Posts

O.T. Microwave blowing the circuit

#1

O.T. Microwave blowing the circuit

Stuart Johnson

The built in microwave I installed to replace the bad one in our oven/microwave combination is too robust for the circuit I installed. Here is the background:

The built in that was replaced had a small plug that fit into the top of the the oven. I tapped into a 110 outlet next the the cabinet and installed a regular 110 outlet inside the cabinet for the new microwave. It turns out that circuit includes all the back splash outlets, stove light and one set of overhead lights. Normal use has not been a problem but on Sundays when we plug in the griddle, have the coffee pot and hot water pot all going and then start the microwave the circuit overloaded and pops.

The oven is wired with two hots and a ground with no neutral. So I can't just run a circuit from there. My question is:

Can I replace the hot on my new circuit with a split from one of the oven hot and leave the ground and neutral in the new circuit connected as they are? By the way the question is not just can I do it but is it safe?

Re: O.T. Microwave blowing the circuit

#2

NO

Mark Mandell - Gone Round In Jersey

Re: O.T. Microwave blowing the circuit

#3

That Said . .

Mark Mandell - Gone Round In Jersey

Check the size of the wire feeding the current (no George) outlet as well as the size of the breaker breaker. If the backsplash feed is a 12 guage, and the breaker is 15amps, you can safely go to a 20 amp breaker which may (but may not) solve your problem. Your other alternative is to fish a new feed wire from the service panel to the outlet in question, break one half of the duplex for the separate circuit, and put that half on a separate 15amp circuit for the mic with a separate breaker in the panel.

Of course, if your panel's full and won't take S-M's you're screwed for my suggestion.

Re: O.T. Microwave blowing the circuit

#4

Re: O.T. Microwave blowing the circuit

Bill Turpin in WNC mountains

Stuart: You answered your own question in paragraph #2. OVERLOAD. It is a wonder that this circuit does not trip without the microwave. A twenty amp circuit (you may have a fifteen) is only good for � 2400 watts on an intermittant basis. Only 1920 on a continuous basis, do the math, on each appliance that is on the circuit. A 1000watt microwave pulls at least 13.5 amps on start-up. The microwave needs to be on a clean 20 amp circuit. Did you step up the wattage when you replaced the microwave? Codes have changed in the last thirty years to make room for all the additional stuff. The refrigerator should be clean and the lights should be separate from the small appliances or counter-top. The microwave has an excitation amp draw that is tripping the breaker.

Re: O.T. Microwave blowing the circuit

#5

Re: That Said . .

Stuart Johnson

Thanks Mark. You sort of lost me on the breaking the duplex. What I have done at this point is just added an outlet to an existing circuit. I'll have to check the wire size to see if the fix is as simple as changing the circuit breaker. I have plenty of room in a sub panel to pull new wiring but would like to avoid this option if possible.

I thought a 220 circuit that consists of 2 hots, ground and neutral could be wired to a 220 and 110 appliance by using 1 hot, ground and neutral on the 110 side and 2 hots and ground for the 220. What I'm missing in the existing oven circuit is the neutral. This is why I thought I could use the neutral from the existing 110 circuit. My reasoning is I have 220 at the oven now, how does the new 110 outlet know where the neutral and ground originate? I'm not talking about using the ground as a neutral.

Re: O.T. Microwave blowing the circuit

#6

Re: O.T. Microwave blowing the circuit

Stuart Johnson

Dang, it sounds more and more like I'm going to have to spend some time in the attic. At least it's not August.

Re: O.T. Microwave blowing the circuit

#7

Re: O.T. Microwave blowing the circuit

Barry Irby

Bill and Mark Are right.

You can not tap into the 220 circuit for the range because the National Electric Code forbids it. There are several reasons but I won't go into a long winded explanation. Its unsafe and dangerous. Yes it would work, until it didn't and someone could get hurt or worse.

Bill is right about the circuit. Kitchens are now supposed to have 2 20 amp circuits over the countertop. The fridge and anything else with a motor (disposer and dishwasher) should be on separate circuits and so should the microwave. That's one circuit each.

