VFD/3 phase mounting question

Posts

VFD/3 phase mounting question

#1

Moses Yoder

VFD/3 phase mounting question

Moses Yoder

>I am hooking up a variable frequency drive to a 3 phase Powermatic table saw. Is it typical to attach the VFD directly to the table saw and use the VFD to switch the saw on and off? The manual instructs me to mount the VFD on a "vibration free wall, otherwise it might fall and hurt someone". This may be extremely helpful to the village idiot, but apparently not so much to an average joe. Will the vibrations from the saw ruin the VFD? Another question is concerning the dust that will get into the open vents on the VFD; is it okay to just blow it out once in a while, or should I protect it with a shroud of some sort? Any other words of wisdom would be apreciated. The motor is a 1-1/2 HP, and the VFD is rated for up to 2 HP, a new Hitachi VFD.

Re: VFD/3 phase mounting question

#2

Re: VFD/3 phase mounting question

galen V

>I'm not a big saw man but you must want speed control to cut plastics or other materials a slower speeds? If table saw motor is fan cooled I assume you will run saw fast enough the motor will be adequately cooled? Not sure what class of service your motor is or if fan cooled.

You did not say what model VFD you have nor features on it to know a lot. Would think a manual will give you most detailed info.

Vibration from a table saw should not be a problem with most VFD mounting. The VFD manual should give you some idea of clearance to other objects to allow for proper cooling since it would have a good size heat sink on a 2 HP panel. Dust would not be a good thing if panel is vented nor putting a shroud around it that would limit good circulation to cool panel. Keep the unit clean. Manual and included features it has should give suggested wiring. In most cases it is not recommended you switch off the motor leads between the motor and VFD. Cut power to to the VFD. Does VFD have local or remote stop/start or enable/dissable? Does panel have some adjustment for inrush current and time to match your motor current and time to bring to speed?

Hope some may answer your questions but sorry to ask more than I may have helped.

Re: VFD/3 phase mounting question

#3

Re: VFD/3 phase mounting question

Bill Howatt

>The VFD on my General lathe is mounted in a gasketed steel box that is probably about 3X larger than the VFD. I wouldn't imagine vibration to be an issue since lathes do vibrate and sometimes a lot worse than a TS. I certainly would build an anti-dust enclosure.

On my lathe, the motor is turned on/off (rotate or not rotate) by the VFD's control inputs. The 24V generated by the VFD is applied via the switching to the correct input to cause rotation. The VFD remains powered up as long as it is plugged in. When using the lathe I leave it plugged in unless lightning storms are predicted. I don't like cycling the 240V power needlessly because I am a firm believer that startup surges are not electronic equipment's friend.

Bill

Re: VFD/3 phase mounting question

#4

Not a biggie.

Forrest Addy

>Not a biggie.

VFD's aint rocket science but they take a little study before the instructions for their become understandable.

Tablesaw dust is not conductive and I doubt if wood sawdust will hurt the drive. However it's a good isea to protect expensive industrial electronics from any kind of dust and that includes sawdust.

I suggest you find an electrical enclosure such as made by Hoffman that's enough oversize to accept the VFD; one that provides cooling allowances in compliance with the VFD's instruction manual. You're looking for a NEMA 12 enclosure (dust tite) and they cost about $60. Here's a start but it may be a little large:

http://cgi.ebay.com/VERY-NICE-HOFFMAN-ELECTRICAL-ENCLOSURE-MODEL-A-161410CH_W0QQitemZ360079076361QQihZ023QQcategoryZ42886QQssPageNameZWDVWQQrdZ1QQcmdZViewItem

Or if you're making one it really should have sheet metal panels. Frame it with angle or wood. Provide a gasketed door for access.

There's not much vibration on a table saw. Mount the VFD and its enclosure where it won't interfere with the saw's operation but where you can get ready acccess to it.

It's specifically stated in every VFD manual I've ever read (dozens anyway) that the should be no contactor or circuit disconnection between the VFD and the motor. Always control it from the VFD's control input terminal strip following the suggested circuit diagram for a three wire control. Use a pushbutton start/stop control station; maybe the control station that came with the saw can be re-utilized. I doubt if you'll ever need the variable speed control on a table saw but you may wish it was handy if you later run a lathe or drill press from the VFD you use on the saw, so plan ahead.

Once the VFD is installed you can have a nice few hours getting the control parameters set for your application. I suggest you leave the parameters in default setting except for accel and decel. I suggest you set the acell and decel to 3 seconds. This allows a surge free start and a safe decelleration without spinning the saw blade off the arbor nut. Most of the other parameters in that long list (probably a hundred) won't mean much for everyday table saw operation.

Finally circuit protection. Most VFD's these days are listed by UL as a motor over-current protection device much the same as line fuses or a motor combination starter. However you still need a means of disconnecting the VFD from the branch circuit that feeds it. The branch sircuit breaker in the shop panel will do if it's in sight of the saw or you may wish to install a wal disconnect. Consult your local code.

Re: VFD/3 phase mounting question

#5

Re: VFD/3 phase mounting question

Phil in NJ

>As others have said, there is good reason to protect the VFD from dust, and to provide adequate air circulation to cool it. The recommendation of a metal NEMA enclosure is a very good idea.

In the rare circumstance that the VFD fails and catches on fire, the enclosure would be a very good thing, in addition to keeping dust off the VFD.

Other things to consider:

- disconnect. The ideal setup is to have a contactor between the electrical supply and the VFD. With a contactor here, there is no chance that a power hit would cause the drive to ever restart the saw motor. Normally the contactor would not start the motor on return of power, but the contactor is an extra safety measure.

- fuses. The ideal setup would have fuses between the supply and the contactor. This way, serious overcurrent conditions will blow fuses.

- grounding. It is critical that the VFD be properly grounded. This means bolt the drive to a metal enclosure, hook ground up to the drive's grounding lug and the enclosure.

- stop and start the drive through buttons, not cutting power to the drive.

essentially you want

outlet -> fuses -> contactor -> vfd -> motor

I setup this kind of system for a lathe recently (Hitachi L200 VFD).

It was a fair amount of work but works very nicely.

-Phil

Re: VFD/3 phase mounting question

#6

Uhhh, Moses - is that VFD big enough?

Tim Greif - West of Chicago

>If this is for your shop at home, remember that in order to use a VFD on single phase input power, you need to de-rate the VFD by up to 50%. i.e. you can run a three phase motor on single phase with the VFD but the VFD manual will tell you how much you need to de-rate it for use on single phase input. I think you may need more than a 2HP VFD to operate that 1.5HP motor on single phase. Then again, I may be full of it.

Re: VFD/3 phase mounting question

#7

Jesper, Denmark

Re: VFD/3 phase mounting question

Jesper, Denmark

>Phil,

I think the codes would like this set-up better:

outlet-manual disconnect in sight of the motor-fuses-vfd-motor.

I do not see the purpose of the contactor and it is not acceptable as a safety disconnect.

Re: VFD/3 phase mounting question

#8

Re: Uhhh, Moses - is that VFD big enough?

Alan in Little Washington (NC)

>Derating a VFD is not always necessary when supplying it with single phase power. It is a function of the VFD and components used. You can often find VFD's, usually less than 3 hp, which do not require derating. Those VFDs will often list the ratings for each type of supply power. It is not a function of the VFD per se, but the current and heat capacity of just some of the components. Some lower hp VFD's are often built with higher rated components.