Header size for large overhead door

Posts

Header size for large overhead door

#1

Header size for large overhead door

Dave Mount

>Hello all--

I'm hoping someone can save me some time searching around for the appropriate tables. I am about to frame a new garage-type building (wood frame, 2x6 stud walls, common roof trusses) that will include a 10' high by 20' long commercial overhead door in a non-bearing (gable end) exterior wall (2x6). The overall wall is 12' high so I have a little less than 2' to work with. I was actually thinking about using a floor truss instead of a conventional header. I'm assuming the alternative is LVLs, though I'm not sure how to size them for a non-bearing app. Over the top is a 24' end truss (6-12) and it will have structural sheathing.

Before anyone tells me to call the building inspector, there are no inspectors or local codes out where I live. That's not to say I wouldn't use code as guidance, and I don't mind overbuilding within reason.

Input or pointers to appropriate resources appreciated. Thanks.

Dave

Re: Header size for large overhead door

#2

Re: Header size for large overhead door

Ed Mulligan, Cape Cod

>No direct experience here but recently when a contractor put in a sliding door for me the building supply store supplied the engineering advice for the overhead beam.

Re: Header size for large overhead door

#3

Re: Header size for large overhead door

Barry Irby

>One theory is that you con't need a header at all. With trusses, you could leave the end wall out altogether.

I would provide some sort of header to give something to attach the door to. Check with the door installer and see what they need as points to bolt things to. Residential doors usually bolt tot he jamb framing. There may be a requirement for a piece in the center to bolt the coiled spring to, if you have that type of spring.

The easiest (But not cheapest) thing to do would be to provide a header of LVL beams. The companies selling them will do the engineering for you and tell you what size you need. I found them to be quite expensive, especially if they are not necessary.

What I would do is build a box beam over the door. Install a 2x4 or 2x6 across the opening at the top of the jacks.Install a skin of plywood across the opening so that the plywood extends up onto the trusses. Install a 2X4 across the opening under the top plate of the wall. Install 2x4's vertically on four foot centers. Cover the inside with plywood and add another layer of 2X? lumber to the inside. Three layers should give you a really solid beam about the same thickness as the stud walls. I would glue and nail all the joints and scatter the joints in the plywood. This home built beam would be very strong. I have used this technique many times of the years. Under a strict building code, this would be frowned upon because it is not and "Engineered" solution. The Building Official would be looking for a manufactured and engineered answer.

Even lighter and cheaper and easier would be a simple box beam. Build a "ladder" laying on its side. A 2x6 laid down flat on to of the jacks. Short vertical cripple stud up to the top plate on 16" or 24" centers. Insulate and install wiring as necessary. Skin both sides with plywood. Break up the joints in the plywood and have it extend up onto the bottom cord of the truss. Glue and nail it securely. Good to go.

Re: Header size for large overhead door

#4

Re: Header size for large overhead door

Chris Friesen

>To add to what the others have said, the header isn't needed for structural purposes. However, it will help somewhat to guard against racking forces, as will securely fastening the end truss to the two short wall sections on either side of the door.

I second the vote to find out from the door manufacturer what they need in terms of mounting. That way you can make sure to provide solid blocking for them if you build a box beam or similar.

Re: Header size for large overhead door

#5

You don't need it...

John in NM

>As others have pointed out, unless the door needs the support. Even then I'd suppose the door "roll" is supported by brackets at the ends (this the kind with the chain for rolling/unrolling?), so you'd just need a couple of nice meaty post built in to the walls on either side, extending above the door opening. If you have space on either side, some diagonal bracing would be a good idea to help make up for the big hole in the wall, you can also sheath the walls with osb for the same effect. The International Residential Code has some guidelines for average wind loading across the country, that should give you some idea how much you need to worry about the bracing or sheathing of the walls.

Re: Header size for large overhead door

#6

Re: Header size for large overhead door

GalenV in Iowa

>A standard header for a double wide garage door on the gable end is two 2 x 12 with a 1/2" nominal plywood filler between to make up the typical 2 x 4 wall construction. The header does add rigidity to the open end of the garage, provides the lateral support for wind loading against the gable end and to carrying the vertical siding load of the gable.

