Relocating shop sink: Possible code issue?

Posts

Relocating shop sink: Possible code issue?

#1

Relocating shop sink: Possible code issue?

Dan Mitchell

>I have an old plastic utility sink in my 2.5 car garage/shop. I want to replace it with a new one, relocated to the position shown in the pic. The current sink is about 8' to the left of where the one in the pic is sitting. The new location would give me much more usable space for my shop. The hot water heater & in fact all plumbing in the garage serve a living space addition added over the garage some years before we bought the house. I'm wondering if having a sink right next to an electric service panel is a code issue. Opinions?

TIA

Dan


img

Re: Relocating shop sink: Possible code issue?

#2

Re: Relocating shop sink: Possible code issue?

galen V

>Electircal panel is not NEMA 3R or 4 for splash of water and I imagine it is not going to meet code by your local building code. Does your living space above garage meet code? I did not worry too much on my own installs. You sure box yourself in to run new plumbing and drain and still get to the cleanout plug I see in sewer pipe.

You must be in a siesmic zone with two straps on your water heater so maybe meeting code is more important.

In my town it never hurt to call local building inspector, it just may take forever for him to get back to you. Not suppose to cost for a determination, just inspeciton here.

Re: Relocating shop sink: Possible code issue?

#3

Re: Relocating shop sink: Possible code issue?

Tom MacGregor

>To meet code requirements in the buildings I've been responsible for outlets within 8 feet of a water source had to be GFI protected, and service panels had to have 3 feet of clear space in front of them for access. The sink may or may not block enough of the access to be a problem, but as you can't add Ground Fault protection to a whole panel it may be too close anyway.

If this is a permitted project and will require an inspection you should be able to question the inspecting agency as to what is acceptable. If liability is a concern get the agent in charge of your homeowner's policy to earn their keep & help find the answer.

There are also those who would choose to set up their personal space in their owned single family dwelling as they see fit and make a few quick changes if they ever sell the place. Not that I've ever done that...

Re: Relocating shop sink: Possible code issue?

#4

I wouldn't wash my hands.....

Mark Goodall - ATL - tooljunkie

>I wouldn't wash my hands in a sink that was that close to an electrical box. Call me a ninny, but it would make me nervous.

Happy Woodworking!

Re: Relocating shop sink: Possible code issue?

#5

Re: Relocating shop sink: Possible code issue?

Fred Davis

>Dan,

because of clearance requirements adjacent and below the panel, you would want to ask a inspector before you do this .

Since the sink is nonconducting plastic and the panel door is not obstructed , they would probably go for it , if the Fire Marshall does.

In my experience with the area in a garage with a Water Heater next to a Laundry Tray , like you show, they would definitely want the T@P valve connected to a pipe and dumped in the sink to keep you from being scalded if it went off while you were standing next to it.

In case they don't allow any of your project as you show it, ask them what they would allow.

It's better to know up front then have a house inspector nail you for it in the event you sell it down the road and ask for a signed off permit.

Permits after the fact always cost more , for the inspection , permit and any upgrading they might require from the Building Dept.

FredD

Re: Relocating shop sink: Possible code issue?

#6

So I'm not seeing a lot of enthusiasm for the sink

Dan Mitchell

>I suspected the sink near volts thing would raise eyebrows, how about if I move the water heater over a tad, like, say, 18" or so? Distance from the water heater to the wall with the panel is 39". This water heater only serves the added space, the main heater in the house is actually 12" max from the main service panel in the utility closet with the furnace. With the heater moved over, I could put the sink on the left side of the heater, where the old one is but over a bit, essentially gaining 18" in the area where I need it most. (The "shop" occupies this area to the left of the heater, a car is parked directly in front of the heater). BTW there is no laundry equipment, sink is just for washing paint brushes, etc!

I know I can call the inspectors, but I'd like to get some informed opinion 1st!

Hope that's somewhat clear & thanks for the input!!! ;-)

Dan

Re: Relocating shop sink: Possible code issue?

#7

Re: Relocating shop sink: Possible code issue?

Kevin Mac Luskie

>The biggest issue, is what Tom Pointed out. The clearance. By NEC, it has to be 30" wide by 36" deep. Doesn't matter whether it's a sink or a cabinet. Nothing fixed is supposed to be in that space. The Panel doesn't have to be centered in the 30" width, but the there does have to be 36" of clear space out from it. Since the sink overlaps the panel(in your picture) that's would be the problem.

Picture I scavange from another form (http://ths.gardenweb.com/forums/load/wiring/msg1122532114915.html) depicting the 30" width options.


img

Re: Relocating shop sink: Possible code issue?

#8

Re: So I'm not seeing a lot of enthusiasm for the

Fred Davis

>You can wash anything you want to in the laundry Tray , Dan, call it a sink if you like , but if you were specifying one on a house plan or remodel or taking to a building dept or plumber , the term is Laundry Tray. Thank you . ;-))

Fredd