OT - HVAC Icing...What happened?

Posts

OT - HVAC Icing...What happened?

#1

OT - HVAC Icing...What happened?

Joe Pack

>une 9 and prior - A/C working fine.

June 10 - Left on vacation; set thermostat to 82 degrees to keep humidity out of the house.

June 27 - Arrived home late p.m.; friend had set thermostat back to 72 degrees earlier in the day so house would be cool when we got home. A/C is running, house is cool (74) and we went almost immediately to bed.

June 28 - House is cool as expected; fan running when we got up. During the day we notice fan not kicking off, but temp is maintaining at 72. Late evening fan is still running, but temp is rising to 74. Went to basement to see what I could see and found water on the floor around the furnace/blower, with no condensate running into sump crock. This happened once before when crud clogged the drain line, so I blew into the drain line to clear it (easier than taking it apart). I heard a gurgle and a bit of water splashed from under the plenum; drain is now open and condensate runs out for about 30 seconds. Problem solved (I think.)

I then notice a bit of frost on the plenum (not supposed to be there). Anticipating what I would find, I open one side of the plenum to find the A coil frozen. I turn the thermostat to 80 (shutting off the call for A/C), but put the fan on constant. I check the 1" MERV 6 pleated filter, which is pretty dirty, but not much more than it sometimes get when I forget to change it. I leave the filter out and run the fan for 2 hours or so, during which time the ice melts. I turn the A/C back on, set to 72 degrees. The A/C goes to work, cools to 72 degrees and shuts off. It has kicked on and off as usual for 48 hours with no sign of freezing.

Related information, if it means anything...the living level of the house was in the low 80's when the unit was reset to 72 on Saturday. The basement would have been about 70 or so. The outside temp was in the mid to high 80's during the day, and only into the mid 70's at night. The next day had similar temps. Temps yesterday and today are in the low 70s.

The furnace and heat pump are 1991 vintage, with the coolant in the heat pump replaced and a leaking line repaired about 6 years ago. Zero problems with cooling this year, even on days when temps were in the low 90's and we had he house at 72.

Bottom line....what happened? Do I have a problem, or did I have the "perfect storm" of conditions unlikely to occur again?

Re: OT - HVAC Icing...What happened?

#2

JL

Re: OT - HVAC Icing...What happened?

JL

>Sounds like low coolant. Possibly a coolant leak. I'd have the HVAC guy out to check the level and put his sniffer on the system.

Re: OT - HVAC Icing...What happened?

#3

Re: OT - HVAC Icing...What happened?

John McGaw

>Agree with that one. In my experience icing of the evaporator is virtually always a symptom of low coolant. Once it ices heavily and then starts to melt you get a chance to determine how effective the designer's drain system really is. If there is a leak anywhere besides in an easily accessible refrigerant line replacing the whole system is often cheaper than trying to fix an older system. The good news is that if your equipment has truly bit the dust the government is giving out sizable rebates if you replace your AC equipment with high-efficiency (15+ SEER?) equipment. That can bring the cost of replacement down while reducing your energy bills. Small comfort but it is something...

Re: OT - HVAC Icing...What happened?

#4

Re: OT - HVAC Icing...What happened?

Barry Irby

>Low refrigerant sounds likely to me too. 18 years is a long life for a heat pump. Don't be surprised if it's time for a new one. The dirty filter may have contributed. Low refrigerant, reduced air flow, and a sudden decrease over a wider range than normal could be your perfect storm.

Re: OT - HVAC Icing...What happened?

#5

Re: OT - HVAC Icing...What happened?

Bill Turpin in WNC mountains

>When a HVAC system is normal, with 45 to 50� air coming out of the inside coil, the actual freon temp is 35 to 38�. When the freon charge is low, that freon temp goes lower. The temp of the first pass of tubing, which will be closer to 25�, causes frost to form on the first few inches of tubing. When the thermostsat gets satisfied, this frost melts and drains out of the condensate line. With a low charge, the on-time increases, which causes even more frost to form. More frost causes lower freon temps, which causes more frost...Eventually the coil stops up with frost. You get hot, and have it fixed.

With the whole house allowed to have gotten warm, a borderline future problem reared its ugly head. Heat pumps are farely critical as to charge. In an attempt to have the proper charge, the pre-charged line sets have great big, o-ring sealed flare nuts that always leak. This requires a re-charge every several years.

During the winter, the cold coil on a heat pump is outside. Low charges then cause icing on the outside unit.

Bill in WNC mountains

NC Refrigeration License #2821

Re: OT - HVAC Icing...What happened?

#6

Orifice partially blocked??

Gil Jones...Georgia

>If you have an orifice at the high-pressure entrance to the A-coil, and "somehow" a tiny piece of trash in the system broke loose and partially blocked it, you could get the same result as LOW FREON. Icing of the coil could occur, and then if the little piece of trash made its way through the orifice and is now trapped in the receiver/dryer filter all is well again.

Just a thought, but if your system is back to proper operation again, that could be what happened.

Gil

Re: OT - HVAC Icing...What happened?

#7

Re: OT - HVAC Icing...What happened?

Bob Lemon , Sacramento CA.

>Joe, you don't want to call a refrigeration service that will try to sell you a new unit. You've already found the dirty filter, now look to see if you have a dirty squirrel cage blower. The squirrel cage has cupped fins on it and over the years they will pack with dirt. This cuts the efficiency way down. The next thing in line is the coil. Check your A coil closely to make sure the face of the coil is not packed with debris. Cat and dog hair will put a mat on the face of the coil. Make sure it is clean and your system will probably work fine.

You got a comment about the particle in the metering device that could have caused the freeze up. That particle could be water. You might consider a partially plugged drier on the refrigerant line. This would require the removal of refrigerant and replacement of the drier and proper recharging of Freon.

I keep hearing about replacing the compressor because it is old. My own AC system was built up 46+ years ago and the compressor is still churning away! I swapped out the furnace a couple of times, but the AC still runs. :)

Bob

Re: OT - HVAC Icing...What happened?

#8

Re: OT - HVAC Icing...What happened?

Lee Schierer - McKean, PA

>I think the dirty filter was the cause and I would watch it for a few days to see if it is icing before calling a service guy and getting a hefty service call bill. What you might want to try was what our installer recommended for our new system. Run the fan on low all the time. The A/C will run as needed to maintain the setting. Running the fan all the time will make the house temp more uniform and will melt any ice accumulation that starts between cycles. We are lucky our new system has a variable speed fan so it runs really slow all the time and kicks up the air flow when the compressor runs.

Lee

Re: OT - HVAC Icing...What happened?

#9

Re: OT - HVAC Icing...What happened?

Andy Barss

>Happens to me once in a while. I live in Arizona, and it's always triggered (for me) by a dirty filter. That slows down the airflow, which somehow creates ice buildup. My HVAC guy told me I need to clean the filter at least once a week.