Electrical problem(strange to me anyway)

Posts

Electrical problem(strange to me anyway)

#1

Electrical problem(strange to me anyway)

Paul Waddle

>Today,one circuit in our house went out. No big deal,I just flipped the circuit breaker and flipped and flipped some more. Satisfied I had a bad breaker,I pulled it out,tested the continuity(tested ok),but I was sure the breaker had to be the culprit. Just as I was heading to the hdw store,wife,who was driving somewhere,signaled me to stop. She said the electic company was working on a transformer accross the street. Well,I STILL was convinced I had a problem,but trotted over and asked the utilty man about my problem. He said sure,one leg of the voltage was down-pulled loose from the transformer!! He went on to say,you had 220v and one leg???? Well I told him something strange was happening; on the circuit that was off,a fan was running very slowly... He said sure,you're getting feed back from your ac.... Dang,I was a naval electrican may eons ago,but never encountered something like this. Hope it is interesting to the readers. pw

Re: Electrical problem(strange to me anyway)

#2

Re: Electrical problem(strange to me anyway)

Chuck W

>You said the wire from 1 leg of the transformer fell off so in my mind you would only have 110 volts to the house.

Re: Electrical problem(strange to me anyway)

#3

Re: Electrical problem(strange to me anyway)

Paul Waddle

>Thats what I would think too,but ac and all other ckts ran fine. I'm just expressing what the utilty man told me... No other explantion.. but wait... 220 is accross two hot legs,110 I suppose ground could suppy the other hot??? This would then explain how 110 would be available on one side and not the other,at least at the same time ????? pw I donno I donno... Have a good 4th

Re: Electrical problem(strange to me anyway)

#4

Re: Electrical problem(strange to me anyway)

Randy Johnson Connersville IN

>The first time I encountered the problem was when I was in the Air Force. I was one of three in my shop that pulled ALL afterhours service calls. It wasn't so much due to expertise but rather from being low men on the totem pole.

The base I was at fed each leg with a seperate line fuse and as a result it was a fairly common problem.

Since becoming a civillian again I have always found the problem to be caused by a loose connection or a bad main breaker.

Usually the read from the "dead" leg to ground will be around fifty volts. An easy way to know for sure if you have a dead leg is to turn on all the lights. The ones on the dead side will just sort of glow a dull yellow.

This is one of those places where you need a volt meter or, at the very least, a "wiggy". Those little testers that look like a small screwdriver with a light in the handle will lie to you because there is enough voltage present to make them show positive.

Re: Electrical problem(strange to me anyway)

#5

Re: Electrical problem(strange to me anyway)

John Ballance

>The electrical service to your house consists of two 120 volt supply legs, plus a neutral leg. (Think of the neutral leg as being halfway between one of the 120 volt legs and the other.) In your breaker panel, typically one 120 volt leg will connect to all circuit breakers/fuses on the left side of the panel, and one 120 volt leg will connect to all the circuit breakers/fuses on the right side. Your 120 volt appliances take power from one of the 110 volt legs and the neutral leg, while your 240 volt appliances take power between the two 120 volt legs (with no connection to neutral). (Note that ground is different from neutral, and is essential for electrical safety.)

It sounds like one of the 120 volt legs from the utility transformer was disconnected between the transformer and your house (per the utility serviceman's comment). However, if you had a 240 volt device (such as an electric range or a 240 volt room air conditioner) turned on when this condition occurred, power would flow from the energized 120 volt leg through the 240 volt device, and provide some small amount of power to all of the 120 volt appliances (such as fans, lights, etc) connected to the dead 120 volt leg (which would be backfed through the 240 volt device). This condition could also occur if any of your neighbors who were served from the same distribution transformer had a 240 volt appliance turned on when the 120 volt leg went dead, as their homes are electrically in parallel with your home. None of the appliances connected to the dead 120 volt leg would receive full power, but fans might run slowly and lights might operate dimly.

This "dead leg" phenomena is well known in the electric utility industry, but fortunately it doesn't happen very often. I could provide much more detail, but this should explain the condition.

My qualifications: retired Director of Transmission and Distribution Engineering for a west coast electric utility.

Re: Electrical problem(strange to me anyway)

#6

Re: Electrical problem(strange to me anyway)

Dan Donaldson

>What is even worse than what you have is if the neutral breaks in a system that does not have the equipment ground and the neutral bonded. You can almost bet that anything that runs on 120 and is voltage sensitive is going to be toast.

Re: Electrical problem(strange to me anyway)

#7

Re: Electrical problem(strange to me anyway)

John Ballance

>Yep, unless the loads on the two 120 volt legs are perfectly balanced, which they never are.

The bottom line - the electrical system works great when everything is properly connected, and if that's not the case, then many strange and sometimes dangerous things can (and do) happen.