>Can anyone tell if I should not use a piece of 6" ABS pipe for a dryer vent. I have a metal elbow out of the dryer, and then about 18" of aluminum snaplock pipethat drops me into the crawl space, I need to run out through the rim joist, a distance of about 6'. I already have a chunck of 6" ABS and a 90 ell. I figured why not use it, and I know the smoother the pipe the better airflow. Any reason not too?
>Seems like you may spend more time on adapters. Your 6" elbow will not fit the 4 inch down pipe. You have a bigger hole to cut in your rim joist and then a standard 4" vent hood would not fit the 6" pipe.
I guess you can get a 6" vent hood but at more money. To me a standard 4" elbow, 4" pipe and 4" vent hood are not a big cost and a 4" hole is easier than 6"
>Actually it is 4" pipe and the down pipe is a nice snug fit in to the elbow, plus I already own the pipe. Somehow I must have picked up Alan's tape measure.
>As Bill said, there are heat concerns. You will be dissipating some of the heat with the elbow and the 18" of galvanized - but maybe not enough.
You are basically venting steam from your drier. It gets quite warm. It is not unusual for some drier vent temperatures to be on the order of 150 degrees F or higher. I have used PVC for steaming wood and it does work - you just have to remember to flip it over every so often :). So it will work - just remember that the heat and steam may cause drooping.
>IRC 2003 Code requires metal duct with a minimum thickness of .016", max. length of 25' with a 2.5 ft deduction for each 45 degree elbow and a 5' deduction for a 90 degree elbow
>The issue is not just heat, but also lint plus heat. The pipe (regardless of composition) will accumulate lint and deposits (fabric softener) over time. This can (and has, many times) ignite. Steel vent pipe will contain the fire whereas plastic of any kind will merely add to it. In my area, even aluminum flex pipe is prohibited for dryer venting. Inspector here wants steel.
>I agree on the metal only. Rigid pipe over any flexible stuff. Like mentioned earlier, anything (seams, corrigations, fasteners, etc) that can snag lint will allow lint to snag & build. Coorgated pipe also creates drag on the air flow. Smooth metal pipe is the best thing to use. Don't get cheap on a potential fire catalyst, especially when we're only talking a few bucks.
you have a relatively short horizontal run of six feet , so using cheaper and illegal materials are not cost effective.
I would use Aluminum , like what your short down run is ,because G.I. heat run duct will eventually rust out.
In your area Aluminum flex is likely to be legal and though I don't like it because it has friction per foot equal to 2 1/2 feet of smooth pipe and is prone to sags between supports, in this case , it would also be effective since it is equal to only 15 feet of smooth duct, friction wise , which is well below the maximum length of run requirement.
Snap lock Aluminum duct is available in lengths to five feet and it's rigidity makes it the best choice.
>With the talk about effeciencies and lint collection I wondered about where the snap-lock should be placed. It would seem to make sense to have it on the top so that gravity is used to keep lint clotting.
My Mom's drier vent was clogged in her apartment. We pulled out a shoe-box sized clot just at the exit flapper. The maintenance crew at her apartment complex started cleaning out the vents now.
>I had a surprisingly small quantity of lint hold the flapper at the exit boot closed against air pressure (it wasn't even blocking the vent, just kind of clotting up the flapper), resulting in symptoms* that the appliance parts people swore were some of the safety temp sensors.
I found the problem after buying at least one of the sensors...oh, well, preventive maintenance.
*Gas dryer; the flame would go on and be OK at first, then start cycling on and immediately off, with no effective heat in the dryer - because there was no airflow. The safety sensors were doing their job right, because the lack of airflow was causing heat to build up in the flame chamber. But clothes weren't drying.
I got a certain number of husband points for diagnosing the problem; would have had more if I'd diagnosed it before spending money (not much, thank goodness) on the sensors.
>Gary, You have gotten good advice here. As a Home Inspector I know a thing or two about this. The threat of a lint fire in the dryer vent is real, especially with gas dryers. In fact the vent on a gas dryer should be treated as a gas vent or flue. But, even on electric dryers a good safe vent is very important, both for fire safety and for the proper operation of the dryer. Here are some of the rules I use when suggesting a Proper vent.
The pipe should be metal. (No plastic or hose vents, and certainly not in a crawl space.
It should be hard pipe and the snap lock should be up, not only to reduce clogging, but because there might be condensation in the pipe, you don't want it dripping out the bottom.
Support it well so that there is no mechanical strain on the joints. Keep the runs as short as possible and use as few bends as possible.
A good sturdy system allows for cleaning the pipe later without destroying it.
The pipe should slop downward toward the wall vent, so that if there is condensation, it will run out.
Any joints in the pipe should be assembled so that the direction of the flow is away from the dryer toward the wall vent. Insert one into the other so that the male end points toward the wall cap or vent. Less edges for the lent to get caught on.
Do not use screws or pop rivets. Nothing that sticks into the pipe for lint to get hung on. Use heat resistant metal foil tape.
Obviously, this is not always easy or even possible, but the dryer vent should be taken seriously. I can't even estimate the number I have seen that have fallen apart in crawl spaces and in some cases there was thousands of dollars worth of damage from mold and rot. A vent partially clogged with lint will cause restricted air flow and that makes the dryer run hotter and that may damage your clothes and cause higher utility bills. During some part of the cycle the lint may be dry enough to ignite. The metal pipe should contain the fire while the plastic stuff may not and the fire could spread to the house.