OT Furnace/Generator Operation

Posts

OT Furnace/Generator Operation

#1

OT Furnace/Generator Operation

Howard Norman

>I spent yesterday afternoon trying to solve an operational problem on an Amana furnace using a Honda generator as the electrical power source. It short cycles with the generator, two-three minutes on and then about the same amount of time off. Voltage and frequency from the generator are fine. I don't have a 'scope to check the waveform coming from the generator. I sent an email to a friend who is an electronics whiz today and he is having the same problem with a Honda generator and a Lennox furnace.

Anyone else observe this issue or have any ideas?

Re: OT Furnace/Generator Operation

#2

Re: OT Furnace/Generator Operation

Bill Howatt

>If the voltage and frequency are fine then the generator is probably not overloaded. I'd be looking at excessive noise on the generator output causing trouble with the furnace circuits. I don't really know much about furnaces.

Bill

Re: OT Furnace/Generator Operation

#3

Re: OT Furnace/Generator Operation

Bob Entwisle in NJ

>Just shooting form the hip here. Can you get a small isolation transformer between the generator and the electronic controls? It sounds like there could be a glitch getting to the electroncis (if it's solid state controls). The iso xfmr might be enough to filter the spikes from the genset. Have you contacted the furnace manufacturer for their input?

Let us know what fixes the problem, or what doesn't fix it as well.

Good luck

Bob

Re: OT Furnace/Generator Operation

#4

Re: OT Furnace/Generator Operation

Basil

>I have no idea.....but having 2,000 watts more generating capacity than needed solved my problem 20 years ago.

Re: OT Furnace/Generator Operation

#5

Re: OT Furnace/Generator Operation

del schisler

>If you had a scope I bet the sine wave would have lot's of spikes on it This could get into the pc board if that is used Electronic's don't like spikes Or Not a clean 60 cycle pure wave Most gen. just generate voltage and not be to clean Not much filtering done Yrs back when i done radio and tv service for 50 yrs The power surge would spike and do dammage Fixed lot's of item's 3 cents worth due to inflation

Re: OT Furnace/Generator Operation

#6

Re: OT Furnace/Generator Operation

Howard Norman

>An isolation transformer. Now that is an idea that I hadn't thought of. I have been planing on buying one for my work on old radios. I wonder if either of the local Radio Shack stores have one.

And yes a Honda generator repairman has told me that these generators don't produce a "clean" sine wave. Also another friend is having the same problem on a Lennox furnace with a Honda generator.

Manu of us have considered Honda to be the preferred generator because of reliability issues. I wonder if the problem is the same or worse with some of the cheaper generators.

Re: OT Furnace/Generator Operation

#7

Re: OT Furnace/Generator Operation

Howard Norman

>Problem apparently solved by connecting the neutral to the equipment ground at the generator. I haven't been in the room to check it out but my neighbor says the furnace is running fine off of the generator since he made that connection.