Do yourself a favor and fish a new wire.

Breaking the outlet means to separate the top and bottom outlet on a duplex receptacle. Look at the side of one and you will see there are two screws and there is a little jumper strip between them. It is easy to break it off and then the two halves of the outlet are separate. You can provide two circuits in the same box by running a three conductor with ground wire. Black/red/white and ground. You could hook the red to one brass/hot screw and the black to the other one and break off the "ear". Then the white goes to a silver screw and the ground to a green. If this is done, the breaker must be a 220 type breaker or "common trip" device. This means both halves of the circuit trip at the same time and it is not possible to turn one off and leave the other live. As a personal preference, I do not like this wiring technique. I think many people would find it confusing and thus dangerous. That's a personal thing and as far as I know this is still "legal" under the code if done properly. You can also branch the circuit after the first box and then it is even less obvious why they would be connected to a 220 breaker.

Ranges used to have 2 wire with ground circuits and no neutral, but when it became the standard to have 120 volt devices such as timers and clocks included in ranges it became apparent a neutral wire was needed. Most water heaters and other devices that use "pure" 220 (240) current still have two wire with ground circuits.

Re: O.T. Microwave blowing the circuit

#8

Re: O.T. Microwave blowing the circuit

Jay

Stuart, the quick answer is no it is not safe. You are correct in your assumption that it should work, it would. Overloaded neutrals turn into heating elements when people "borrow" the neutral from another circuit or move circuits around in panels and end up with both circuits of the network (1 A phase, 1 B phase and a common neutral) on the same phase. The current code requires both circuits sharing a neutral have a common trip, which helps with the moving around in the panel stuff but people still insist on "borrowing" neutrals, or even worse using the conduit (metal conduit is required in my locale) as the neutral. As an electrician for 40 years I personally hate the common trip stuff, and I especially hate the new arc-fault, ground fault requirements. Under the latest code ( fortunately not adopted yet by very many municipalities because of the same concerns I have) just about every opening in residences must have either arc-fault or ground fault and they don't rule out both! Nuisance tripping on arc fault breakers is terrible, and I ain't plugging my freezer, fridge, or sump pump into any ground fault outlet ever! The technology is not as reliable as they claim, we replace bad GFI's a lot. It's a great time of the year to be climbing in the attic, bring a couple extra circuits while your there, sounds like you need them.

Good Luck,

Jay

Re: O.T. Microwave blowing the circuit

#9

Thanks to all, I'll run new circuites 

Stuart Johnson

Re: O.T. Microwave blowing the circuit

#10

Re: That Said . .

Dan Donaldson

One issue is that the oven will be either a 30 or 40 amp circuit, which is too heavy for the wire feeding the plug.

Could you rig up something that would work and not electrocute you? Probably, but it would not really be safe, and it definitely would not meet code. If a fire started, even in some other area and that was found, it might negate any insurance coverage you have.

You really need to run a new circuit for that.

Re: O.T. Microwave blowing the circuit

#11

Whoa, Barry

Mark Mandell - Gone Round In Jersey

Breaking a duplex for an extra 115v circuit is one thing, wiring it as a 220 is another. Code here will NOT allow 115 and 220 in the same terminal box. His mic is a 115 machine, why would he want a 22- circuit? I was suggesting he break the duplex and fish a new 115v circuit for the Microwave. That would call for a 12-2 w/ ground, but not a "3-wire" [2-hot/red) conductor

Re: O.T. Microwave blowing the circuit

#12

Re: Whoa, Barry

Barry Irby

I will have to check on that.

You can wire one half switched and one not, but that would not be 220 would it?

I know you can have two duplex receptacles in the same double box and have one on the red circuit and one on the black. There would be 220 in the box and thus the need for the common trip breaker.

Re: O.T. Microwave blowing the circuit

#13

I don't think he suggested wiring it 220...

John in NM

But that aside, its time to quote an actual chapter, section, and paragraph. If you can have more than one circuit in a box, what Barry's describing with the linked trip breaker is the safest way to have two circuits in one box - when one is off they are both off. But it is not the same thing as having a 110 circuit and a 220 circuit in the same box.

