Wire Gauge for Garage Shop

Posts

Wire Gauge for Garage Shop

#1

Wire Gauge for Garage Shop

Howard

>I could use help with this one. I had an electrician install a 100A sub-panel in the new shop. I got him to agree to let me place the outlet boxes and wire them to the panel. BTW, I have experience with electrical work and do not take the tasks lightly! I ran 4 different circuits - one with 4 outlets, one with three and 2 with 2 each and used 14 GAUGE wire. Got a call from the electrician (who was pissed) and said that the inspector failed the inspection because only 12 GAUGE wire can be used in a garage. I have the 2002 NEC code and do not see anything that requires this. Also, I'm confused that the electrician used 14GAUGE for the garage door openers and ceiling lights. Could someone clarify the requirement for 12 GAUGE, I now need to remove the wire and replace. Thanks for the help.

Re: Wire Gauge for Garage Shop

#2

Re: Wire Gauge for Garage Shop

Sean Troy

>He's correct. 20 amp needs 12 ga. and 30 amp needs 10 ga.

Re: Wire Gauge for Garage Shop

#3

Re: Wire Gauge for Garage Shop

Rod Peterson -- Ormond Beach

>I guess my first question would be, “why would you wire with 14 gauge in the first place?”—particularly when you put in a 100 Amp load center (sub panel).

Almost everyone I've read about in the last 15 years who was wiring a shop (garage or otherwise) always errs on the side of more capacity with a minimum of 20 Amp capacity for each circuit (consequently 12 gauge wire), and in some cases, 30 Amp or greater (5 HP machines and/or welders).

I don't know whether there is a requirement for 20 Amp circuits in a garage, but I just can't imagine why one wouldn't, especially for a shop. Most people figure that between compressors, dust collectors, battery chargers, and the particular corded tool one is using at the time, a 15 Amp circuit might be challenged a bit. That's also the argument for multiple circuits even though John-Q-Average-Homeowner probably only needs one.

Did you also wire for a couple of 240V circuits? I put five (20A) in my sub panel—compressor (might come on at any time), dust collector (running while major tool is running), table saw, planer, jointer—all running on 240V, by the way. I also have four separate 120V 20A circuits.

As far as I know, it's typical to use 15 Amp circuits for lighting (and the opener) as it would take a lot of lights to tax a 15 Amp circuit. Even the garage door opener is probably only a 1⁄3 HP motor—roughly 250 Watts.

There have been a lot of shop wiring discussions here on WoodCentral, and I've seen plenty on the wreck (rec.woodworking on usenet), as well. I can't imagine it's a foreign topic on any other woodworking forum, either, so there should be plenty of information extant on the subject. Take a look at the archives.

Rod

Re: Wire Gauge for Garage Shop

#4

JL

Re: Wire Gauge for Garage Shop

JL

>I would have no problem using 14 gauge for a lighting only circuit. I would not use 14 gauge for a receptacle circuit. I would use 12 gauge. Many power tools can pull a large number of amps - so I would want a large (20 amp) breaker and heavy wire.

I just talked to our local inspector (it's a very small county) and he said that he would have no problem with 14 gauge wire being used in a garage lighting circuit. He also said that he would prefer 12 gauge for the garage door opener because they can occasionally pull some current.

Re: Wire Gauge for Garage Shop

#5

Re: Wire Gauge for Garage Shop

Al Stokka - Cambridge, Iowa

>Howard,

I wonder...did you install 20 A receptacles (outlets)? If so, I can understand the inspector insisting on 12 ga. wire. If, on the other hand, you installed 15 A receptacles, the inspectors command that only 12 ga. wire be used in a garage is a new one on me.

Al

Re: Wire Gauge for Garage Shop

#6

Re: Wire Gauge for Garage Shop

Dan arrowsmith

>reading this thread mad me wonder what I have in my garage. How can I check whats installed, its all run in conduit. I have a small elec dist box that feeds from the house which has a square D 150 amp box.

