Re: Lots of questions raised here
Rob Stokes in North Vancouver
>You're close - the blower is tied into the low-temp/hi temp switch, but that's just to ensure it's on before the flame is, and off after the flame has cooled off. The blower fan can run fine on it's own and the 24VAC wire associated to the unit's t-stat is usually a pretty safe direct run to the manual fan on/off cct.
BUT - I too have questions on why you want both blowers. If the intent is to run two furnaces side by side and have them both pull air from the same return air path and push air into the same supply air path, you need to think this through.
1) Your ductwork was sized for a specific volume of air to run through. If you run two fans in parallel, you'll probably increase the net airflow, but you will not double it. You'll also take that net total airflow and roughly split it between two fans meaning each fan will see something over 50% of it's intended airflow. Fans have a floe curve and ar a rule they are not at all efficient if you place them into a situation where they run off their curve. This means neither fan will be performing to it's expectations and in fact, it's highly probable that neither will be performing at all.
2) Air will take the path of least resistance meaning that unless your two fans are perfectly sized (extremely unlikely), one will be stronger than the other. This means that when both fans are running the stronger one will take air and the weaker one will be idling. If the fans are totally our of shack with each other it's conceivable that the weaker unit could actually have air flowing backwards through it (this is extreme, unlikely, but possible).
3) You will not be able to maintain a decent temperature control as you'll have one furnace pushing heated air, and the other one pushing air at whatever temperature it's receiving.
4) Your elec. energy bill will go up but you won't benefit from the use of that extra power.
Based on these reasons (and a few more), I think it wise to abandon the concept of "AND" when it comes to running these units and instead concentrate on a concept of "OR". In other words, you'll either have furnace #1 running OR furnace #2 running but you'll never have furnace #1 AND furnace #2 running at the same time.
In order for this to occur (and assuming you have one set of ductwork), you'll need to isolate one furnace form the other one as far as the air paths are concerned. As someone mentioned here, that means dampers. Depending on the duct configuration you'll need two four of them. If the duct work is configured as a "Y" (the sheet metal fitting for this is commonly called a "pair of pants") and you're having it made up, they can sometimes put a flapper-style damper at the junction of the "Y itself. This can flip one way or the other to close off one of the paths. This sounds cool, but is $$ and rarely works properly.
More than likely you'll need four dampers. One for each furnace's return air path and one for each furnace's supply air path. On these dampers you'll have 24VAC motors (on/off) and you'll want them to have a spring return (remove power, a spring will swing the dampers to their default position. On your primary furnace, these will be set up to spring open (to ensure one set is always open). On your secondary furnace, they'll spring closed.
Now your furnaces are able to be isolated and ready to be controlled.
For control, I'd be tempted to use one thermostat and instead of hard wiring it to your primary furnace as it is now, I'd wire it to a small relay bank (one for power source, one for heat, one for fan etc.). This relay bank can be controlled by a simple toggle switch for Primary System or Secondary System. The signal for heat from the t-stats would then be diverted to the appropriate unit (depending on your selection on the toggle switch), and parallel with that call would also be a signal to your dampers. This can further be wired (with additional components) for an auto-changeover in the event of a unit failure, but that's more than I want to go into here.
So there you have it. It's not a simple as you'd like it to be, but it's also not that complicated and if it's important to you, I'd take the time, spend the $4 and do it properly so you have a safe installation and an efficient heating system.
Rob