Tim Greif - West of Chicago

>Last week, Richard Jones asked if there's anywhere in the NEC (the "Code") that specifically prohibits running Cat5 network cable in the same conduit as power. I told him I'd dig it up this week when I got back from Europe. I'm re-posting here in case anyone else can benefit as well.

Metallic Ethernet communication media is considered a Class 2 circuit by NEC, Section 725. It's also covered in Section 800. The following scans of the pertinent Code pages show the articles that prohibit the installation of Class 2 or communications cables in any raceway or device with power conductors.

Hope this gives you what you need Richard.

Tim


img

Re: OT Update - Cat5 cable with Power wiring

#2

Re: OT Update - Cat5 cable with Power wiring

Richard Jones

>Tim,

Thanks so much for your research. In a commercial application, I can get on board with this and enforce the NEC as is. However, in VA, anything that operates at less than 50 volts is exempt, so I can't do the same for residential. I'm still stuck with just telling the contractor that it's a dumb idea. I have yet to do a follow-up inspection at this particular site, so will have to wait and see if he changed it or not. Seems quite a lot of potential trouble for just not drilling an additional hole..............

Again, thanks for the steer.

Rich

Re: OT Update - Cat5 cable with Power wiring

#3

Re: OT Update - Cat5 cable with Power wiring

Tim Greif - West of Chicago

>Your VA exwmption for anything less than 50 volts would presumably allow someone to route thermostat,door bell and phone wire in the same conduit as power feeds, and through the main breaker panel as well. That's pretty wide open for residential stuff and pretty ill-advised as well from a safety standpoint. With ethernet cable, the electrical noise potential would increase running the cable with power conductors. Logic level signals on ethernet cable is in the 0.5 to 3 volt range.

Good luck.

Re: OT Update - Cat5 cable with Power wiring

#4

Re: OT Update - Cat5 cable with Power wiring

Alex Grigoriev

>Even though <50V is exempt, you still can't put 110V circuit together with CAT5. 110V > 50V. Or so I understand.