thanks in advance

Re: Wire Gauge for Garage Shop

#7

Re: Wire Gauge for Garage Shop

Larry Clinton At Frankfort (Central)., Indiana

>Howard, the NEC is a guideline for minimum safe installation requirements. Often states, counties or localities will require more than the NEC. (Just like California requires more than the EPA etc). This may be the situation in your area. I can't cite the new NEC code since I don't use it since I retired. That said, I would never run #14 gage wire in a shop (except #14 is ok for certain lighting circuits, as you can't plug in heavy loads). My shop has a 100 amp circuit box (fed from 200A main in house). ALL my 120V wiring is #12 (including my lighting circuits). ALL my 240 is #10. I rewired a large portion of my house a few years ago - all #12 except the kitchen outlets over the counter are #10. In shop environment's, I would never use other than 20 amp breakers for the 120V outlets and 30 Amp for my 240. - this is needed to start some of the equipment normally used (most lunch box planers, 120V joiners etc. As many / most woodworkers buy newer / larger equipment as they progress with their hobby, I installed the 30 amp 240 circuits - sure glad I did as I now have a 5 hp 20" planer and a 4.8 Hp (Minimax MM16) bandsaw. The 30 amp also run my 3 hp equipment with less voltage drop so their is no downside except for the initial cost of the wire.

Re: Wire Gauge for Garage Shop

#8

Yup, yellow ROMEX for EVERYTHING !

steve mackay

>

Re: Wire Gauge for Garage Shop

#9

Re: Wire Gauge for Garage Shop

Howard Norman

>I am not aware of a code requirement for using 12 g wire in the garage but that is what I would use for outlet circuits. Fourteen gauge wire is fine for most lighting circuits when protected with a 15 amp breaker. Outlet circuits for 110 should nominally be 12 g with a 20 amp breaker. Once in awhile a 30 amp circuit is needed and that requires 10 g wire in most instances.

Re: Wire Gauge for Garage Shop

#10

Re: Wire Gauge for Garage Shop

Kneale Brownson Dreaming of the Snow in N. MI

>You can look at the copper wire ends where they enter the breakers if you take off the box cover in the garage. Turn off the breaker in the main box to be safe if you take off the cover. If you have some bits of wire around, you can compare them visually.

Re: Wire Gauge for Garage Shop

#11

Re: Wire Gauge for Garage Shop

Fred Davis

>Everything Larry said is correct and none of the different yearly versions of the NEC permit outlets wired with 14 AWG, with the lone exception being ,allowing switched outlets for lighting , such as lamps.

In addition as "new and Improved" continues to degrade equipment like motors, they become more sensitive to voltage drops , case in point being the recent (last ten years) power requirement for 3 HP motors. some and maybe most will draw much more then 20 amps on startup and some even during heavy use like ripping.

The Electrican was quite right in being "pissed" because his trade is heavily inspected and held to strict standards. I am surprised he allowed himself to be talked into a deal like that , just to save a few bucks.

In addition to having to do it over which negates any cost saving by DIY amatuers , Howard has caused the inspector to really look close for any other substandard wiring .

You can't negoiate with a surgeon to let you do some of the work, why run the risk of burning your house down and voiding the home owner insurence policy.

Do what your trained for and let the trades do their thing, much safer, less costly in the long run and the Electrican will feel like doing more of your work, instead of spreading the word about his experience.

FredD

Re: Wire Gauge for Garage Shop

#12

Huh?

Rod Peterson -- Ormond Beach

>> …none of the different yearly versions of the NEC permit outlets wired with 14 AWG, with the lone exception being ,allowing switched outlets for lighting , such as lamps.

Please point me to the section of the code that says that. Virtually every bedroom I can remember seeing has been wired on a 15A circuit, just as one example. Living rooms and family rooms are also frequently so wired. That's not to say there aren't sometimes receptacles which are switched (or half switched) on those circuits, but I'd love to see a bedroom with a 20A circuit in it. Please show me one. I must have missed the change.

Rod

Re: Wire Gauge for Garage Shop

#13

HiJak - PM2000 Outlet ?

Tony - Memphis

>I've been pondering the purchase of a Powermatic Pm2000 3hp model. The motor is rated at 13 amps. So, I am assuming I can get buy with a 20 amp 240V outlet?

My current saw is 110 and I have a floor outlet for it. I had originally thought I could just change the breaker and the outlet and label the wires correctly to identify both hots and be good, but then I realized this outlet is on a circuit with another outlet (just the two floor outlets on this circuit) and they are both controlled by a light switch. Great plan...until now! My saw resides in the middle of the shop which is on a slab, so this might get tricky. I may just have to install a wall outlet and run the cable across the floor. I have to step over the DC hose now anyway. I'll hire an electrician for that to make sure everything is done to code. I'm sure I can do it, but for the small cost, I'd rather make sure everything is legal. Besides the safety factor, I plan on selling the house someday. I'll do all the non-electrical work myself (like cutting the hole in the sheetrock and such). He/She will just run the wire and hook it up - 30 minutes probably. Wonder if I need a permit here? Hmm, maybe my old Delta CS ain't so bad! Heck, I still haven't figured out how I'd get the new saw off the truck and into the shop anyway.

