OT-Electrical Wiring

#1

OT-Electrical Wiring

howard

>I am going to connect my sander and planer. Can I run 2 hot 10 gauge wires (coming from a 30AMP breaker)and 2 hot12 gauge wires (coming from a 20 AMP breaker) through one run of 3/4" EMT?? There will also be a ground wire for each machine. So there will be a total of 6 wires, but 4 conductors. Both the planer and sander are on 220 V. I wasn't sure if I needed to use separate EMT for each machine. Appreciate your help with this.

Re: OT-Electrical Wiring

#2

Re: OT-Electrical Wiring *LINK*

Stuart Johnson

>This link should help you.


Conduit Fill

Re: OT-Electrical Wiring

#3

Stuart - This is very useful- Thanks

howard

>

Re: OT-Electrical Wiring

#4

A couple of general cautions

Rod Peterson -- Ormond Beach

>First, the NEC upon which that table is based is fifteen years old. While I'm sure the laws of physics haven't changed in that time, the folks who write the NEC may have made revisions based on more complete data.

Secondly, I'd have to say that while the numbers may be adequate for the purposes of fire protection (in 1993), from the standpoint of physically pulling wire, they may be a little optimistic. It's hard for me to imagine getting ten #12 wires through ½" conduit past one bend!

Still, that's not what you're proposing, so you should be more than safe based on the conditions you postulated.

Rod

Re: OT-Electrical Wiring

#5

Thanks Fod

howard

>

Re: OT-Electrical Wiring

#6

So Sorry - Thanks Rod!

howard

>