>I'm in the process of running wire for lights in my shop using metal boxes and metal conduit (EMT). Do I need to run a ground wire to each switch or is it sufficient to establish the ground at the first box and then ground each light to the box that supports it. I want to do the job right but I don't want to waste wire.

Re: Electrical Ground and Number of Light Switches

#2

Not sure of current code

Bill Houghton, Sebastopol, CA

>Traditionally, EMT was considered a sufficient ground if the intervening boxes were all metal too. Someone with more current code knowledge should weigh in, though.

Re: Electrical Ground and Number of Light Switches

#3

Re: I'd ground all with wire

Brian in Brighton

>I am not sure of the code, but if you are using romex you should have a ground wire in the cable. I would not rely on the box ground, only because of the effects of time on the ground circuit. You are trying to rely on one connection after another in series without any real tight grounding.

Brian in Brighton

Re: Electrical Ground and Number of Light Switches

#4

Re: Codes vary with location, BUT....

Kneale Brownson Thru skiing in CO till fall

>I'd never use the metal shielding. Used to be standard practice until folks discovered a loose piece of conduit could eliminate your grounds. If you're running individual wires, just add the one more for ground. If you're running Romex, it'll include the ground wire anyway.

Re: Electrical Ground and Number of Light Switches

#5

Re: Codes vary with location, BUT....

Bob Entwisle in NJ

>and make sure to pigtail the ground to both the metal box and the fixture. This is one area of NEC that makes good sense!

Re: Electrical Ground and Number of Light Switches

#6

NEC allows the conduit to be the ground....

Tim Greif - West of Chicago

>Article 250.118 of the National Electric Code allows metallic conduit (rigid, IMC or EMT) to be used as the equipment grounding conductor. So all you have to do is make sure all the fixtures are securley connected to the consuit system and all connectors to boxes and fittings are securely fastened. You are effectively grounded and bonded.

Some folks still feel a separate grounding conductor is good practice. I can't criticize ultra safe practices since as Kneale said, a loose conduit connection can cause a loss of ground. However, I can make the same satement about a loose grounding conductor connection, so you make the call. All that is required by code is to have everything grounded and bonded, by whatever means is allowable in your area. You do not need to run separate ground wires to every switch.

I can tell you from experience that it is important to have every fluorescent light fixture properly grounded, again by whatever means you choose. and it has nothing to do with safety. Without a good ground, the light fixtures will not perform well, especiall in humid conditions. DAMHIKT.

Re: Electrical Ground and Number of Light Switches

#7

Re: Electrical Ground and Number of Light Switches

Stuart Johnson

>Thanks everyone for your input. I've decided to go with a ground wire just to be on the safe side.

Re: Electrical Ground and Number of Light Switches

#8

Jesper, Denmark

Re: Just because it needs to be said....

Jesper, Denmark

>For lurkes and uninitiated:

A Neutral is NOT a ground.

In metal conduit, it is not a bad practice to run the ground wire uninsulated - and it needs to be properly connected to a separate grounding rod. If you have city water, the grounding can be done to the incoming water pipe uif it is metal pipe in the ground, not plastic.