Tony

Re: Wire Gauge for Garage Shop

#14

Don't give up too quickly…

Rod Peterson -- Ormond Beach

>How is the wire fed to the floor receptacle? Seems to me there's a better than even chance it's in some sort of conduit. That would make it dead easy to alter, even considering the other receptacle in the circuit. Too little info in your post to be more helpful, but an electrician should be able to give you at least a hint in about two minutes.

Rod

Re: Wire Gauge for Garage Shop

#15

Some puzzling and uber-conservative advice here

Tim Greif - West of Chicago

>I can't figure out why nobody is bringing up GFI requirements. If this is a garage as you described, all 120 volt receptacles have to be GFI protected, unless not easily accessible (think door opener ceiling outlets), or a single yoke mounted receptacle dedicated to an appliance that is always plugged in (think refrig or freezer). NEC Article 210.8 I'm really surprised the inspector didn't flag that.

I'm curious about all the other's recommendations to upsize the conductors to 12 gauge, even with 15 amp breakers. The most often cited reason is to avoid voltage drop. If you have a subpanel in the garage, it's unlikely you have any cable runs in excess of 40 feet. The additional voltage drop for a 120 volt power tool at that distance due to 14 gauge versus 12 gauge is barely measurable. Power tools these days are designed to run perfectly well at a supply voltage variation of +/- 10 percent. If a 20 amp circuit is needed, there'll be a 20 amp plug on the tool cord that will only fit in a 20 amp rated receptacle. And yes, that will need a 20 amp breaker and 12 gauge wire. I feel all other receptacles can easily be 15 amp with 14 gauge wire.

I have never heard of any requirement for a minimum of 12 gauge wire in any garage or shop. I'd love to see that reference.

All that being said, there's absolutely nothing wrong with upsizing the wiring in the interest of being conservative. I can't criticize it. Kind of like there's nothing wrong with using nitrogen in your tires or changing your oil every 700 miles. There's no harm, it's simply not necessary. But if it gives you peace of mind, go for it.

Please add the GFIs though. That's required by code.

Re: Wire Gauge for Garage Shop

#16

Re: Some puzzling and uber-conservative advice her

Rod Peterson -- Ormond Beach

>I haven't reread the posts, Tim, but I don't recall anyone counseling 12 gauge wire on 15 Amp breakers (not that there's anything wrong with that—it's precisely the same effect as pulling 10 gauge wire and putting in 20 Amp breakers, as is so often suggested—foolishly, in my mind). Not only that, but I think everyone's focus has been on the wire size and the NEC with respect to it, and not the peripheral, yet admittedly pertinent, issue of what breakers to use.

I am fully aware of the GFCI requirement, as, I'm sure, are many of the posters—but it just wasn't the question at hand. I think the real question the OP had was of the size wire, and, by extension, the capacity of the circuit as expressed in breaker size and whether it was required by the NEC.

I can only speak to my intentions in posting, but I was trying to express curiosity as to why someone would even consider 15 Amp (or 14 gauge wire) in any circuit in a shop—garage or otherwise. Once that question was answered (and so far, it hasn't been), I figured it would then be time to raise the specter of GFCIs.

My sole regret is that I didn't mention the AHJ (authority having jurisdiction—that is, the local governing body) as Larry did so eloquently.

Rod

Re: Wire Gauge for Garage Shop

#17

Re: Wire Gauge for Garage Shop

Andy Lincoln,In Dearborn MI

>I'd like to have more information on how this turns out.

From n=my reading of Howard's post we as a group do not know if the circuits/outlets are of the 15 amp variety or even 20 amp or 30 amp.

Like Rod,I don't see any gain in NOT Putting in the 20 amp/12ga circuits,but the original post doesn't give us all the req'd info to answer the question,unless someone has the NEC/local code issues.

Andy

Re: Wire Gauge for Garage Shop

#18

Re: Wire Gauge for Garage Shop

JoeW in Detroit, MI

>According to Table 210.24 you can have 15A receptacles on a 20 A circuit. The key is what size is the breaker or fuse at the panel for that circuit.

Also don't forget that the circuits must be GFCI protected. The circuit for your garage door opener is an exception because it is not readily accesible and has only the one oulet on the circuit.

Additionally, the CODE only allows that for cord and plug connected equipment the maximum load is 80 percent of the circuit ampere rating (210.23(A)(1). One circulaar saw would put you over on a 15 amp circuit.

