Electrical motor power cord questions

Posts

Electrical motor power cord questions

#1

Electrical motor power cord questions

wilbur

>I have a motor that I would like to replace the power cord on, and was looking at another machine that I have for some guidance as to what type of power cord I need.

Two questions:

First, is there a chart or reference somewhere that tells you what gauge wire you need in a power cord for a motor that draws a given amperage, as stated on the nameplate? Such as, "10 amp 1.5 HP motor on 230V needs 14/3 wire"

Second, on the machine that I'm working off of, the motor is rated at 8.9 amps at 220V. The power cord has a NEMA 6-15 plug on it, obviously meant for a 15 amp circuit. But the wire on the power cord says that it's 16/3. I thought it was a no-no to have 16 AWG wire on a 15 amp circuit, and that you needed 14 AWG wire, since 16 AWG wire can't carry that much current, and you have the risk of a fire. If 16 AWG wire is bad in the wiring, it should also be bad for the power cord. So why would a machine with a NEMA 6-15 plug have the power cord made from 16/3 wire?

Re: Electrical motor power cord questions

#2

Re: Electrical motor power cord questions

Howard Norman

>A power cord using #16 wire for a motor that draws <10 amps is fairly common based on my experience. The cord normally is relatively short <10 feet usually.

Re: Electrical motor power cord questions

#3

Re: Electrical motor power cord questions

John in NM

>If you have a copy of the pocket ref book, it'll have a table or two you can use for this.

On the second question, the motor is still only drawing 8.9 amps, so the wire is sized ok. It has a 15 amp plug because thats pretty much the minimum circuit "size".

Re: Electrical motor power cord questions

#4

Re: Electrical motor power cord questions

Chuck in ND

>The motor is rated at 8.9 amps per leg at 220V. Meaning the motor would be drawing 17.8 amps at 110V. If you were running the saw at 110V you would need a heavier gauge cord and breaker. The motor is drawing 17.8 amps weather you run it at 110V or 220V. It's just at 220V your spliting the amps and you can use a lighter cord than at 110V because your running less amps per leg. I hope I didn't confuse you.

Re: Electrical motor power cord questions

#5

JL

A good book to have is linked here. *LINK*

JL

>I've seen it other places than Highland also. It has plug guides, wire guides, etc. etc. One of the best little reference books. Sort of like a CRC Handbook for shop work.


Handyman In Your Pocket guide

Re: Electrical motor power cord questions

#6

Re: A good book to have is linked here.

Clint Searl, at the base of Haycock Mtn

>I still have my CRC Chem&Physics and Math tables from 1957. Eshbach from a couple years later, too.

Clint

Re: Electrical motor power cord questions

#7

Re: Electrical motor power cord questions *LINK*

Bob Entwisle in NJ

>Hi wilbur,

The 14 guage for 15 amps, is an NEC spec for house wiring etc. The actual ampacity of 14 gauge wire is nealy double that. The ratings on wire size vs current capacity is all about the resistivity of the wire and the temperature rise on the wire due to the ir drop when current is flowing through it. A larger ampacity plug on a lower ampacity wire is no problem as long as the device that the cord is supplying is rated at or below the wire capacity. What you can not do is us a 10 amp plug on a 15 amp rated wire to supply a 15 amp device, that would cause the plug to overheat.

I've attached a link to to a wire table to further confuse and muddy the waters.

Bob


http://www.powerstream.com/Wire_Size.htm

Re: Electrical motor power cord questions

#8

Re: Electrical motor power cord questions

Barry Irby

>I probably should not shoot from the lip here, but I think there are a couple of other considerations. I believe there are exceptions in the NEC that allow for what would appear to be overloads on short cords. In other words, It is permissible to at least heavily load a short cord briefly. Also, stranded wire will carry more current than a similar solid wire. And, The rating of the insulation on the cord is important. Much of the stuff about electricity is about heat. Passing electricity through wire generates heat. Joulean Heat, named after the early physicist Joule. All of this an much more is why there is no simple answer to your question. Any "simple" chart would have to have a column for the time duration of the load, the type of Insulation on the wire, Whether the wire is in open air or in a conduit, the type of metal the wire is made of, Stranded or solid, the length of the wire, and perhaps the environment. Probably a couple of more. So the charts you see are simplified by making a bunch of assumptions and then list a wire that is "conservative" and will easily handle the load without over heating.

Re: Electrical motor power cord questions

#9

Re: Electrical motor power cord questions

Rick Christopherson

>

Chuck Said:

The motor is rated at 8.9 amps per leg at 220V. Meaning the motor would be drawing 17.8 amps at 110V. If you were running the saw at 110V you would need a heavier gauge cord and breaker. The motor is drawing 17.8 amps weather you run it at 110V or 220V. It's just at 220V your spliting the amps and you can use a lighter cord than at 110V because your running less amps per leg. I hope I didn't confuse you.
Well, you confused me, and I am an E.E. (grin). Actually, what you stated is a very common misconception with 240 volt circuits and gets repeated quite often. A circuit is a circuit, regardless what voltage it is operating at. There is nothing magical happening at 240 volts. Whatever current is flowing "out of" one wire (so to speak) must flow "into" the other wire.

Saying that 1/2 of the current is coming from one phase and the other 1/2 of the current is coming from the other phase is leaving one very important question unanswered: Where is all this current going? If you had two roadways leading to your favorite beach, but no roadways leading away from the beach, it wouldn't take long before the cars began to pile up and you could walk across the lake on the roofs of the sunken cars.

Instead, you would have one road going to the beach, and one road leaving the beach, and all the traffic flows smoothly. If you want to account for the "AC" in AC power, then on even days the traffic would flow in one direction on both roads, and on odd days, the traffic would reverse.

To understand why there is a difference in the current on a motor operating at either 120 volts or 240 volts, consider having two pieces of roadway that are each 120 feet long. Each piece of roadway can have a maximum of 10 cars per minute pass through the single lane while maintaining the 2-second safety spacing between cars.

If you place the two pieces of roadway end-to-end, then you have a single section of roadway that is 240 feet long, and 10 cars pass per minute. But if you put the two pieces of roadway side-by-side, then you have a 2-lane roadway 120 feet long, but with a total traffic flow of 20 cars per minute. At any instant in time, there is always the same number of total cars on these two pieces of roadway, regardless how you have them connected.

Re: Electrical motor power cord questions

#10

Re: Electrical motor power cord questions

JoeW in Detroit, MI

>The rules for flexible power cords are different than that of regular house wiring (Look at the cord on your toaster). NEC Table 400.5(A) gives you the ampacity you would need. As someone stated above, wires can usually carry more ampacity than what we are normally used to. If your motor was factory wired with AWG16, I would think the factory engineers have done the research. Table 400.5(A) for type SO cord AWG 16 wire gives ampacties of 10A for 3-conductor cord and 13A for two conductor cord. For 14 AWG wire 15A for three conductor and 18A for two conductor wire.