>I am trying to install a recessed light in our shower on the second floor. I have an insulated attic above the second floor with blown fiberglass installation installed. A couple of questions:
I have to cut through a vapour barrier that is on top of the drywall ceiling. Once I install the light, how do I re-seal this vapour barrier?
Once installed and wired, can I put the blown insulation around and on top of the recessed light fixture? The fixture is "IC" rated.
>insulation , blown or otherwise is kept clear of recessed fixtures where the can is in the crawl space.
Some fixtures , depending on the wattage use asbestos clad pigtails 36" long for the wire connection for that reason.
For blown insulation where you getting 12" deep or so , it's a good idea to make a four sided box that will keep the insulation from moving back in to the fixture can area.
Beyond that I wouldn't sweat the vapor barrier for that small of a intrusion, since you wouldn't want a combustibile like a paper vapor barrier that close to heat.
>The newer IC rated fixtures, as noted on the package the fixture came in, are made for insulted contact. The box or data sheet should define what to do to be safe. They are UL listed for this type of installation such as blown in insulation.
You do need to insure you use the correct wattage bulb or smaller as anything higher would create more heat, the fixture cannot dissapate.
They are a lot better than the older style can that basically your home heat went right up and out of the housing.
>penetrations of the vapor barrier are inevitable in most settings. For instance, most electric boxes penetrate the vapor barrier, unless you go to a lot of extra work to use a design that runs the barrier behind the box.
Fine Homebuilding has started referring to "vapor retarder," apparently the term of art in the building codes, since an actual barrier - nothing can get through - isn't possible and isn't even always desirable.
Try to limit the size of the hole you cut to no larger than you must to get the fixture in. If the hole has to be big to gain access for wiring, installing, etc., get some polyethylene sheet at the hardware store and do your best to tape that to the existing vapor barrier.
Once you've patched the drywall (if you're coming in from below), use a flexible caulk (fond as I am of acrylic latex, I wouldn't use that in this particular application - a little too stiff. Unless your caulking is even sloppier than mine, your caulking work will be covered by the trim ring, so you can use one of the hard-to-tool caulks like silicone here) or minimal-expanding spray foam to seal up the edges of the recessed light, so there's no gaps at the drywall.
And I concur twice with the other post:
1. "IC" means "insulation contact." I believe you can wrap the light in insulation.
2. NEVER exceed the wattage rating of this fixture type. Although you're never supposed to do so, some fixtures give you more latitude. This type, with no air vents and insulation crammed up against it, has very little latitude.
Bill, not an electrician, but some experience, and learned a lot recently about the current state of things when I did our kitchen remodel.
>Thanks for the update Bill , one never has enough update , so if he is smart he plans ahead.
While your "IC" fixture may be "wrapped in insulation" ( hard to believe I know) you posted the caveat about not exceeding the stated max. wattage which I am sure is frequently done to peoples sorrow.
I have many times in remodels removed old light fixtures and found the paper on the sheetrock fried.
"IC" is current state of the art so that's good .
The millions of homes already up without that update run the risk of a homeowner upgrading his insulation and burying his old style fixture cans (like mine for instance) because he is not aware of the fire risk. That's not good.
So if you had adhered to common building practice and avoided the contact with insulation, your doubly safe and if some home owner or Electrician comes behind you and for what ever reason , needs to find the fixtures locations in the dark crawl space, he will not have a problem doing so under 30 inches of insulation depending on what zone your in.
>Both codes have a specific envelope around a tub or shower where the type of fixture is restricted to one rated for damp installations that is not a cord connected fixture. The envelope ends 8 feet above the tub rim or shower threshold. We installed a solar tube with a fixture inside and had no problem with the inspector, as the fixture is more than 8' up from the threshold and there is a diffusing lens at the ceiling that provides a bit of a steam barrier. I might have even caulked the diffuser (can't remember now) but it was not required that I do so.