Re: Wire Gauge for Garage Shop

#19

Re: Wire Gauge for Garage Shop

Wayne Carson

>14g wire is used for general lighting, which is fine for the Garage door circuit as it is a dedicated use and which has a load of less than 15 amps. It is also used for bedroom wiring. Garages are the same as kitchen circuits and require 20 amp circuit which is #12 wire. You need to put in 20 amp outlets also or you stand a good chance of burning them up with high current appliances. The inspector is correct. #14 wire can only be protected with a 15 amp breaker which will trip with more than one motor load in a shop, you will thank him in the end.

Re: Wire Gauge for Garage Shop

#20

Mostly okay…

Rod Peterson -- Ormond Beach

>> You need to put in 20 amp outlets also or you stand a good chance of burning them up with high current appliances.

Actually there is zero chance of burning up a 15 Amp receptacle installed on a 20 Amp circuit. Either 15 Amp or 20 Amp duplex receptacles may be used on a 20 Amp circuit. That is a particular and specific exception in the NEC. The 15 Amp receptacles are not limited to 15 Amps of current flow—they are keyed so that 20 Amp plugs can't be plugged into them.

Rod

Re: Wire Gauge for Garage Shop

#21

Re: Wire Gauge for Garage Shop

Fred Davis

>Wayne , you can join Larry at the head of the class ;-))

Light circuits 14AWG, any outlets in the Kitchen , Garage, utility room that are 120v. are 12AWG.

Just staying on the subject of 120 V. outlets, in a Kitchen for instance with a dishwasher and a disposal, most efficent Electricans will run a 12/3 AWG wire run to the area under the kitchen sink and divide that into running the disposal and the dishwasher thereby satisfiying the requirement for each applience to be on a dedicated circuit.

Then even a journeyman Electrican will sometimes forget what he is doing and switch the disposal with a 15 amp switch , since that was what he had the most call for in the house.

Having stood frame inspections on thousands of living units in the state of California with inspectors who while on the frame inspection also do the rough in for Electrical, Mechanical, Plumbing and roofing trades, I can state with certainy what the inspector is looking for and how far from standard practice he will let the trades deviate.

Case in point , we had one electrican who invariably would put more then one common wire in a slot on the neutral bus. When the inspector for one juridiction was breaking in a new inspector who had no common sense yet, the new guy said , ah hah , he can't do that.

The older and wiser inspector simply said " don't bother telling the electrican how much you know because he will just pigtail the neutrals and that will satisfy the requirement of no more then one wire in a slot in a neutral bus".

For those of you who have not upgraded or wired a shop in a garage or other building. you need to know not only the wire size for 240v machines, but the fact that each and every one has to be on a dedicated circuit by it's self .

For the ones that subscribe to the " Marcel Ledbetter" school of building , lots of luck and keep your fire insurance paid up.

FredD

Re: Wire Gauge for Garage Shop

#22

Re: Wire Gauge for Garage Shop

Al Stokka - Cambridge, Iowa

>Joe,

Yes, 15 A receptacles can be installed on a 20 A (12 ga.) circuit. My suggestion was that Howard might have installed 20 A receptacles on a 15 A (14 ga.) circuit, which is, I believe, not allowed.

Al

Re: Wire Gauge for Garage Shop

#23

Re: Don't give up too quickly�

Tony - Memphis

>Thanks. It is in a conduit. But I'm not even sure where the conduit comes out since it goes to a switch. My guess is they ran the quickest/shortest route, which would have been straight to the wall. I am looking for my pictures I took of everything pre-drywall. I'm sure I have a pic somewhere. That's another reason I may hire some help - to get more options that I wouldn't come up with since I don't know much about wiring. Hey, maybe I can get the electrician to help get the saw from the truck to the shop! Ha!

Tony

Re: Wire Gauge for Garage Shop

#24

Thank You ALL..................

Howard

>for all the great comments, I pulled out the 14 gauge and replaced with 12AWG and yes, they will have GFCI's in each one.

Re: Wire Gauge for Garage Shop

#25

Re: Thank You ALL..................

Fred Davis

>Howard , save yourself some bucks on the GFIC outlets.

You only need one for each circuit at the first outlet in that circuit and the rest (downstream) will be protected.

In addition to that . it is possiblie , tho a little more expensive , to have the GFCI in the branch circuit panel that will protect all of the outlets. You may want your electrican to install that one. ;-))

FredD