OT Dehumidifier Problem

#1

OT Dehumidifier Problem

Nat Robison

>I have a portable Haier dehumidifier in my basement. It's a little over 2 years old. Lately, it's been running but doesn't seem to be extracting any water from the air. Can they be recharged with refrigerant? Any other things to try??

Re: OT Dehumidifier Problem

#2

Re: OT Dehumidifier Problem

Barry Irby

>You might be able to go to the manufacturer's web site and find out if the unit is repairable. If there are ports on the unit to allow them to be refilled, the repair technician will have to know what the refrigerant is and what the internal pressures should be. It will also be necessary to find the leak and cure it. This may make it not a valid financial decision to repair the unit.

Re: OT Dehumidifier Problem

#3

Re: OT Dehumidifier Problem

Dave Paine

>I had a similar problem 18 months ago. My unit ran, but no condensate. The likely cause is that the refrigerant has leaked out over time.

Although the unit can theoretically be checked to find the leak and "maybe" the leak repaired - depending if in a line or the coil, the cost is likely to be higher than a replacement. Very sad to say.

I went the replacement route. The unit I replaced was only a few years old. The original unit lasted perhaps 20 years. Sad that sometimes technology advancements do not mean reliability advancements.

Re: OT Dehumidifier Problem

#4

Re: OT Dehumidifier Problem

GalenV in Iowa

>When you say it is running what do you mean?

Is the fan running and clean to get good air flow?

If the compressor is running are the coils cold?

Don't know what the basement temp is but if it is too cool the coils will just ice up and may never defrost to show condensation it is pulling out.

How humid is your basement to begin with as it will not do much good if air is dry already.

Units I have owned were not set up to recharge as lines sealed after factory filling. Only had three in about 36 years.

Galen

Re: OT Dehumidifier Problem

#5

Different Problem...

Tony - Memphis

>No ideas for yours, but I do think it would cost more to try and service it thatn it is worth. They aren't made to service (like window units).

I have a small unit that sometimes turns on and keeps running until it is full. I replaced the humidistat, but that didn't help. I did learn that if I slap the top pretty hard, it shuts off. Most of the time, it works fine. The unit is about ten years old. Parts are very expensive and a few parts adds up to a new unit almost. Anybody got any tips on newer models? I just use a small unit for my shop - I can't recall the "pint/hr" rating. I run a window unit and it doesn't run long enough to remove the humidity.

Thanks,

Tony

Re: OT Dehumidifier Problem

#6

Re: Different Problem...

Don Evans

>Tony:

There are 2 switches on these units that are operated by the water bucket.

One detects if the water bucket is removed and shuts the unit down. The second switch detects if the bucket is too heavy, indicating that the bucket is full of water.

These switches can get out of adjustment, normally due to roughly puttng the bucket in and out.

The fact that you can "slap it" and it will start indicates that the likely suspect is the first switch mentioned, it doesn't recognize the bucket is installed.

When you put the bucket in "gently" listen for the switch to "click" when you have released the bucket.

Some units have a spring piece of metal over the switch that can get bent and you have to do a "form" adjustment on it to get it to work right, can be a bit of a pain.

But that sounds like your trouble, simple adjustment.

Keep in mind that the bucket actually moves in a pivoting motion from empty to full.

Don

Re: OT Dehumidifier Problem

#7

Re: OT Dehumidifier Problem

Don Evans

>Nat:

Cannot, obviously, say that this is your problem with the limited information but:

There is a thermostat that "snaps" onto one of the copper lines with a spring clip. It just rest against the outside of the pipe. It's job is to monitor the temp of the refrigerant. If the refrigerant gets too cold this therm turns off the compressor but on most models now days the fan keeps running. The idea is that the cold temp is an indication that the unit is freezing up and the fan keeps running to help defrost and or melt the ice formed on the coils.

If the unit is NOT really frozen up, then it indicates that this thermostat is defective. They general aren't expensive and is something you can change yourself. Just made sure you know where the different color wires go before removing the old one.

What I do in cases like this, I'm going to toss the one any way so I cut the wiring near the connection point leaving some wire so can see the color of the wire. Then as installing the new one, remove only one old wire at the time and put the new one on that location. There will be 2 or 3 wires on it, just put the red where the red was etc., then snap the thermostat on the pipe and you're back in business.

FYI, on some older units the thing turned off the fan also.

NOTE: this is NOT the thermostat on front that you turn for more or less humidity. UNPLUG THE AC FROM THE WALL BEFORE DOING ANYTHING.

Look in yellow pages for local "appliance parts" to get the therm. switch. There should also be a schematic on the inside of the cover of the unit.

Don

Re: OT Dehumidifier Problem

#8

Actually...

Tony - Memphis

>I slap it to turn it off. Mine only has a float activated switch. Can't recall, but I think it is a White-Westinghouse. This is a small roll a round unit that is rated at 25 pints or something like that. I got it marked down at Best Buy around 10 years ago. They actually had marked the higher capacity model at the lower capacity sale price, but they honored it anyway. Good bargain! I hate to toss it to the curb. It's a big hunk of metal and refrigerant that I really don't want to send to the dump only to replace it with a new one. I've been putting up with it for a couple of seasons. I only run it in the summer. I'd have to keep the shop temp really cool for the ac to keep the humidity down. The dehumidifier seems to be more efficient at removing humidity, so I am assuming it is cheaper even though it introduces some heat to the room. For a small 16x20 shop, I've really had a tough time keeping it cool/warm and not so humid. I'll do something different next time.

Tony

Re: OT Dehumidifier Problem

#9

Re: OT Dehumidifier Problem

sputre

>Can I just vent some frustration here? I have been very disappointed with two dehumidifiers I have bought over the past 6 years. The first one (GE) broke after about a year, was repaired, then broke again a year later. I then replaced it with a Kenmore with digital controls which ran OK for a year or two. For the past 2 years it just stays on all the time and does not shut off (the membrane power switch does not work and the humidity control just says 'on'). Are dehumidifiers all unreliable these days? After all, they are just simplified refrigerators.

My dad had a Fedders, vintage 1978, which I believe is still running reliably after 30 years.

Does anyone have a late-model unit which has been trouble free for more than 5 years?

Thanks for putting up with my rant.