220 Breaker Question

Posts

220 Breaker Question

#1

220 Breaker Question

Tony - Memphis

>I'm adding a 220 outlet in my shop. I got everything installed with no issues. Then, when I went to plug the circuit breakers in (20A double pole), I realized that there was no contact to the bars. In other words, the bars that are in the oopen slots I have only allow connection on one side. There are already breakers on the other side (the right side). But, because the bar doesn't go across, no breakers could be added to the open slots on the opposite side of the panel (the left side). I shoulda took pictures. Oh well. Can you replace those bars? Without changing those, the two open slots are not useable. At first, I thought I'd just move some things around, but that wouldn't work.

Thanks,

Tony

Re: 220 Breaker Question

#2

Re: 220 Breaker Question

Bill Hammond, Oregon Coast

>You may be able to replace several single pole breakers with half size breakers. Often they look like mini 220 breakers but the handles are not ganged together. They come in 15, 20 and 15/20 versions. If your lucky you can replace 4 single pole breakers with 2 of these and have an opening large enough for a standard 220 breaker. When buying the breakers be sure to get ones that are made for your panel. Some panels are made so that this type of breaker can not be used. Ehe way around that is to modify the breaker, but I can not tell you that as it's probably illegal.

Take care when messing around in the panel, remember the inconvenience of turning off the power to the house verses being dead.....

Bill, on the foggy Oregon Coast

Re: 220 Breaker Question

#3

Re: 220 Breaker Question

Kneale Brownson dreaming of snow in N. MI

>If you use the mini breakers to solve your problem, be certain not only that the breakers will fit your box, but also that they're made by the manufacturer of the box. I read about someone's insurance company declining a fire claim because they had used some cheaper "aftermarket" breakers in their breaker panel rather than the original manufacturer's product.

Re: 220 Breaker Question

#4

Re: 220 Breaker Question

Rick Christopherson

>The phases on a load center are not grouped by right and left sides of the panel. They alternate one for the other vertically on both sides. If your 2-pole breaker is connected to the same phase on both of its poles, then you simply need to move it up or down by 1 position (by a single-pole breaker).

Re: 220 Breaker Question

#5

Re: 220 Breaker Question

Barry Irby

>I am a Home Inspector, not an electrician, co take this with a grain of salt.

It sounds like you tried to put the new breaker in a blank area that was not really intended to have a breaker and therefore had no buss bars. And no, you can not change out the buss bars.

Rather than change out four single pole breakers to make room for one standard 220 breaker, why not remove an existing 220 breaker and replace it with a 220 mini breaker? If you have a 20 amp 220 breaker, it would be easy to replace it with a mini or half sized breaker. Even if you have to replace a 30 amp breaker, they make the mini's in mixed sizes such as a 20 and a 30 in the same unit. Be sure to buy one that is manufactured for your panel. Also note that the wiring pattern appears odd. One circuit attaches to the two "inner" breakers and those handles are ganged together and the other circuit attaches to the two out breakers and those two handles are ganged together. Look at the instructions carefully.

Re: 220 Breaker Question

#6

Re: 220 Breaker Question

Tony - Memphis

>Well, I really should have taken a picture. Its hard to explain in words. I may take the door off and take some pics tonight. The two open slots I have are full size slots. The way the bus bars are done, the breaker connection is screwed to the bus bar. These connections are like tabs where the breakers attach. They are different. On some slots, they extend across such that you can attach a breaker on either side. On the open locations I have, because of the way the tabs are, you can't put a breaker there (there is nothing to connect to the bus with ie no tab). There are breakers on the right of these. My box does have some of the 1/2 size breakers.

Thanks,

Tony

Re: 220 Breaker Question

#7

Re: 220 Breaker Question

Tony - Memphis

>Thanks. I have a main breaker inside the garage that shuts off power to the shop completely (code). I shut it off before I do anything. And my dad taught me to treat everything as if it was live anyway. I also check with a meter to make sure things are dead.

Tony

Re: 220 Breaker Question

#8

Re: 220 Breaker Question

Tony - Memphis

>I already have a couple of minis in there. Fortunately, my box is a GE and the big boxes carry GE stuff.

Tony

Re: 220 Breaker Question

#9

Re: 220 Breaker Question

Tony - Memphis

>Yeah, I understand the alternating thing, but that's not my issue. These two open slots have nothing to connect to. There is a small piece that is screwed to the bus bars that have little tabs sticking out for the breaker to grab. On these two open slots, there are no tabs to grab. Not sure if they came that way or if the electrician put those in according to how he wired things.

Tony

Re: 220 Breaker Question

#10

Re: 220 Breaker Question

Tony - Memphis

>Thanks. I wasn't suggesting changing the bus bars, just the pieces that attach to the bars that have the tabs sticking out for the breakers to attach to. This is a GE box, btw. What I'm looking at deosn't make any sense to me. MOst every other box I've looked at had just plain old alternating connections were it would be easy to snap in a breaker. I got everything wired up, plugged in my breakers, turned on the power, and checked the outlet with the meter and...nothing! That's when I got to looking at where the breaker is supposed to attach to the bus. I tried to research my box online, but I couldn't even find a mention of it. I may have written down the number wrong. I wrote down GE PowerMark PLus Load Center Cat # TLM6F. It has 4 full size slots on each side. Right now, I have two 20's for my ac in the upper right, two 20's below that for receptacles, and other side, I have a full size 20 on top and two 1/2 sizes in the next slot for lights. That leaves the lower left two full slots empty. That's where I was trying to add my double pole 220V 20 Amp breaker. I may just have to break down and call an electrician. Hate to do that, but if something fancy is required, I'd rather let someone else do it. I was quite comfortable with what I was doing, but beyond that, its easier and smarter to call a pro. Thanks for the input. I appreciate the help. I am learning much more than I knew about all this stuff. I've wired several outlets and lights, but never been inside a panel. I've been doing a lot of research to get to this point. One issue too is that there is not enought wire to move some of the breakers. This may be a big mess by the time its all over!

Tony

Re: 220 Breaker Question

#11

Hmmm...

Tony - Memphis

>Well, I just found the part number quide and my box only has 6 full size spaces. That must be why the two in question don't have tabs! That makes sense. Now I just gotta figure out how to arrange things to get my new outlet in.

Tony

Re: 220 Breaker Question

#12

Re: 220 Breaker Question

Fred Davis

>Tony ,

this not meant to be a attack on your manhood , but I guarantee from reading your posts , that your box is to small for what you want it to do and your experience level has got you to the point that you can hurt yourself or burn down a building.

Call a electrician, they shouldn't charge you to tell you what you need. Think about it.

FredD

Re: 220 Breaker Question

#13

Agreed..thanks.

Tony - Memphis

>