>My house is pretty old, and most of the wiring in the house is 2 conductor wire in armored cable, where the armored cable seems to serve as the ground.
There are a few GFCI outlets installed in the house, but when I was doing some fixing of the wall plate, I found out that the GFCI outlet's green ground screw actually isn't wired to anything. I know that normally the ground wire would be hooked up to the green screw. The test/reset buttons on the GFCI outlet seem to work normally, and if I plug in one of those three prong circuit/polarity testers, the lights indicate that the polarity and ground are okay.
Does the ground screw of the GFCI outlet need to be wired to ground? And for that matter, if I have a three prong outlet in a box that is fed with two conductor wire, do I need to hardwire the ground screw to the box/armored cable?
Re: OT: GFCI outlets in a house with old wiring
Lee Schierer - McKean, PA
>I believe that what you are seeing is the electrical path of the metal bracket that holds the GFI in the box to the metal box, which in turn is attached to the shielding on the cable. Ideally the GFI should have it's own ground as the other connections can be unreliable due to loosening or corrosion or get changed in the future without anyone noticing that the ground path has been lost. I do not know if code allows this or not as a safe connection for a GFI.
Lee
Dan Donaldson
>In some jurisdictions they will allow addition of a GFI on an existing two conductor circuit where it is not practical to get a ground wire there. Most GFI plugs have a sticker in the box that says something like "This is an ungrounded circuit" and is required to be on the plug when used in this manner.
Bill Howatt
>The armour is likely providing the ground which is why your tester showed it as being wired correctly with a ground. The connection to the GFCI outlet is being made by the "mounting" screws holding the outlet to the box. I would imagine it would be better with a copper wire between the box ground bonding screw and the outlet's green ground screw. I have no idea about code requirements when using armoured cable but if the house was wired with it then the boxes/bushings are most likely appropriate.
The good news is that a GFCI measures the current going down one wire and back on the other without any need for a ground connection. If the currents don't match within about 0.005A then the GFCI assumes something undesired (like a person) has the difference current running through it and trips the circuit.
Re: OT: GFCI outlets in a house with old wiring *LINK*
Alan in Little Washington (NC)
>The NEC requires you to install grounding-type receptacles on 15A and 20A branch circuits. Per Sec. 210-7, it also requires you to effectively ground the grounding contacts of those receptacles to the branch circuit equipment-grounding conductor. But, what can you do about old 2-wire nongrounding-type receptacles, where no ground exists in the outlet box?
Sec. 210-7(d)(3) permits any of the following installations when replacing a 2-wire ungrounded receptacle:
(a) Replace it with another 2-wire receptacle;
(b) Replace it with a GFCI-type receptacle and mark the receptacle with the words �No Equipment Ground;� or
(c) Replace it with a grounding-type receptacle protected by a GFCI device (circuit breaker or receptacle). Since the grounding terminals for the receptacles are not grounded, you must mark the receptacles with the words �GFCI Protected� and �No Equipment Ground� (see sidebar below).
For more info see the link
GFCI and grounding info