If you are using 2 x 6 wall construction and are going to finish the inside you may make up a box beam so the header is flush to the inside and outside of the frameing.

Re: Header size for large overhead door

#7

Re: Header size for large overhead door *LINK*

Mark Nowicki

>For a 20 foot span, roof and ceiling load only, specified snow load of 1.0 kPa (aprox. 20lbs per square foot) and supported length of 2.4 meters you need a glued laminated timber header 130mm by 342mm. (5.3" X 14")

Supported length means half the length of truss or rafter plus the length of overhang.

Five 2X12 ganged together can span about 16 feet, same conditions as above.

My source: National Building Code of Canada, sec 9.131:Span Tables

Mark


Roof load zones

Re: Header size for large overhead door

#8

(2) 2x12's with a 1/2" plywood filler is correctt.

RobV

>

Re: Header size for large overhead door

#9

Re: Header size for large overhead door

Fred Davis

>Dave,

Since your dwelling in non -regulated territory code wise , the chance for a bad mistake is increased ..

None of the suggestions so far would pass a UBC code inspection which is governed in wide spans by some pretty rigid rules .

I am a retired building contractor , so I feel comfortable in suggesting two things.

If your Trusses are being manufactured to order by a real truss company as opposed to the neighbors helping out , they can tell you what will work and what to avoid and in the area of a engineered header would have the correct information for that span and make it for you.

Secondly a Glu-Lam specified by the manufacturer for that span will also work , though it would be heavy as hell and need a fork lift available.

You can get one the thickness of your 2x6 wall or one for a 2x4 wall thickness and furr out one side or the other to match your studding.

Avoid attaching sheathing from the wall to the gable end truss ,by crossing the plate line in a continuous skin, this will add a load not planned for by the Truss company to the Gable truss, though a sheathed in the factory truss will carry a lot of weight.

Since your not subject to inspection , be sure to double the trimmers on each end of the opening or use a solid 4x6 post instead to carry the header.

Glu-lams on the west coast typically are delivered to lumber yards in one piece 80 feet long and they cut off the required length for the customer.

While this works great for the lumber yard , you want to be sure that the piece you buy if you go in that direction will include a 1/8th" to 3/16ths' inch camber which is where the Glu-lam draws it's strength to resist sagging from.

Do not be afraid to ask a local Structural Engineer how to go about it , that would be a cost effective question.

Good luck and remember big spans require careful planning and you don't have the backup of the structural Engineer in a typical Building Department checking your plan before permit issuance.

FredD

Re: Header size for large overhead door

#10

Re: Thanks all!

Dave Mount

>Thanks everyone. I like the box beam idea a lot. Also saves me from having to do it in two elements, the header and the cripples above. I'm thinking it would work well to make it with 2x6's ripped down to 4.5", which would make the full assembly 5.5" thick and flush with the adjacent framing -- then I can tie it in with everything else by sheathing over it and the frame above and to the side. Should also have a lot more rigidity to wind loading than a regular header.

Just to reiterate as I think a couple folks missed it, this is not a bearing wall.

Thanks again!!

Dave

Re: Header size for large overhead door

#11

Re: Calculations

Dave Mount

>Hi Fred--

Thanks for your thoughtful response, I didn't see it before I posted below.

I certainly recognize the box beam suggestion is not an engineered approach. Hearing your concern over potentially overloading the truss (yes, I am using engineered factory trusses), I did some calculations. The weight of the 20' unsupported section of a box beam would be 218 pounds (excluding glue and fasteners), based on 1.5" by 4.5" hem fir framing inside and 1/2" plywood skins on both sides. Even if one assumes it has no structural value and just hangs from the truss, this is equivalent to a 5.5 lb per square foot dead load on the roof (218 pounds spread over 40 ft^2). Given that the truss will be sheathed, and that the roofing will be very light (2x4 purlins and 28 gauge metal roofing), this does not seem like an inordinate load, even if the box beam was only dead weight.

I have a Bobcat, so I can set the beam in place using forks. I can also measure the deflection after setting the box beam, to help determine whether the construction of the beam was sufficient to achieve meaningful strength.

