Heating Spray Booth

Posts

Heating Spray Booth

#1

Heating Spray Booth

howard

>My new shop is 24' x 24' and I am going to build an 8 ft square finishing booth in the corner. The shop is fully heated and I'll use an open window to pull in fresh air when the exhaust fan is on. my plan is to turn the heater up so the whole shop is warm once I start spraying. What are your thoughts, would the booth get too cold anyway.

Re: Heating Spray Booth

#2

Re: Heating Spray Booth

Clint Searl, at the base of Haycock Mtn

>If you're planning to spray anything bigger than a bread box, you may find 8x8 to be too restrictive. And if you're going to spray solvent release finishes, you'll need lots of air movement to get rid of the overspray, which probably means more air exchange than the heating system can keep up with. Unless it's a small job, I do any spraying outside.

Clint

Re: Heating Spray Booth

#3

Re: Heating Spray Booth

Pete LaBelle

>Yup, you will suck heat from the shop. Don't turn up the thermostat, it'll take care of itself. Your spraying will only take a few minutes, not hours on end. Once you get done spraying, turn off the fan. It's done its job of drawing off overspray. If it is fumes you are trying to expell, maybe install a speed controller to the fan to dial it back to an idle at this point, or turn off the fans and go in the house for the night.

In all cases, if you don't have a door/window open while the fan is on, air movement will be very small.

Also, as a safety concern, if your exhaust fan is on and no doors or windows are open, it will draw air thru the exhaust of a gas furnace or wood stove, making the shop air hazardous to breath.

Re: Heating Spray Booth

#4

Thanks Guys!

howard

>

Re: Heating Spray Booth

#5

Re: Heating Spray Booth

jan derr

>this is from a bit of experience. FIRST! don't draw air over your work; it will dry too fast on the surface and orange peel. so, put you suction low and place your air return ports close by the suction port and work it so it won't suck the air out of your shop.

SECOND! don't use sovent based finishes that you wouldn't want your children to breathe. They don't want you breathing that shit either.

THIRD! if your not using solvent based thinners why not filter your air back into your shop? May be I'm wrong?

Re: Heating Spray Booth

#6

Re: Heating Spray Booth

Barry Irby

>My friend has a shop about 26 by 60' with a spray room in the end that is about 10'. (so the shop is 26 by 50 and the spray room 26 by 10). He builds kitchen cabinets for a living. For the shop, he has an 85,000 BTU gas furnace. It has a regular return and filters the air. For the spray room he has a 400,000 BTU furnace. It draws air from outdoors and blows it through the spray room. There is an explosion proof exhaust fan in the spray room. This is all on Propane.

He built the windows for his shop and never got around to completely finishing them. The sashes are held in place by a number of small blocks with a staple or two in each.

One day, something went wrong with the big furnace and it failed to fire, but kept dumping gas in the shop. He opened the door from the spray room just as the gas reached the pilot in the other furnace. BOOM! Apparently, the thing that saved him was the fact that it blew all the windows out, letting the pressure off. All the sashes were laying out in the yard. Only broke one or two panes. He says he just stood there while the air in the shop burned all around him. It was so fast he did not have time to poo his pants.

Have no idea what this has to do with your situation, just thought I would share.