Sort of long response
richard jones
>B,
I will hazard a fairly educated guess and say that IF you fill that space completely you will certainly be creating an overstressed situation. If you have access to the specs on the trusses or know where they came from, see if you can find out the design load. Doubtful it is going to be more than 40psf live load, so you can do the math there. It is possible to design a truss to bear your imposed loading, but I would think it would be far larger than a 2x8 bottom chord, maybe even some LVL members. I have seen some very large room trusses for ROG's with bottom chords composed of 4-ply 11 7/8" LVL's that I'm glad I don't have to lift.....:)
That said, I quite often see drywall stacked in ROG's such as yours and that has pretty good weight, and would incur more of a concentrated load stress than your rack would. Of course, the closer you keep the load to the outside walls, the less stress you place upon the assembly (imagine a see-saw with more and more people on one end. Move the people closer to the fulcrum and you don't stress the load end of the see-saw board as much. There are compromises with everything).
I've never seen a properly applied gang nail fail, altho' I've seen folks saw them in half and expect them to still do the work of the original size........:)
Track the deflection by measuring from some points on your garage floor and marking them permanently on both the floor and the bottom of the truss so that you can re-create the exact vertical line from which you originally measured. Or, use a string stretched from top plate to top plate. If you start to get quite a bit of deflection, say, more than L/360, then you may want to reconsider. Here's an excerpt from the American Wood Council, but keep in mind, this is for nominal lumber, not trusses, but does give you a good starting point: "Maximum deflection limits are set by building codes. They are expressed as a fraction; clear span in inches (L) over a given number. For example: a floor joist appropriately selected to span 10 feet with an L/360 limit will deflect no more than 120"/360 = 1/3 inches under maximum design loads. Drywall attached to the underside of this system is not expected to crack when the floor joist system deflects 1/3"." The truss specs should also include the deflection limits.
As far as catastrophic failure, unless you load the entire thing in one day, you will more likely see a gradual deflection in the bottom chord. Eventually, it could fail entirely.
Remember, you can go out and buy another car, but it took you a long time to fit those quartersawn runners on your TS sled.........:)
Rich (whew!) in VA