If you still think it is a concern even with the calculation above, what would you think of doubling the end truss and tying them together well? I believe the cost of an additional truss would be considerably less than a glulam or LVL beam (the cost of labor does not concern me). It seems to me that sheathing across the plate would be desirable to help resist racking of that wall.

Thanks for giving it some thought,

Dave

Re: Header size for large overhead door

#12

Re: Calculations

Fred Davis

>Hi back at you Dave,

In doing this type of building for many years, one learns a few of the basic no -no's in construction.

One of them as a general rule is not to load a rafter or a truss unusally.

This means for instance though you may have see it is running ceiling joists on one end to a rafter and fasenting to the rafter which is not meant to carry a load of the ceiling in addition to the load the roof places on it.

This is what I meant about your project in the sense that you have said you will have about two feet of wall and header below the plate line and attaching it to a roof truss which is above the plate line and only designed to carry the load placed on it by the roof , increases the load on the truss which is meant to carry it's design load free span from outside wall to ouside wall.

All of the above dosen't really mean much in a practical sense , because you have no oversight from a Engineer or Truss company or even the stress and strain tables in a span chart of a code book.

Your calling what amounts to a curtain wall a non bearing wall which is not the case when you consider the roof load and wind load and impossiblie to predict Snow and Ice loads, which may in many instances become for a period of time a dead load, until it melts.

Simply put the truss carries this load which is designed with a safety factor with little or no problems . Adding to this load needs the advice of your Truss company or a Structural Engineer.

It sounds to me like your willing to err on the side of caution, so happy building.

One other thing and I will leave this subject alone , I too have a Bobcat 700 series diesel and it will not reach over the top of eight foot stalls in our Horse barn , let alone the ten foot reach , you talked about. ;-))

FredD

Re: Header size for large overhead door

#13

another thought

Barry Irby

>Dave, You did not tell us where you are. We have no idea about snow loading or wind loading.

As I mentioned above, I believe the home made box beam will work. I also think you should skin the end of the building with plywood for several reasons. The plywood will help resist the raking forces on this wall with a large hole in it. It will tie the truss down securely and allow the end to function as a structural unit.

You mentioned a metal roof and purlins. This could be a very light roof/roofing system. Blow off is a real consideration. Pay close attention to fastening the ends of the trusses down and tie the walls down to the footings as well. Be sure to keep up with the fastening schedule on the purlins and the metal roofing.

Since you are using manufactured trusses, why not ask the truss manufacturer how to solve this problem? They may be able to make you up a truss to serve as a header. Discuss with them the idea you had about doubling the end truss. You may find you can do that and "hang" your box beam under it.

Cause a stud to fall directly under each truss. Tie the truss to the stud with appropriate metal strapping and tie the stud to the footing.

Re: Header size for large overhead door

#14

Re: Calculations *LINK*

Dave Mount

>Hi again Fred--

I'm getting the sense you think I'm arguing with you and that's not my intent. What you said seemed to conflict with my understanding and calculations. It's not that I disrespect your knowledge and experience, but if I don't understand why something is wrong, I don't really learn anything. Give a man a fish v. teach a man to fish. . .

Re: Bobcat reach, I have an S175 and its reach is 118" to the hinge pin.

Thanks for taking the time to respond.

Best,

Dave


Bobcat S175 specs

Re: Header size for large overhead door

#15

Re: Calculations

Fred Davis

>Dave ,

there is no intent on my part to argue with you or anybody else, you asked for suggestions , the ones I had are the ones I had to live with as a Building Contractor in CA, which as lot of the folk can tell you is the most heavily regulated state in the Union.

Operating under the Uniform Building Code , enforced by the Inspectors gives little room for departure from accepted methods of work , unless you can pay for testing and have that result accepted by the various entities that govern building.

You do not have this circumstance, so be careful, a twenty foot hole in the side of a building has the same potential for disaster anywhere you live.

That does not infer you will have one, only time and gravity will tell.

As for my poor old Bobcat it can reach over a eight foot stall wall with a bucket of sand , but does not have the height to dump the bucket without hitting the wall first.

So it is still a lot of shovel work. ;-))

FredD