OT: Air Conditioner Question

#1

OT: Air Conditioner Question

Ken Krawford

>A service man came out 2 wks ago because the air coming out of our ducts was 76 degrees. He determined that the unit was low on freon and was topped up. If I remember correctly, it was about 6 lbs. The unit worked better (duct air was now 64 degrees) but the house never felt as cool as it did last year and the compressor ran all night to hold 75 degrees.

Last night the duct temp was 70 and the compressor ran constantly with 76 degrees as low as it would go.

This morning I looked at the condenser coil and it was iced.

Is there anything I can do or do I need a service call again?

PS After the first call, the compressor would not start and it turned out the system was overcharged. He adjusted it then.

The compressor is 3 yrs old and the coil is 17 yrs. Ambient temps range from 80 to 93 degrees.

Re: OT: Air Conditioner Question

#2

Re: OT: Air Conditioner Question

Curly Smith

>The most common cause of ice is a low refrigerant charge. However, ice can be caused by a dirty air filter, which restricts air flow, a dirty evaporator coil, or excessive run times --- which you have in abundance. If changing your air filter doesn't solve the problem then you need to get the unit serviced (again).

If your unit really does run all night when functioning "properly" then it's either dreadfully inefficient or undersized for the heat load. Call somebody in your area who does "energy audits" and have them check your system. You may have leaks in your ducts, you may need more attic ventilation, you may need more attic insulation, or your a/c unit may need some major work. Or, you may need all of the preceding.

Re: OT: Air Conditioner Question

#3

One more thing

Curly Smith

>If you're using the new and improved HEPA filters then try using the old standard, and cheap, pleated filters. Your system wasn't designed with the new filters in mind and they may restrict air flow below the unit's tolerances. Use the cheap filters and change them bi-weekly or monthly.

Re: OT: Air Conditioner Question

#4

Re: OT: Air Conditioner Question

Larry Clinton At Frankfort (Central)., Indiana

>The first sign of an undercharged unit is icing of the inside cooling coil. If it is easily made visible by removing a panel etc. I would look at it. Icing of the inside coil may also occur when the air flow is low. This can be caused by - dirty filter, vents shut off in several rooms etc. Properly sized an air conditioning unit should cool about 15 to 20 deg below ambient outdoor temperature when running continuous. So if you have your thermostat set at 70 deg and it is 85 outside, the unit will run continuous (or almost so). This sizing is done so that the humidity is properly reduced. Over-sized units that run 15 minutes out of an hour at those temperatures don't keep the inside environment as comfortable as they do not remove the humidity properly. This results in a "clammy" feeling as normal perspiration doesn't evaporate properly.

Re: OT: Air Conditioner Question

#5

Re: OT: Air Conditioner Question

Barry Irby

>Larry and Curly have weighed in. I guess that makes me Moe.

They are correct. There are a number of things that cause restricted air flow. dirty filters, crimped ducts, poor duct design, dirty coil, debris in the ducts, to many vents closed, Etc.

Once the icing starts, it is the self fulling prophecy. It restricts the air flow and restricting the Ari flow causes further icing. Think of it like this, the cold is cooling the air, but the air is warming the coil, preventing icing. Chicken or the egg.

Turn the unit off and let the ice melt away. This may take hours. If you can open the unit and see the ice, you may be able to set up a fan to blow on it and excellerate the process. And you will get a little of the "cool" in the house.

Try the cheap blue filters.

Once the system is free of ice and running, put a thermometer on a return grill. Then put it on a supply register. Subtract one form the other. Delta T. You are looking for 14 to 20 degrees Faren.

Less than 14 often means low refrigerant. More than 20 often means restricted air flow.

If the unit can maintain 15 to 20 degrees below outdoor temp, that's pretty good.

Re: OT: Air Conditioner Question

#6

Re: OT: Air Conditioner Question

Larry Clinton At Frankfort (Central)., Indiana

>As usual you are correct Barry. One other thing - he said the unit inside was 15 years old, compressor a couple and that the air wasn't as cold as last year. I take that to means the system DID work ok, so I would pretty well ignore the possibility the ducting was inadequate. I have seen systems that had enough dust in the system to cause trouble but only one or two out of several hundred. I used to take the blower assembly out of the real dirty units (usually ones that had sucked in grease / smoke from kitchens or ones that had been ran for years without any filter)and take them to the pressure car wash. I would cover the motor / wiring with aluminum foil & tape and spray them clean - works like a dream. (the car wash high pressure soap & water also really clean venetian blinds easily.) IMHO the service guy doesn't know how to properly charge a system or the compressor has a weak cap and won't start with a correct charge. As he already had to return to remove freon, he may have mis-diagnosed the problem or removed too much freon.

Re: OT: Air Conditioner Question

#7

Thanks for the help

Ken Krawford

>I took the air filter out temporarily (it was very clean) until I could get a new one. I had been using one of the Filtrete filters so it may have been restricting air flow. I'll try one of the "blue" ones. All vents were open. I measured supply - return differentials in 3 different areas of the house. There is 10 degrees in the warmest room and a Delta T of 14 degrees in the area that has the shortest duct run from the air handler to the vent. Since there hasn't been any remodeling, etc that has occurred in the basement, I doubt that a duct is crimped but I'll double check it.

Thanks again for the input.