>I'll try to keep it short. I'm adding on to my deck and am adding a Siemens 50amp GFCI subpanel to power a 220v circuit for a 1hp pool pump and a 110 circuit for an outlet. The 50 amp breaker that came with the panel is GFCI but to add other breaker(s) to the panel would they also need to be GCFI or can they be a standard breaker and still be protected properly? Am I making sense?
Re: Outdoor GFCI wiring question
Jesper, Denmark
Jesper, Denmark
>You are making sense.
The GFCI breaker will check the complete panel for ground faults and the other breaker do not need to anything other than standard breakers that fit than panel.
It is an eccellent safety idea, but somet�mes troublesome in severe thunder storms.
But That Ain't All
>If your pool will be "inhabited" by humans, [or even small children] you must have a DPST cutoff switch within sight of the fixture, and the pump [+ any heater] must be "bound" with at least a No. 6 ground wire independent of the cable ground. At least that's the requirement here in NJ.
m
Dave LaPine
>Thanks guys those answers help- Also I'll tell everyone to not "Inhabit" the pool during severe thunderstorms.
perhaps
Bill Hammond, Oregon Coast
>Most likely there is no main breaker at the sub panel. The 50A GFCI in the sub panel is for the spa. Remember the Spa shutoff (it doesn't have to be a breaker it can be a disconnect) must be within sight of the spa from where the equipment is accessed and more than 5'away from any part of the spa (local regs may very, check to be sure). Any more breakers for outside must also be GFCI. This assumes the breaker for the sub panel in the main panel is not the GFCI. If the breaker in the main panel is the GFCI then no more GFCIs should be used down the line from the first GFCI.
Personally I would have separate GFCIs for each circuit and not use the GFCI as a main breaker. You don't need the spa to shut down just because something else tripped the GFCI (like Christmas lights or the blow up pumpkin at Halloween) and you don't notice it right away.
Power to a spa is one of those areas where you really don't want to make a mistake, make sure you really understand how the spa needs to be wired and how the connections up to the spa need to be made up. Even if you have an electrician do the work make sure it's done properly and the connection at the spa is done the way the manufacturer says it should be done.
Spas come in 4 wire and 3 wire varieties where the 4 wire one is two hots, a common and ground and the 3 wire is two hots and a ground. However you must have 4 wires to the box with the GFCI in it even if the spa is a 3 wire hookup. On a 3 wire spa if the electrician brings 4 wires to the spa the common and ground must not be tied together there. Remember too that anything metal that is within 5 feet of the spa or overhead must be bonded to the spa ground with a No 6 ground wire.
Most spa manufactures have wiring diagrams on their web sites. Study them to make sure your understand your setup.
Bill,
I believe code still requires
>a main breaker at any subpanel beyond a (very short) distance from the main.
I would not use a GFCI for the main breaker for a panel - if you get one ground fault on any circuit from that panel, the whole panel goes out, and tracing the problem gets more complex. Also, as GFCIs get old, they often fail in the direction of hypersensitivity - which is a good thing from the safety perspective, but frustrating if you have to go to the hardware store to buy a new breaker when you just wanted to use your 'lectric hedge trimmer.
If Bill Hammond is correct that the 50A breaker is for the spa, then you may just used up that subpanel, and shouldn't be adding anything else to it. What does the spa call for in breaker size? Unless you've got a spa for the extended family, 50A seems big to me; but what do I know? Our spa is 30+ years old, on its third wiring and probably fourth motor, and runs from a 20A 110V circuit. It's not a good idea to use a breaker larger than the machinery calls for, or for the wire running from breaker to fixture.
ANY outside outlet, or any outlet in close proximity to water (though, for some reason, inspectors don't seem to require them for washing machines - which I think is odd), or any outlet that will get frequent use of a power tool should have GFCI protection - although it's darned hard to find 220V GFCI outlets (fixtures), and the breakers are expensive.
Thanks, Mark
>Very useful info. I'll be rewiring the outbuilding next to which our spa sits, and will use this information in running the wiring to the spa.
Re: I believe code still requires
Dave LaPine
>OK- I'm learnin' stuff now. I was under the impression that the 50amp breaker on the sub panel I bought would feed the rest of the locations on the panel but it looks like not. The 1hp motor I'm using is just for a recirculation pump on an above ground pool not for a whole spa. It is rated at 5.6 amps in the 220v mode (about 10amps when wired for 110v)so a 50amp breaker could be somewhat deadly.Looks like I need to rethink this. It's too bad for me that 220v GFI breakers are so spendy.
Contact
>Your local e-code guy or municipal building office, or even a friendly (and licensed) electrician for the details applicable in your area. I know several people who started to do this themselves saying they would by-pass inspection. I convinced them otherwise because if something happened in an uninspected hot tub, especially one that violated Code, there would be a strong possibility that their homeowner's insurance would NOT COVER THEM. Another one of those fine-print policy gotchas.
Joel M. Dibbern-Kramer
>There is one other thing that has to be looked at. I used GE GFCI Ckt breakers (CB) and the wiring/hookup of the 50Amp CB for 220vt was different than for the 50Amp 110vt wiring/hookup to the main panel. In NYS any exterior (outside the main building) electrical hookups to the main CB panel have to be on a GFCI CB. This was done for a wood shop that I built and had inspected by an electrical insp. for the C. of O. that the local bldg dept req'd which was not attached to the house. A word of caution if you do not totally understand & know what is req'd I would leave this to the professionals.