent and capable of careful work after thorough research can do it; but it's really easy to do wrong if you miss one of the steps.
Power comes down the pole, through the meter and at the base of the meter there is a means of attaching a 2nd wire- one to the house and a second smaller wire to the lumber shed. I ran a 60 amp service to the lumber shed (can't remember the wire gauge required) and set a breaker box in the shed for 60 amp service. Presumably any electrician could make this installation.
I am nearly certain an owner can entirely build his own house including all of the electrical work. Its grandfathered under the what is locally called "the homestead exemption." I am pretty sure it also applies to upgrading the service, in your own home that you occupy, not rental property.
OTOH, I fully agree that only a qualified person should do this. I bet there are cases of people that have hurt themselves or their property by attempting work they don't understand. So, Don't do it unless you really do know what you are doing.