Re: O.T. Microwave blowing the circuit

#14

Re: Whoa, Barry

Jay

Mark, 110 and 220 are routinely run in the same box. We regularly run networks with 2 hots and a common neutral. Breaking the tab and putting the red hot on one screw and the black hot on the other screw ON THE SAME SIDE, and the white on the silver screw on the other side of the outlet is not wiring the device for 220, it will simply give you 2 separate 110 volt circuits.

Re: O.T. Microwave blowing the circuit

#15

Re: Whoa, Barry

Mark Mandell - Gone Round In Jersey

I KNOW that, Jay. But the box in question already was part of another 110 circuit. Running two MORE hots and a common into that box would have made 3 110 circuits in the same box. My suggestion was to break the duplex bridge and run a separate 12-2wg circuit to the isolated receptacle for the microwave's discrete line, thus avoiding having to put in a separate box for the microwave circuit.

Re: O.T. Microwave blowing the circuit

#16

Re: Whoa, Barry and a question for Jay

Barry Irby

Mark, I did not mean to use the same box you were discussing, I was just describing the technique. I was not clear about the box.

Jay, I was sure you had to use a "common trip device" (220 breaker) for this type of wiring. One person i talked to today said it must NOT be a 220 breaker. His argument was that if you pulled two 110 volt circuits out of the same 220 breaker and one side overloaded a tried to trip, the one not under load at the moment would resist tripping and keep the breaker from tripping.

My thinking was it was important the two hots be from the two different 120 feeds and that using a 240 breaker would assure that. It would also assure that if you turned it off, both leads would be off.

So, which is it?

PS. Is it still 110/220 or should we be saying 120/240?

Re: O.T. Microwave blowing the circuit

#17

Re: Whoa, Barry and a question for Jay

Galen Vetterick

Barry

The split receptical with each on it's own 120 volt source is on two breakers with a tie bar so that when the power is cut it insures there is no hot left at the outlet. If one circuit is overlaoded it will trip both breakers just like it would if a 220 circuit had an overload or short on one leg.

The switched split receptical uses the same hot from the outlet out to the switch and back to the other half of the receptial with the hot bar removed.

Think you had things right just getting mixed in the string.

Galen

Re: O.T. Microwave blowing the circuit

#18

Re: That Said . .

Stuart Johnson

I am going to run a new 20 amp circuit to a box inside the cabinet. When all is said and done I think this is the best approach even better than checking to see if the existing wire is okay for an upgraded breaker. Without looking I doubt if it is 12 gauge wire as the house was built in the mid 80's.

Thanks for all of the input and discussion. As so often happens in this type of thread from time to time there is a misunderstanding. Some advice is good, some bad and some misdirected. Whenever we ask for help especially about topics like electricity where there is the potential for some serious consequences the end result is our own responsibility. In my case I knew just enough to possibly cause a problem for myself or maybe someone else down the road if we sell the house.

Re: O.T. Microwave blowing the circuit

#19

While You're At It . .

Mark Mandell - Gone Round In Jersey

With an eye to the next resident, since "Code" now requires those backsplash circuits to be GFCI, make them so if they're not already. 2 options on this: a) put in GFCI breaker(s) on the circuits or b) use a GFCI duplex in the first box fed from the service panel. If your basement is finished, b) may be a bit hard to determine.

Re: O.T. Microwave blowing the circuit

#20

Re: Whoa, Barry and a question for Jay

Jay

We should actually be saying 120/240, old habits die hard. The whole common trip requirement is new. It was changed in this last code upgrade. We never used to do it and I still think it is unnecessary. I only do it now when I absolutely have to. I have begun just running separate neutrals for each circuit, then each one can trip separately. As far as one circuit resisting tripping when the other one trips, I don't believe that is true. Most municipalities I deal with have not adopted the new code, mostly because they don't want to enforce some of this stuff (common trip breakers, arc faults everywhere in the house, etc.) that they don't agree with themselves.