Not exactly…
Rod Peterson -- Ormond Beach
>> And 220 lines do not use the uninsulated ground wire as a nuetral.
This part is true. But not for the reason you think. Technically 240V systems do not use or need a neutral at all. Two conductors carry the current and the ground is for safety.
Modern ranges and clothes dryers, however, are frequently designed with 120V subsystems. Up until around 2000 (I don't know the exact year—could be earlier or later by two or three years), the NEC permitted the customary two conductor plus ground 240V connection and internally the appliances used the ground as a neutral for the 120V systems inside. That is no longer permitted for new work, and a four wire (three conductor plus ground) feed is required to supply them. New replacement ranges or dryers are still permitted to use older existing supplies (two wire conductor with ground), however, and instructions are provided to jumper the ground bus to the neutral bus in the appliance to use them.
> They are three wire system with ground.
In new work, yes. Since the date described previously. But primarily for ranges and dryers. Other 240V circuits may not require a neutral.
> Only two wire 220 I know of may be some older submersible pumps where controls are submerged…
Nope. Water heaters, for example, are permitted to be wired with a two conductor plus ground supply. I think most woodworkers wire their 240V machines with two conductor plus ground supplies, too.
> …and they scare me.
No reason to. The ground should provide the protection needed. Besides, they're just motors. What would a separate neutral do for them anyway?
Rod